I have a saltwater dock that extends 625 feet from shoreline with an elevated junction box at the dock entrance, which is located an additional 175 feet from the dock entrance to the main panel of my house.
I plan to completely renovate the house including the house electrical system in a couple of years. I want to wire the dock so that eventually I have 240 volts for a 12.8 amp load for dual 1 HP motors for a future mechanical electric 10,000 pound capacity boat lift. I also want to have 120 volts to receptacles for various small electrical appliances, a ceiling fan, and lights on the dock.
I would like to wait on installing the boat lift until the house has been renovated, but would like to have available the 120 volts for outlets, fan, and lights now. I want to run the final wiring down the 625 foot dock to the elevated junction box at this time rather than later to reduce the cost. I am anticipating needing a sub panel at the far end of the dock.
Using the Southwire calculator, I calculate a 4 AWG cable for the 800 foot run (625' + 175') with a 15 amp breaker at the sub panel with less than a 3% voltage loss. If I use the 80% rule for load on a single circuit, this bumps the amperage to 16 amps and the Southwire Calculator recommends a 3 AWG cable to keep the loss at less than 3%. I understand that having a much greater voltage drop significantly shortens the life of the motors, which are about $500 each and difficult to replace, but I understand that the cost of much larger wire is significant as well. I plan to place a separate grounding rod installed in the soil at the entrance to the dock and plan to use copper wiring for the project to avoid corrosion problems.
Specific Questions:
Would 6 AWG 3 wire with ground cable be adequate or should I use 4 AWG 3 wire with ground cable or even a 3 AWG 3 wire with ground cable for the 625 feet dock run at this time anticipating the future boat lift?
Can I temporarily run 10/2 AWG with ground cable for the 175 feet from the house to the junction box at the dock entrance in order to have 120 volt outlets and lights on the dock now if I use the larger 6 AWG cable, or 4 AWG cable, or even 3 AWG cable for the 625 foot dock run? Or would a 12/2 AWG cable from the house be adequate for the temporary run if I use LED lighting, a small ceiling fan, and limit the wattage of the small appliances?
I plan to have an electrician install the sub box and make hook-up to the house main panel, but is there anything in particular that you would recommend about the wiring or breakers in the sub panel which would provide the 240 volt circuits for the 2 motors and provide 120 volt circuit for the outlets, fan, and lights in a manner to avoid any imbalance in the electrical circuit?
Lastly, will code allow me to run a water line in the same trench as the temporary electrical line from the house as long as I keep the water and the electrical line 12 inches apart? If I use an electrical PVC conduit for the temporary electrical line, can the water and power be placed only 6 inches apart?