I am not an electrician, however, used to work for an electrical engineering firm so I’m pretty familiar with electrical circuits. Having said that I purchased a home where the previous owner had done some sketchy remodel work.
One of the areas he remodeled has a GFCI outlet in it. It is in an office downstairs with what we call a sitting room adjacent. All of the receptacles in the office and two in the Sitting Room are on the same circuit. That GFCI tripped the other day, I thought it had gone bad, as it would not reset so I replaced it. The new one tripped immediately after energizing it (yes it was installed correctly).
I unplugged everything downline, but still tripped, I checked every outlet downline for loose wires, etc. all was good. The GFI of course is at the head of the circuit. Panel —> GFI —> Load (7 outlets). I double-checked the ground, neutral and hot wires, only the hot wire coming from the panel has power coming to it.
When I connect the hot and neutral coming from the panel the GFI operates correctly and the test plug indicates correct wiring. As soon as I plug in either The neutral or hot load (yes I am plugging it into the load side of the outlet), the breaker trips and won’t reset. If I bypass the GFI everything works fine - all circuits test as correctly wired, nothing shorts out, breaker stays cool, and everything works.
I’ve tried two different GFI outlets in case I had a dud. Am I good just to put a standard receptacle in place of the GFI? In case you were curious I believe the reason there is a GFI there in the first place is the office was originally part of the oversized 5 car garage.