8

I've recently moved into a new home with a few outbuildings. Due to the property being in rural unincorporated area, no inspections or permitting was required on the outbuildings when they were built last year.

To mitigate the risk my insurance company paid for and completed a comprehensive electrical inspection to check for fire risks. The inspection report listed a deficiency with all of the outlets in my largest outbuilding. It was not deemed a fire risk, so I don't need to immediately fix the situation, but I am wondering how important it is to get fixed (For safety reasons).

The report listed the deficiency as: "Possible MWBC without pig-tailed neutrals in all outlets within building 4"

I've pulled apart one of the outlets as seen below:
Outlet Pulled apart

I have a total of 60 outlets (30 boxes with 2 outlets each) wired this way, so I'd rather not change if not necessary.

The 3 matching breakers for these outlets are These 2 pole GFCI breakers, additionally if I measure between the red and black at each outlet box, I get 248 volts, so I assume I do have multi-wire branch circuits in use here.

For what it is worth, the building should have been built to NEC 2018. The lack of conduit will be addressed.

Specific questions:

  1. What is the risk of not using pig-tailed neutrals when connecting MWBC outlets?
  2. How important is it to get fixed (Shut off breakers and don't use until changed, get to it in a month, within next year, don't bother changing).
cyclops
  • 837
  • 1
  • 9
  • 18

3 Answers3

11

Multiwire branch circuits (MWBCs) share a neutral. There is a code rule that prohibits wiring devices, such as receptacles, in a way that the removing the device would open (i. e., disconnect) that shared neutral. If the device is pigtailed, that rule is satisfied because removing the device doesn't disconnect anything else on the circuit from the neutral.

The prohibition exists for MWBCs because opening the neutral causes major trouble on those circuits. When the neutral is opened on a MWBC, the voltage at the outlets destabilizes - on a 120V MWBC, you could see anything from 0V to 240V*, causing all kinds of problems. So if someone removes a device and unwittingly caps the neutral, leaving it open, you can wind up with a very bad situation.

Obviously if you wind up with 240V applied to appliances and etc. intended for 120V, they may by destroyed immediately, especially sensitive electronics, and think how many things around the house have sensitive electronics. Motors may run way too hard for a short while, then fry.

A device like a space heater, a purely resistive load, may not be destroyed or damaged, but will pull up to double the usual current, overloading the circuit. Hopefully the breaker is functioning correctly and it will trip quickly before anything is damaged. But if anything is wrong with that breaker, it could fail to trip and cut power, and the resulting overload can damage wiring and connections, and is a major fire risk.

I wouldn't let this go for long. The risk is just that someone working on the wiring removes a receptacle and unintentionally leaves the neutral open. So until it is corrected, I would not allow any other work be done on the wiring.

If everything is nice and neat and roomy like the box in your photo, it's likely a day's work with very little materials required. Open the box, use the one pigtail that's already there, add a pigtail to the other receptacle, nut the four together, close the box, lather, repeat.

By the way - there is no 2018 NEC.

*With the neutral open, a shared neutral circuit degenerates into a 240V parallel - series circuit, such that the loads (in parallel) on L1 are collectively in series with the loads (also in parallel) on L2. The voltage on the L1 side and the L2 side will depend on the load on each side. If there are no loads on L2, the L1 side will see 240V. If the loads on the L1 and L2 side are the same, the voltages will be the usual 120V on both the L1 and L2 side - until something is turned off.

batsplatsterson
  • 24,664
  • 1
  • 31
  • 80
8

No, you really need to fix that. Search this site for "Lost Neutral" for what happens when the neutral wire has a problem. It's bad, and it can set stuff on fire.

Look at that neutral in your photo. Simply to transit this box, current must go through four splices. Two on each receptacle - supply, jumper, jumper and onward. That's 4 places for things to go wrong. If you pigtail it as Code requires, you're now down to 1 - and 1 that is unlikely to fail if done competently. You're not even hoping the guy at the receptacle factory wasn't even having a bad day - not much to go wrong on a properly tightened wirenut.

I can't even call this work sloth, because 4 shepherd's hooks is a lot more work than pigtails. That's why I pigtail stuff I don't even have to.

The above is not the (only) reason Code requires pigtailing. It's for a different reason too, but that will seem irrelevant.

If the receps are in an uncomfortable location to work at, then just remove the 6 wires and sever the ground, and drag receps and domed cover back to the workbench. Put pigtails on the receps and mount them back into the domed cover. Then go back to the site, trim the 6 wires to length for a red wire-nut, then nut 'em up to the receptacle wires. That way you're spending minimum time in the stress position/crouching/up ladder etc.

Note that if the ground wires are properly attached to the metal box, and the receps mount to the domed cover with 2 screws each (not only the center screw), then that metal-metal contact is the valid grounding path and you don't need ground wires too.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
4

The problem is not a fire it is a shock hazard. As far as if it is important, it has been code for decades. The issue comes when the neutral may get separated then everything down from there won’t work, but there are still 2 hot legs with GFCI protection. The risk is low but it should be updated. A wirenut and pigtails to the receptacles really won’t take long and is code compliant.

George Anderson
  • 22,321
  • 3
  • 31
  • 76
Ed Beal
  • 101,306
  • 4
  • 72
  • 150
  • I can't tell if the backstabs were used in the original construction but if they were, the OP will want to eliminate those when he adds the pigtails. +1 – JACK Oct 09 '20 at 19:18
  • 2
    How is it not a fire risk? If the neutral becomes disconnected, but there are 120V loads on both legs downstream, they'll divide the 240V among themselves. It seems the GFCI would not interrupt this situation. The loads on one side may/will get substantially more than 120V applied and the magic smoke will be released from some. If the loads are UL approved their risk of flame-out in this scenario may be reduced but I wouldn't think the risk goes to zero. – Greg Hill Oct 09 '20 at 19:38
  • @GregHill it might help if you grasp a bit of what things go through to get UL-listed. Double voltage may well ruin electronics, but it's very unlikely to light much on fire. Other than unlisted self-imported crap, anyway. JACK it looks like screw connections only, at least all the visible ones. – Ecnerwal Oct 09 '20 at 19:54
  • @Greg hill First they are contained in metal boxes the breakers are GFCI if a direct short the breaker will trip if a fault to ground by the neutral the GFCI would trip, not a fire risk. I would say a back stab has a higher risk of fire and code allows them even though they routinely fail I have seen heavily melted boxes but no full on fires. As far as a pair of devices the lower wattage one may be damaged but still not a fire risk. – Ed Beal Oct 09 '20 at 19:58
  • 1
    @Ecnerwal I've actually shepherded a mains-powered device through UL listing. Over-volted components absolutely can flame out and UL does look for protections in components and assemblies against that. Ed, I was referring to risk of smoke/fire from over-volted plugged-in devices, not the outlets themselves. Open neutral on a 2-pole GFCI does not imply ground fault; current can flow between L1 and L2 barbequeing some 120V devices by over-volting them and the GFCI doesn't care. – Greg Hill Oct 09 '20 at 20:26
  • I have seen the neutral go several times in industrial / commercial facilities and the worst thing I remember is small wattage devices like radios let them smoke out but never a fire there is a big difference in fire hazard and going up in smoke. – Ed Beal Oct 09 '20 at 21:43