I am trying to install a portable hot tub in my back yard. Starting at the tub, I ran two hots and a neutral plus ground back to the 60 amp GFCI in my disconnect box. Then, I ran the same wires back to my main panel, but my main house panel does not have a neutral bar, what can I do?

Silverback
  • 21
  • 2

2 Answers2

5

Connect the white wire to the bar the other white wires are connected to -- it is not rare for a main service panel to have a combined neutral and ground busbar, as that is the (only!) point where neutral and ground connect.

ThreePhaseEel
  • 79,142
  • 28
  • 127
  • 220
3

Neutral and ground are kept separate absolutely everywhere, except one place: the main panel. Here, it is OK to simply use one bus for both neutral and ground.

You will probably find a lot of whites and a lot of bare wires going to the same bus. That's the one.

Just for reference, DON'T do this in a sub-panel or you can create a lethal hazard.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
  • Thank you both for the advice. I did use the ground bar in the main service panel, and the spa is now working great! – Silverback Jun 14 '16 at 04:04