Questions tagged [gfci]

Ground Fault Circuit Interrupter(GFCI). Sometimes known as a GFI, or a residual-current device (RCD or RCCB). Can refer to receptacles as well as circuit breakers. They detect a leak in current, or an imbalance between the current on the hot and neutral wires. This is used to prevent electrical shock. Use with the [electrical] tag

Ground Fault Circuit Interrupter(GFCI) devices are usually required where electricity can contact water or some other ground, including kitchens, bathrooms, and outdoors. They work by detecting an imbalance (usually around 5mA) between the draw on the hot and the returning current in the neutral, and thus will disconnect(interrupt) the circuit. This prevents electrical shock. GFCI receptacles can protect down-circuit receptacles, provided those outlets are attached to the LOAD side of the GFCI.

The breakers may be installed within the breaker panel or as a receptacle or stand-alone, "dead-front" device in North America; they are typically found in the breaker panel in other parts of the world. In Europe, these may be called a Residual Current Device(RCD, usually for receptacles) or a Residual Current Circuit Breaker(RCCB), but they work the same way.

Similar to (but not the same as) Arc Fault Circuit Interrupters(), which are used to protect against arcing that could cause a fire. Some circuit breakers will do both GFCI and AFCI.

1178 questions
29
votes
9 answers

How do I install a GFCI receptacle with two hot wires and common neutral?

In my kitchen, I want to replace a regular 120V receptacle with a GFCI-protected receptacle. The instructions describe what to do with a regular 2-wire + ground feed, with and without daisy chaining to other receptacles, but not how to do it with a…
Matt Fox
  • 475
  • 1
  • 5
  • 8
27
votes
6 answers

Where should I NOT use a GFCI or AFCI?

There is a lot of information out there about the benefits of GFCI and AFCI and the places where they must or should be used. But are there any circumstances where you're better off without them? If I won a free box of dual-function GFCI/AFCI…
dlf
  • 607
  • 1
  • 11
  • 20
27
votes
3 answers

Now I realize I used too many GFCI outlets. How can I reclaim them?

Yeah, so the building inspector redflagged a bunch of outlets for not being GFCI. Before I understood how the LOAD terminals work, I just replaced every single one with a GFCI outlet. Most had a second cable for onward power, so I just attached…
Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
22
votes
3 answers

Replacing 2-prong outlets in basement - existing wiring has two hot wires, one neutral?

I'm replacing the two-pronged outlets in my basement with 3-pronged grounded outlets in the United States (Illinois). All the wiring is in metal conduit with metal conduit boxes, which are grounded to the breaker box (I checked with a multimeter…
David
  • 221
  • 1
  • 3
22
votes
4 answers

How do I properly wire GFCI outlets in parallel?

I have two countertop outlets in my kitchen that I am in the process of replacing with new, GFCI-protected outlets. These two outlets are on a circuit together, and they are the only loads on that circuit. After wiring the new outlets up and testing…
Drew Spickes
  • 385
  • 2
  • 3
  • 8
20
votes
4 answers

Which Kitchen outlets do NOT need GFCI?

I have the 2 circuits in the kitchen with GFCI outlets, but I'm not quite sure which other ones do NOT need GFCI. Other circuits in the kitchen include Microwave, Fridge, and Dishwasher. It makes sense to me to not have the fridge on GFCI though.
rcav8r
  • 249
  • 1
  • 2
  • 4
19
votes
9 answers

I live in an older home without ground wiring. Is it safe to install 3-prong GFCI with only a hot and neutral?

I live in an older home that doesn't have any ground wiring. Is it safe to just install 3-prong GFCI outlets and use devices and appliances that expect a ground wire connection when I just have the GFCI outlet and no actual connection to…
Dan
  • 309
  • 1
  • 1
  • 3
17
votes
4 answers

When to use holes instead of side terminals to wire an outlet

This question comes from Shirlock's comment on this GFCI wiring question. When and why should you use the holes on the back of an outlet rather than the side terminals? I always assumed the holes on the back were only for lazy electricians and…
BMitch
  • 42,463
  • 14
  • 91
  • 196
17
votes
10 answers

Why would a GFCI trip on refrigerator circuit?

My refrigerator is tripping the GFCI on the socket into which it is plugged. Searching about this topic seems to indicate that this is a reasonably common complaint. However, I can't find any concrete information about general causes or potential…
hoc_age
  • 273
  • 1
  • 2
  • 7
17
votes
5 answers

If I install a GFCI on the first outlet in a circuit will the other receptacles on that breaker circuit have GFI protection?

I have three electrical outlets in my garage which appear to be connected to one circuit breaker. I am assuming the outlet closest to to the panel is first in the three receptacle circuit. How can I test this assumption? If it is, will…
provlima
  • 451
  • 3
  • 10
  • 18
16
votes
1 answer

Do GFI/GFCI outlets have a potential to damage Nespresso machines (and coffee machines?)

I had a Nespresso Vertuo Next machine. It stopped working properly and during the troubleshooting video call, the Nespresso support agent said that the machines should not be connected to a GFCI outlet because they can potentially damage the…
Steve V
  • 300
  • 1
  • 6
16
votes
3 answers

Is it normal for GFCI receptacles to explode and burn?

I noticed my tooth brush wasn't charging one morning and none of the plugs in my bathroom were getting power, I went down to the circuit box and saw a flipped breaker so I flipped it back and it immediately tripped again. I tried it once more with…
almarshall
  • 171
  • 1
  • 1
  • 5
15
votes
1 answer

Can I add a standard receptacle on a GFCI circuit

So, I want to add a receptacle in the bathroom (I tend to run out of batteries on my phone while crapping at the end of the day). There's a GFCI outlet on the other side of the crapper wall that faces the bathroom sinks, so would be a simple matter…
SDGator
  • 343
  • 1
  • 3
  • 8
15
votes
4 answers

GFI outlets tripped after power outage

I live in a rural area that has frequent power outages (Several per month. Less than a minute in duration). When the power is restored, several GFI outlets always trip. I am trying to track down the cause of these trips, as one of the outlets…
cyclops
  • 837
  • 1
  • 9
  • 18
15
votes
3 answers

Why did my leaking pool light trip the circuit breaker, but not the GFCI?

This is, I am sure, an extremely naive question. I hope that's okay (and I hope it can be answered at a level I'll understand). The background: My swimming pool has underwater light fixtures, on GFCI circuits. I recently replaced the bulb in one…
WillO
  • 283
  • 3
  • 9
1