14

My house was completely rewired by the previous owner. They tore out all the old knob-and-tube and replaced it with modern wiring. I definitely appreciate this, but unfortunately they left absolutely no extra space on the new breaker box. Every single slot is filled with a circuit breaker.

It's not that the circuits are doled out too liberally either. Its just a small breaker box. It fits the requirements of the house exactly, but leaves no room for future expansion.

So, what are my options for adding more breakers? Can I add a sub breaker box? Or should I just replace the whole thing with a larger one?

Steve Armstrong
  • 763
  • 1
  • 9
  • 14
bengineerd
  • 491
  • 3
  • 8
  • 15
  • A tandem breaker costs about 3 times as much as two single breakers. Depending upon how many you want to add, it might be cheaper to just get the sub-panel. – Paul Feb 15 '13 at 23:06

6 Answers6

13

You have two options:

  1. use tandem breakers
  2. Install a sub panel

There are caveats with both routes. When using tandem breakers on a 120 volt system (i.e. with a neutral present), you want to avoid something that is called a multifeed. This is, two circuits on the same phase sharing the same neutral. When using tandem breakers, its very easy to inadvertently do this.

If you are in the US, you will see two feeders from the meter, one of them probably has some red tape on it, the other is black. These are your phases. Normally, every other breaker is on a different phase, but tandem breakers put both circuits on the same. Take care that both circuits attached to a tandem have their own neutral (white wire).

While you might be able to install a tandem breaker yourself (I highly recommend calling a qualified professional), you will surely want an electrician to install a sub panel. They aren't much different from a regular panel except:

  • Ground and neutral conductors are isolated, not bonded on sub panels
  • You want to watch your loads
  • You'll want to be careful about where you place the breaker that feeds a sub panel, so that you don't develop a hot spot on the main panel bus. For instance, you don't want a 100 amp sub panel breaker right in the middle of a water heater and an air conditioner.

In either case, I really recommend calling an electrician.

Tim Post
  • 1,664
  • 12
  • 23
  • I want to add that if you have a 240V circuit and you want to install a tandem breaker, you can get a quad-pole breaker. It's basically 4 1/2-size breakers glued together. – Jay Bazuzi Jun 23 '11 at 04:33
  • In some countries it's illegal to do your own electrical work unless you're a qualified electrician. Some countries allow minor changes to be done to but not in the breaker or meter box. If anything goes wrong (your insurance may not cover you). I'd call in an electrician for this work. – hookenz Jul 11 '13 at 22:24
  • Maybe he could have a larger higher capacity panel installed? – hookenz Jul 11 '13 at 22:25
  • Yeah, a service 'heavy up' would also be a good option here. – Tim Post Dec 08 '15 at 06:09
  • I think you have the wrong terminology, a multi wire branch circuit is 2 circuits that share a neutral. Also the panel needs to be rated for tandem breakers for them to be code compliant. – Ed Beal Nov 17 '17 at 20:29
13

The only reason to replace the entire box is if aesthetics: if there isn't enough room on the wall for two boxes, or the box is in a closet or cabinet where there isn't physical space.

Putting in a new breaker box is much easier than replacing an entire box. If you replace the entire box, you will need to rewire every breaker. When the original box was wired there was lots of slack on each wire, but after each breaker was installed the wires would have been trimmed. A good electrician will allow slack in the wires for reconfiguring breakers, etc. but if it's a small box you may not have enough wire, or you may end up running the wires in ways that aren't as neat or professional as it should be.

With a new box, on the other hand, you only need to remove one 220V or two adjacent 110V breakers. The old wires can be run into a junction box to provide as much length as you need for wiring into the new box.

As Mike Sherov noted, you need to be sure that your service can handle the load and number of circuits. That'll be a location specific code issue. If the knob-and-tube wiring was recently replaced I'd be surprised if the old service (probably 50 or 60 amp) wasn't upgraded as part of that process (likely to 150 or 200 amps).

If your new circuits are within the capacity of your service and local regulations permit, this is a job you can do yourself. If you choose to do it yourself, in some jurisdictions you can ask the inspector if your plan will keep you in code, to save the cost of a consultation with an electrician. (In some places of course, they're too busy for such questions.) Or you can research it yourself: it's not difficult if you have access to a code book.

Rod Fitzsimmons Frey
  • 2,652
  • 16
  • 23
  • 1
    Excellent point about wire slack. Sadly, whoever rewired the house left very little slack in any of the lines. It's been a total pain in the ass every time I've had to splice into an existing circuit. It sounds like adding a second box is the best way to go. If I go that route, are there more power limitations on the second box? – bengineerd Jul 22 '10 at 19:12
  • 1
    @bengineerd: the sub-panel will have its own limitations, and it's also limited by the size of breaker in the main box used to run the sub-panel. Common sizes for sub-panels are 40A and 60A. Obviously adding a 60A sub-panel doesn't mean you have an extra 60A capacity on the house, you're still limited by the service coming in. – gregmac Jul 23 '10 at 02:12
  • You can use a 100 amp sub panel and feed it with a 40, 60, 80 or 100 amp breaker from the main using a larger sub would provide for more spaces and not run into the current problem again as long as the main panel can handle the additional load. – Ed Beal Feb 08 '19 at 15:52
3

It really depends on how many breakers you intend on adding and what level of service you're already getting. Most of the time, the number of circuits in your breaker box corresponds to the level of service you're getting.

Personally, I'd recommend getting an electrician for this to calculate your energy needs.

However, if you know you have adequate power, and you're only interested in adding one or two circuits, you can use piggy back breakers to split the space normally reserved for one breaker into two.

As always, make sure you're using parts that are specified as appropriate by the manufacturer.

Mike Sherov
  • 1,469
  • 7
  • 22
  • 26
1

Assuming your service can accommodate the additional circuit(s), you can install tandem circuit breakers to replace your 15amp circuits - basically two breakers siamesed into a single breaker form factor. If you replaced all your singled up breakers with tandems that should plenty of space to add in any extra circuits allowed by code. That's really the only way you can get additional circuits into your breaker box short of replacing the entire service.

Tandem Breaker

kkeilman
  • 3,431
  • 1
  • 19
  • 17
-1

I believe that it is against NEC Code to install a tandem breaker in an electrical panel code says you can not exceed the number of poles that a panel was designed to accommodate like a 30 circuit panel with 2 stacked or tandem breakers makes it using 32 poles as each single breaker is 1 pole and a double breaker is 2 poles so if the panel is full and you put in a tandem breaker in place of 1 normal breaker you are adding 1 more pole than the panel was designed for I know I can not get away with that on a new construction panel it would fail inspection not saying that as a home owner you can't do it just saying it is against code for an electrician to do it

  • Hello, and welcome to Stack Exchange. There's good information in your answer, but it's hard to read. You might consider editing it to add a few periods. – Daniel Griscom Dec 06 '15 at 12:29
  • 1) Code applies to *everyone*, not just licensed electricians. 2) Tandem capable panels will account for this in their panel rating (a type BR, for instance, will be listed and diagrammed as say, a 16/32 slot panel indicating it can take 16 full width breakers or 32 circuits worth of tandem/quadruplex breakers). – ThreePhaseEel Dec 08 '15 at 00:52
-3

If your panel is loaded to capacity then chances are you need a service upgrade. Sub panels are the cheap shorcut and will only cause more stress on your main circuit breaker, and when that goes you could be looking at an emergency service change which will be BIG bucks.

  • 1
    This couldn't be more wrong. If you add up the breakers in any panel, the amperage will likely exceed the service size. Sub panels don't themselves cause stress on the main circuit breaker. Assuming load is properly factored, there is no reason you would need an emergency service upgrade. – Steven Jan 23 '14 at 00:15