19

I live in an older home that doesn't have any ground wiring. Is it safe to just install 3-prong GFCI outlets and use devices and appliances that expect a ground wire connection when I just have the GFCI outlet and no actual connection to ground?

What are the exact differences between a no-ground GFCI outlet and a grounded GFCI outlet in terms of safety?

Dan
  • 309
  • 1
  • 1
  • 3
  • 8
    The proper thing to do in this situation is to get the house rewired to add grounds to all the outlets, but I imagine that would be very expensive. – Hearth Jun 01 '21 at 00:54
  • 4
    Where in the world are you? – user_1818839 Jun 01 '21 at 13:01
  • 3
    @Hearth "proper" in what way? A homeowner in OP's circumstances could replace all outlets in a typical home with GFCI for $200, or critical outlets for much less and gain 90% of the safety benefits of rewiring with ground. Rewiring might cost tens of thousands. Of course there may be other benefits to rewiring, especially if the wiring is very old or obsolete but I think your comment may unnecessarily dissuade people from an easy step that improves safety a lot. – jay613 Jun 01 '21 at 15:51
  • While not ideal, the neutral line can be an effective ground path, provided the circuit is not overloaded. – jwdonahue Jun 01 '21 at 18:09
  • 3
    @jwdonahue Actually, it doesn't work that way. Ground for static/surges/etc. on neutral would be fine. But when it comes to true faults, this could result in turning a temporarily dangerous situation into a permanently dangerous situation. **Not a good idea.** – manassehkatz-Moving 2 Codidact Jun 01 '21 at 18:53
  • Wouldn't it be permanently dangerous anyway, if the ground post was not connected to anything at all? At least it provides an alternate current path from case to ground, other than through a persons body. I understand it's not ideal, but I have used it in old houses in the past, to connect my computer equipment surge protectors. I always verify the neutral lines are properly connected at the fuse/breaker box to earth ground first. – jwdonahue Jun 01 '21 at 19:14
  • @user_1818839: My first house was built in the early 1920s in Montreal (Canada). Though there had been some electrical renovations on the first floor (which were done to current code) there was still a lot of the original wiring, particularly for the second floor. In the basement, it was easy to pick out those original circuits, the two wires were mounted on separate insulators and ran about 4 to 6 inches apart. When I wire went through a joist, it ran through an insulating grommet-like thing that went through the joist and kept everything insulated. My second house was built in 1908 &... – Flydog57 Jun 02 '21 at 21:35
  • @jwdonahue: A GFCI that was *designed* to use a supplied neutral as a grounding path could provide more safety benefits than would be obtained by using a normal GFCI without connecting downstream grounding connections to anything, but connecting a downstream grounding terminal directly to an upstream neutral without purpose-designed safety circuitry to ensure such a connection was broken in all fault conditions would create dangers of its own. – supercat Jun 02 '21 at 21:53
  • Not an answer, but I was in a similar situation last year. I re-did the outlets and couldn't be happier with it. For whatever that's worth – TCooper Jun 03 '21 at 20:40

9 Answers9

41

Absolutely!

There are a number of different functions that an ordinary ground wire performs. A GFCI, despite the "G", does not actually need a ground wire to function. In fact, a properly installed GFCI will provide protection similar to (and actually in some ways better than) a regular ground. That doesn't mean you shouldn't have ground. But it means that if you don't have ground, GFCI can protect you anyway.

When you install GFCI in this way, you do everything the same as a regular installation except that you don't connect anything to the ground screw. You are supposed to label them no equipment ground.

How does this actually work?

The traditional ground wire has no power flowing over it in normal usage, with the exception of some special types of switches or other equipment that are allowed to send a very small amount of current over ground (this generally has to do with smart/dimmer/timer/etc. switches with no neutral available - not ordinary receptacles). The ground gets power in two ways:

  • Natural - lightning, static electricity, etc.
  • Fault - device failure that sends power either directly to ground or via a metal case (or other metal parts) to ground.

The second case - actual faults in wiring or equipment - is designed in a way that if lots of power goes over ground, the breaker (which is on the hot wire) will trip, shutting off the circuit.

A GFCI takes this "fault" a few steps further. Unlike a regular breaker:

  • It activates on tiny amounts of current (not enough to kill, but far less than it would take to trip a breaker)
  • It activates extremely quickly (a regular breaker will trip very quickly if it gets a huge overload but not so quickly for a small overload (e.g., 30A on a 20A circuit).

A GFCI also doesn't really "care" whether the current is going to an actual ground wire (and directly back to the breaker panel) or if it is going through a person to the ground under their feet.

The end result is that a GFCI can effectively substitute for a ground wire, since the same faults that would normally use ground will instantly trip a GFCI, and additional safety because it trips on small amounts of current and very quickly.

Note that a GFCI does not substitute for the regular breaker in every aspect. In particular, a short circuit where all current goes back on neutral (and nothing on ground or through a person) will have no effect on a GFCI because the GFCI still sees the hot & neutral as balanced.

Note also that "better protection" does not, generally speaking, mean that "everyone should put GFCI everywhere". GFCIs are not free, so there is a cost-benefit analysis involved. GFCI also can have some drawbacks (an unnoticed GFCI trip turning off a refrigerator can result in spoiled food). Since the extra protection provided by GFCI is most useful in wet areas, GFCI protection is required in kitchen, bath, outdoor (rain) and certain other locations, but not "everywhere". That being said, using it in place of retrofitting ground is often practical and cost-effective protection.

TylerH
  • 994
  • 8
  • 20
  • 21
    Just note that most people think a breaker protects people. It actually doesn't. It protects the building. You will be LONG DEAD before even the weakest 6A breaker trips. The GFCI trips on 30mA, about 200 times less than what the breaker's rating are, but it'll still hurt. 100mA is enough to kill you. – Nelson Jun 01 '21 at 02:01
  • 8
    @Nelson Most GFCIs trip in the 4-6mA range – Machavity Jun 01 '21 at 12:06
  • 2
    Note that any surge protectors will not work, but that is a problem with not having the ground wire attached to the ground prong on the outlet - just because the GFCI has a third hole doesn't mean it does what it does in a 3 wire system. – Jon Custer Jun 01 '21 at 12:26
  • 4
    @JonCuster A surge protector normally diverts the current to ground. That won't work with ground being an unconnected pin. If the surge actually came via hot and is large enough then that may still trip the GFCI - not quite as good as "divert the surge and keep the computer running" but better than "zap everything". – manassehkatz-Moving 2 Codidact Jun 01 '21 at 14:05
  • 3
    @manassehkatz-Moving2Codidact Yeah, I would definitely consider it a 'still worked' scenario if the GFCI threw during a surge and ended up preventing my stuff from getting fried... most surge protected power strips I see people buy don't have enough protection for the kind of surge that would cause problems anyway. – TylerH Jun 01 '21 at 14:40
  • 2
    @Nelson: Breakers help protect people from building fires. – supercat Jun 01 '21 at 15:12
  • 2
    @JonCuster: A surge protector that has MOVs between hot-neutral, hot-ground, and neutral-ground will protect equipment using the first of those. Some surge protectors omit the first one, but such designs are inferior in two ways: (1) They will provide inferior protection in the absence of ground; (2) They will cause a GFCI to trip in most cases where they suppress anything, even if what they were suppressing was an otherwise harmless minor voltage spike caused by e.g. switching off a motor (the latter point is why surge suppressors have a reputation for tripping GFCIs). – supercat Jun 01 '21 at 15:19
  • 5
    Good point about a GFCI on a fridge. I had exactly that problem, until I replaced the GFCI with a higher quality unit. The replacement I used also has an audible alarm so if it does trip, I might notice before all the food is spoiled. – Phil Frost Jun 01 '21 at 17:46
  • 1
    GFCIs also have the problem of false trips caused by starting loads on heavy motors. Our old house had one outlet in a position that wasn't actually required to have a GFCI but it was cheaper for the builder to include it in a GFCI line. It was also by far the most convenient outlet for the vacuum cleaner--except for the tendency to pop when the motor started up. – Loren Pechtel Jun 02 '21 at 04:17
  • 1
    @LorenPechtel In addition to cost, nuisance trips are a big reason, I think, why GFCI is not required "everywhere". But if you don't have ground available, GFCI can be a very cost-effective fix for that. – manassehkatz-Moving 2 Codidact Jun 02 '21 at 04:30
  • @PhilFrost How do you not notice the lack of a light in the fridge though? – Dean MacGregor Jun 02 '21 at 13:56
  • 1
    @DeanMacGregor It is actually a 2-part problem. (Ignoring: Some people don't bother to replace the bulb in the refrigerator when it goes out.) Step 1: GFCI trips, turning refrigerator off. This happens and you *don't recognize the problem* - which can easily happen if the GFCI is located either at a different receptacle or in the main panel. Many people, many times, will get frustrated at not being able to figure out and leave it for "call the electrician *tomorrow*". 2 - When finally reset *after several hours out* they open the refrigerator – manassehkatz-Moving 2 Codidact Jun 02 '21 at 14:06
  • 2
    *after it has been back on for a few hours* and find the light on and everything cold, **and they do not realize the refrigerator was out for several hours because power did not go out for the whole house**. Sounds crazy/stupid. But it can easily happen. Particularly since kitchen GFCI-protected circuits can be shared with dining room (so no obvious "this is all related to the kitchen, better check things out") and while the labels are technically required ("GFCI protected") they are often (*nearly always*) left off or removed **and** the refrigerator would be even less obvious because the – manassehkatz-Moving 2 Codidact Jun 02 '21 at 14:08
  • 2
    receptacle is behind the refrigerator so out-of-sight, out-of-mind. I had a non-GFCI similar situation a while back when I was doing work on the cooktop exhaust fan and ended up leaving the circuit off overnight (deliberately). I didn't realize that the secondary refrigerator/freezer downstairs was on the same circuit (I *should* have, but I didn't, and I could have easily connected an extension cord to another circuit if I realized it) - freezer was pretty much OK but I had to toss some refrigerated stuff to play it safe. If I hadn't thought to check at the right time **I would not have** – manassehkatz-Moving 2 Codidact Jun 02 '21 at 14:11
  • **realized that stuff had gone bad** and someone could have gotten sick. **Stuff happens**. – manassehkatz-Moving 2 Codidact Jun 02 '21 at 14:12
  • 1
    @DeanMacGregor I did notice, which is why I replaced the receptacle :) – Phil Frost Jun 02 '21 at 17:30
  • 2
    @DeanMacGregor The light being out doesn't mean the fridge is powered. It could just mean the bulb went bad or has an issue due to condensation. Or what actually happens in a lot of smart fridges: the door open sensor has an issue. That's all in addition to it being impossible to detect much of the time when food has gone bad even when the fridge has cooled back down after a power reset as manassehkatz has already mentioned. – TylerH Jun 02 '21 at 21:45
13

Safety

In terms of safety, GFCI is all you need. The ruling factor for safety is that the GFCI will shut off if more than 5ma leaks (e.g. via a human being shocked). That is better human protection than grounding, actually.

Lack of ground, however, reduces the chance of a shock happening (and thus a shock being detected). If a human touches hot and ground and the system is grounded, current will flow and the GFCI will trip. If the human touches hot and ground and the ground is isolated, then all of it - hot, human, chassis ground, and any grounds in that "island" (i.e. grounded power strip) -- will cheerfully float at 120V from neutral, like a bird on a wire. No one will ever know there was a problem.

Note that GFCIs do nothing about a human getting between hot and neutral. But that is highly improbable with good equipment design.

Labeling

GFCI is not a receptacle, it's a protection system. Any GFCI device can protect a downline part of a circuit. (GFCI receptacles protect their own sockets, obviously). So in fact, you can have full circuit GFCI protection without a single GFCI receptacle being involved.

Anyway, GFCI receps give you the choice whether to protect the downline or not. If you don't want to protect a downline, you use only the "Line" terminals - and they are designed to accept 2 wires (check the instructions). If you do, then you remove the warning tape and use the "Load" terminals. In that case, you must label the downline receptacles "GFCI Protected". (you don't need to label a GFCI receptacle that, because it's obvious).

Regardless, if the GFCI is not grounded, you also needs a "No Equipment Ground" label both on the GFCI and any downline receptacles.

The reason for the "No Equipment Ground" label is to warn users that there is no ground to assist in surge suppression. This can be a threat to electronics.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
  • The tripping current of a GFCI is 30 mA in some places. 5mA tripping current is way too little to overcome loss due to magnetic field build up. –  Jun 04 '21 at 06:30
  • 1
    @Berend those aren't GFCIs, those are GFPEs. (Ground Fault Protection of *Equipment*). They are not considered adequate for life safety. – Harper - Reinstate Monica Jun 04 '21 at 16:36
  • Some of these terms are less defined than others, so you're probably right. I just get the creeps when people call things electrical "safe". GFCI at any amperage does not replace ground protection. It simply doesn't do the same thing. –  Jun 07 '21 at 22:47
4

What are the exact differences between a no-ground GFCI outlet and a grounded GFCI outlet in terms of safety?

Consider what happens when a wire comes loose inside an appliance and touches the case metal case. In the design of a "Class 1" appliance this would be considered a "single fault condition".

If there is a proper ground connection then current will flow through the ground connection and cause a trip almost immediately. Since most items are not being touched most of the time, the chances are it will disconnect the fault before anyone gets a shock.

If there is no ground connection then there will initially be no trip, the case of the appliance will remain live until someone (or something) touches it. Only after they have touched it and are getting a shock can the GFCI detect there is a problem and disconnect the power. In most cases, it disconnects the current before the shock becomes fatal but it would still have been vastly preferable not to have had the shock in the first place.

So why do codes in the USA allow fitting 3 pin GFCIs, in place of regular 2 pin outlets in retrofit applications (but not in new installations)? Because it's a lesser evil. In the real world people will use their electrical appliances even if that means cutting off the earth pin or using a cheater plug. It's much safer to have a missing ground and a GFCI than a missing ground and no GFCI.

Peter Green
  • 4,871
  • 10
  • 28
3

Summing up and coloring in

Here are several common failure scenarios and the behavior of various grounding configurations. A GFCI without a ground is much safer than a regular grounded outlet or an ungrounded one, and almost as safe as a grounded GFCI. Red is bad. Yellow is undesirable as it employs the user to trip the GFCI but it does so quickly and without injury.

Referring to the Question we are moving from an entirely red column to a slightly yellow one. A good investment for just swapping out some outlets.

There are other situations where a ground is needed eg some medical devices, surge arrestors, etc. I have not tried to account for those.

enter image description here

jay613
  • 28,850
  • 2
  • 36
  • 112
  • Keep in mind that on this chart, a 3-wire dryer or range is off well to the right, with the added bonus of automatically becoming zappy if neutral fails – ThreePhaseEel Jun 04 '21 at 23:40
  • 1
    Oops. I just hastily tried to think of a metal appliance not connected to plumbing. I should have used a 120V plug-in one as an example. A stainless steel tea kettle would have been good. – jay613 Jun 05 '21 at 14:15
2

This is exactly what the electricians did for a few outlets in my home.

I had most of them grounded for the sake of the computers, but there were two or three where it was extra difficult to fish a ground wire and they installed ungrounded GFCI outlets. (House built circa 1951, this work done in 1995 or so.)

Others have explained well why this works, and the limitations, so I won't repeat that; just giving a data point that it is done by licenced professional electricians.

Tom Swiss
  • 21
  • 1
1

Yes!

GFCI does not need a connection to Earth to work. If you put a GFCI in your main electrical panel, it measures the difference in current between Live and Neutral wires, and if that difference exceeds a threshold like 30mA, it will trip.

The idea is, under normal conditions, all the current that flows from the power company's cable through the live wire then flows through the various appliances in your home then back through the neutral wire. If there is a difference between these two currents, it means some current is returning through a path that it shouldn't take, for example through someone's fingers, their body, their feet, the floor, then through Earth, then back to the power company's transformer neutral which is usually connected to Earth. Or something like that. So it trips.

However:

if someone cleans the toaster in the sink and then plugs it, or if the washing machine has a leak that sprays water into the electric bits, or any other similar problem that causes a current leak from live to accessible metal, then the metal enclosure of the appliance could carry dangerous voltage.

If the appliance is earthed, and the earth wiring in the house works properly, then this causes a current to flow in the Earth wire instead of returning via the neutral wire, and the GFCI trips before someone touches the dangerous device. If the appliance is not earthed (or there is no Earth in the house) then that won't happen, but the GFCI will still save your skin if you touch the appliance and get zapped. In this case you act as the Earth conductor, and you get zapped, but only for about 10 milliseconds.

In theory, a GFCI does NOT protect from electrocution when touching both live and neutral, because in this case there is no way to distinguish a finger from a legit electrical load consuming current. However, if you are standing barefoot on a somewhat conductive floor, enough current will still leak through your feet to make it trip. Same if you dump the hairdryer in the tub, and the tub is earthed, it should trip.

So, basically, if you don't have Earth, the GFCI will not provide an early warning when an appliance is unsafe, but it will still protect you from surprise electrocution. But it is not a magic bullet nor idiot proof.

bobflux
  • 8,484
  • 22
  • 28
  • There are currently 2 classes of GF protection devices,: 5mA ground fault protection for personnel UL 943, and 30mA ground fault protection for equipment UL 1053. Receptacles are UL 943, 5mA. – NoSparksPlease Jun 01 '21 at 15:41
  • Yeah, here (France) at least one 30mA is mandatory at the panel. There are usually more, for example one for the freezer, so it doesn't lose power if the main RCD trips. – bobflux Jun 01 '21 at 15:54
  • Here in the UK we consider 30mA to be sufficient for supplementary personal protection in most cases, 10mA RCDs exist here but are rare and anything lower than that is practically unheard of. – Peter Green Jun 01 '21 at 16:18
  • Good point. Usually on this forum when people use the abbreviation GFCI rather than RCD many people assume it is a North America question. Maybe you could have deterred someone from the TD if you had used European terminology. Should have recognized that you weren't since you said "in your main electrical panel". Also you used a toaster in your example, might not be the best example since in N.A. toasters do not typically have an equipment ground. – NoSparksPlease Jun 01 '21 at 16:18
  • 2
    Yeah, I've tried to use the same terms as OP... Oh, btw, the toaster example was courtesy of the tenants. Some also call me to inquire why there is no power after they wash the cooker in the sink and then plug it in. You know, teenagers cooking for the first time, always quite the experience XD – bobflux Jun 01 '21 at 16:20
1

Safer? Yes. Safe? No! Think for a minute and ask yourself "Why does the NEC require a sticker that says 'No Equipment Ground' if the receptacle is safe?".

The key to this answer is your question asks about "appliances that expect a ground".

The sticker is there to warn you to not use the receptacle where a ground is required.

Here is the edited NEC section that allows GFCI protection for 3 wire receptacle replacement for ungrounded receptacles, note most carefully the Informational Notes at the end.

406.4(D)(2) Non–Grounding-Type Receptacles. Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(2)(a), (D)(2)(b), or (D)(2)(c).

(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles or their cover plates shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.

Informational Note No. 1: Some equipment or appliance manufacturers require that the branch circuit to the equipment or appliance includes an equipment grounding conductor.

Informational Note No. 2: See 250.114 for a list of a cord-and-plug- connected equipment or appliances that require an equipment grounding conductor.

Informational notes remind you to refer to other codes or parts of this code that have bearing. Note 1 generally refers to NEC 110.3(B).

110.3(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.

So if you have a window AC unit, and the user instructions (which are part of the UL Listing) or tag on the cord says to use a grounded outlet then it is not certified for use on an ungrounded circuit, and use of a labelled receptacle does not change that.

NEC 250.114 goes further explaining certain equipment, labelled or not, is not safe enough without a ground.

250.114 Equipment Connected by Cord and Plug. Exposed, normally non-current-carrying metal parts of cord-and-plug-connected equipment shall be connected to the equipment grounding conductor under any of the following conditions:

(3)In residential occupancies:

(a)Refrigerators, freezers, and air conditioners (b)Clothes-washing, clothes-drying, and dish-washing machines; ranges; kitchen waste disposers; information technology equipment; sump pumps; and electrical aquarium equipment

(c)Hand-held motor-operated tools, stationary and fixed motor-operated tools, and light industrial motor-operated tools

(d)Motor-operated appliances of the following types: hedge clippers, lawn mowers, snow blowers, and wet scrubbers

(e)Portable handlamps and portable luminaires

So an ungrounded GFCI receptacle will provide protection in case of fault to ground with a two-wire circuit, and allows polarized plugs to replace old non-polarized plugs, but it is not legal to use those receptacles for many applications, which is the main reason you are required to label it "No Equipment Ground".

And you asked difference about grounded or ungrounded GFCI's, at least one aspect is if a fault develops to the ungrounded chassis the chassis will remain energized until something or somebody completes the path to ground. A GFCI functions by running both wires through a current sensor (current transformer). If no current is leaking to ground the magnetic fields cancel each other and nothing is detected in the current transformer. If there is an imbalance then magnetic fields don't cancel, current is developed in the CT, and the device is triggered to open. So just energizing the chassis doesn't upset the current flow, a grounded chassis provides that path. I think most of the items listed in 250.114 are there because human contact with the chassis is the likely event to complete the path.

NoSparksPlease
  • 14,833
  • 1
  • 12
  • 40
  • NEC quotes from 2017. – NoSparksPlease Jun 01 '21 at 16:21
  • 1
    I wonder how hard it would be to have a standard for a purpose-designed no-equipment-ground GFCI which would provide a *current-limited* path from the grounding conductor of protected equipment to the neutral, and trip (disconnecting such path) in response to an excessive potential difference between the grounding conductor and neutral, as well as in response to unbalanced currents flowing between line and load terminals. – supercat Jun 01 '21 at 23:11
  • 1
    *allows polarized plugs to replace old non-polarized plugs* - No! A standard 2-prong receptacle **is** polarized. Switching to 3-prong w/GFCI doesn't change that. – manassehkatz-Moving 2 Codidact Jun 02 '21 at 03:40
  • 2
    *I think most of the items listed in 250.114 are there because human contact with the chassis is the likely event to complete the path.* Hard to guess *why* they are in 250.114. But the reality is that a properly functioning GFCI provides the "human contact" protection for these devices that an ordinary ground wire does *not* provide. – manassehkatz-Moving 2 Codidact Jun 02 '21 at 03:44
1

Interesting that this was migrated from the EE SE.

I remediated this problem in my first house. It's very common. Two-prong outlets in an old house and some nitwit puts in three-prong sockets without a ground. The local authority (Ontario ESA in this case) says "No good, either ground it or put GFCIs on every socket" He also said I could put back 2-prong outlets, but I would have to go to an antique shop to find them.

In regards to safety, GFCI ungrounded is IMHO far safer than no GFCI with ground. The GFCI works with a toroid which is electrically balanced between the current in the live and the neutral. If there is an imbalance, a relay triggers and breaks the circuit.

Chassis grounds on things like fridges and dishwashers etc can be dangerous as in the event that a low enough current leaks through the chassis somewhere in the circuit, then every fricking chassis of every appliance with a chassis ground on that circuit will electrify. This isn't even that weird given the service neutral and ground are electrically bonded at the panel. In modern houses, large appliances have their own circuits, so only the appliance itself will electrify, but in old houses, i.e., yours, it's not always clear. In terms of this causing a fuse to blow, it would require a catastrophic short for live to hit ground and put 15A through the chassis. If the neutral shorted to the chassis, you wouldn't even notice a current change in the appliance, but the chassis would still be electrified.

The danger of current passing through your body is all about finding the path of least resistance to ground. If some current takes a shortcut through your body to get to ground, you may be in trouble. When this happens with a GFCI, the current of the live and neutral will differ and that relay will trip. With a well-grounded outlet?... your body will still be part of the circuit, unless you're in the bathtub, you might only feel a buzz, as you have a relatively high resistance compared to the copper wire.

To throw a wrench into the whole thing, large electric motors imbalance the live/neutral current too, spinning up that motor takes current, and when the motor stops, the momentum of the motor can send that current back. Washing machines and electric lawnmowers can trip GFCIs, so there are limits to their usefulness.

In Ontario if you do any work on your own house where you live, you need the electrical inspectors to give you a pass before it's ok. If the house is not yours or you don't live in it, you're not allowed to do the work.

All this said, grounding equipment as a non-safety issue is desirable as it eliminates problems caused by floating grounds https://en.wikipedia.org/wiki/Floating_ground ... but if you're having problems like this, you're on GFCIs and you're not relying on the ground for safety, then you can run a wire from the chassis to a pipe or radiator. Most stuff doesn't even have a three prong plug these days anyway.

Only rewire the house if the walls are already open, you're worried about resale or have problems with insurance.

In the end, I put in GFCIs and the ESA inspector passed me.

mgjk
  • 113
  • 3
0

Do yourself a favor and install some kind of ground.
There is no such thing as absolutely safe electricity. Any electricity is potentially unsafe, which means anything being safe in electrical systems is always relative to how you treat it. I went to school in a building that had open metal power lines running along the ceiling. That was considered acceptable then, but only safe if you didn't jump for it.

In your house, a GFCI will be an improvement over no GFCI, but installing any ground wiring will be still safer than that. Proper ground wiring has to live up to local regulatory standard, but 'improper' ground wiring doesn't. Electricity will prefer running along a home made ground connection over running through you any time. Provided you stay away from the electrical system itself, you can ground pretty much anything you like completely unrestricted and it does pay off.

A GFCI may be what keeps you alive, but the trip current is still far from enjoyable and that current will pass through you unless it finds a shorter way home.