I have no idea what a GFCI actually is, or what makes it trip. Therefore, replace it.
Just kidding, of course!
Circuits are meant to flow current out the "hot" wire and back the "neutral" wire. Current is not supposed to go anywhere else. If it does, something is wrong, and if any of that current flows through a human, it could stun or kill them. If they fall or end up face down in water, a stun is a kill. This condition is called a "Ground Fault" hence GFCI is "Ground Fault Circuit Interruptor".
So, GFCIs compare the hot wire current going out to the neutral wire current coming back. If they are not equal, leakage is occurring and they trip.
So the best response to a GFCI trip is look for a ground fault. Start by unplugging anything fed from that circuit. If unplugging appliances works, then plug them back in 1 at a time until you find the tripper.
Or, the leak can also occur in the wiring, e.g. if mud wasps build a condominium inside an outdoor receptacle box. When that gets damp, it starts conducting electricity from hot to ground.
So you hunt for things like that, starting in the most obvious places.
If nothing is found, break the circuit at the halfway point by removing the downline hot and neutral. See if it still trips, and that will tell you which side of the break the problem is on. You can thus narrow down.
If disconnecting the Load wires from the breaker causes it to stop tripping and behave normally, that strongly indicates a problem with the circuit and not the breaker.
It's pointless saying the GFCI is defective until you've done those checks.