15

I just purchased a band saw and I have the option of running it at 120 V or, by opening the cover on the motor and swapping around a couple of wires, running it at 240 V.

In general, I understand that running it on 240 V is "better", but what are the actual advantages that make it "better"?

NOTE: I'm building a new shop to put it in, so I'll be able to (and am actually planning to) run a couple of 240 V circuits with several receptacles per circuit, so that is not a concern for me at this time.

Peter Mortensen
  • 303
  • 2
  • 8
FreeMan
  • 37,897
  • 15
  • 71
  • 155
  • 4
    OK, some unsolicited advice (which is always dangerous (LOL)), but 2 things: 1) Go big on your panel (and or-sub-panel) When I build out my shop (attached to my house, even though it was a sub-panel in the shop I went with a 42 space 200 amp panel, feed by 125 amp circuit from the house's main panel. 2) I have found that shops are constantly evolving with new tools , changes in layout etc. So to future proof my shop I went with Wiremold 4000 raceways connected directly to the main sub-panel...which also provides a good ground path. This may seem like over-kill in your situation. – George Anderson Apr 29 '23 at 20:58
  • 2
    ..., a bit more: While it may seem like over-kill, large panels are not expensive, but a total PITA to change out later. and while product recommendations are OT here, I'm going to bend the rules a bit and attach a link to the product I used: http://www.wiremoldproducts.com/catalog/dept_id_1417.htm?sid=C0C06BCE374586523884F4ED64C63F76&pid=1228 – George Anderson Apr 29 '23 at 21:00
  • Too late, @GeorgeAnderson. I've already got a 40/40 panel installed in addition to a new meter main and the fully stuffed 26 space panel that the house came with. ;) Not only will the new panel pick up all the new circuits for the 2 new construction projects, but I'll be adding (much needed) additional circuits for the kitchen and other areas of the house. One step ahead of you, my friend! – FreeMan Apr 30 '23 at 11:14
  • 1
    Tim Allen's character on Tool Time (Home Improvement) would have loved this! – JosephDoggie May 01 '23 at 12:49
  • I would have thought the main advantage is not having to drag a step-down transformer with you everywhere you go. But many building sites use 120V for reduced shock hazard in wet environments. – Toby Speight May 01 '23 at 16:18
  • Not sure how that impacts a stationary tool in a new-construction wood shop, @TobySpeight... – FreeMan May 01 '23 at 18:17
  • 1
    @GeorgeAnderson Note that asking for product recommendations is what is not allowed; giving them as supplementary information is allowed, unless it is spam (you get some kickbacks or advertising fees) – user253751 May 02 '23 at 22:20
  • The wire will be thinner and lighter. – Hot Licks May 03 '23 at 00:21

7 Answers7

20

As alread mentioned by others, Half the current, which makes 1/4 the resistive losses (if the wire was the same size, which it probably won't be.)

The more subtle follow-on effect is that what resistive losses there are, particularly the ones that bite you on startup surges, will be half the percentage of the overall voltage. Resulting observation - starts easier, less prone to stalling. Likewise, less resistive heating in the motor windings means it will run cooler.

Basically, unless you need to drag the saw around to sites where a convenient source of 240V isn't something you can depend on, there's no reason to wire it 120V. If it lives in your shop, that does not apply, because you'll have convenient sources of 240V there.

Ecnerwal
  • 174,759
  • 9
  • 212
  • 440
  • 1
    When I've heard/read advice to use 240 for table saws, the reason given was that it was less likely to bind up and shoot the piece you are cutting back at you. That would fall under 'stalling', right? – JimmyJames May 02 '23 at 20:26
  • actually they would be 1/4 the percent of the overall voltage – user253751 May 02 '23 at 22:21
17

IMHO it's always better to run at 240v than 120 if possible. For one thing you can run smaller, less expensive wire and get the same amount of power.

Next, even if you keep the same wire size for 120v you get a LOT less voltage drop from the panel to the tool. I have a hobby wood shop with a table saw, band saw, jointer, compressor, dust collector, planer and drum sander. All of them run at 240v.

Next, next (LOL) running everything possible at 240v puts virtually no load on the neutral, which I feel is a good thing.

So my humble advice is to run everything possible at 240v.

George Anderson
  • 22,321
  • 3
  • 31
  • 76
12

You get around the 1500 watt limit. 120V plug-in appliances won't get UL approved if they take more than 1500 watts (or 1800 watts in rare cases). In fact drawing more than 1800 watts will trip a 15A breaker.

With 240V, you have a 3000 watt practical limit and a 3600 watt hard max. That's twice as much. At half the current, the breaker is far less likely to "nuisance trip".

In a 3-phase shop, it's easier to balance the panel. Many shops in 3-phase country are wired 120/240V "wild-leg delta" - which looks like normal split-phase, but with a third phase 208V away from neutral and 240V away from the other hots. However, 120V loads all wind up on the same phase, which annoys the power company and they may charge you for the phase imbalance. Going 240V lets you plug the saw into the other phases.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
  • 1
    The 1500 watt limit is already in play here, is it not? This saw can be (and is currently) configured to run on a 120v circuit and, therefore, is subject to all the _design_ limitations of a 120v circuit, no? – FreeMan Apr 30 '23 at 11:15
  • re: "1500 watt limit", does that mean that, e.g., plug-in electric kettles are all limited to 1500W? – njzk2 Apr 30 '23 at 12:22
  • 7
    @njzk2 yes, which is [why Americans don’t use electric kettles](https://youtu.be/_yMMTVVJI4c)! – Jacob Krall Apr 30 '23 at 14:23
  • 3
    @Jacob +1 for linking a Technology Connections video. It's the "mouse-drawn red arrow" of DIY stackexchange! (the real reason is, we don't drink a lot of tea... we have Mountain Dew :) – Harper - Reinstate Monica Apr 30 '23 at 21:51
  • @Freeman depends what's happening inside that jumper box. – Harper - Reinstate Monica Apr 30 '23 at 21:51
  • Would you expand on that please? I'd like to learn... – FreeMan May 01 '23 at 15:11
  • @FreeMan I really don't know - AC motor design is witchcraft, and even Thomas Edison couldn't figure it out, and Tesla gave up trying to explain it, hence their fallout. Jumpering the thing to 240V *could* include additional windings that would allow it to pull more current on 240V, for instance. – Harper - Reinstate Monica May 01 '23 at 19:46
  • Ah, I see. Sorta... :) Thank you that does make some sense, then. I just assumed that the motor was the motor was the motor and never thought about a possibility like that. – FreeMan May 02 '23 at 14:49
5

Depending on the exact implementation of the 120/240 wiring of the motor, the benefits of 240 range from small ones like

  • energy efficiency gain (2-5%),
  • less light dimming on motor startup,
  • less interference with the other appliances (you don't want your old-ish workshop computer restarting each time you turn on this tool, do you?)

... all the way to e.g. twice the usable power of the tool. Yes, the motor has its power rating and also yes, its practical performance depends a lot on the power fed to it.

As a proud citizen of a 240-only country I always noted how hesitant and sluggish are 120V motors and how careful people need to be when plugging multiple appliances into a single circuit.

Go 240 whenever you are sure you won't need to plug the same thing in a 120-only place.

fraxinus
  • 2,821
  • 5
  • 11
  • 1
    if you do need to plug it in a 120-only place occasionally, of course you can just change the jumpers again – user253751 May 02 '23 at 22:24
3

The 240 volt wiring will use half the current as the 120 volt wiring so maybe it will be a reduction in the wire size since these saws can have large motors. 240 volt wiring is "better" because it automatically balances the loading in the panel when you have many 240 volt appliances hooked up.

JACK
  • 72,186
  • 15
  • 68
  • 170
2

It will be more efficient. For the same amount of power your current will be half as much. There will be less energy loss due to resistive heating. Also running at 240v you will have more torque and it will perform better under heavy load.

JD74
  • 1,305
  • 2
  • 10
0

Does your tool use a switchmode PSU ?

Many data centers make both 208V and 220V available in customer racks. Switchmode power supplies are slightly more efficient at higher voltages, with the difference being 1-3%.
Source https://www.servethehome.com/120v-208v-power-consumption/

There is also slightly less heat produced, and therefore less cooling power is needed.

This saving can also apply to computers and devices at home, though 3% of the power cost for one computer is a few cents a month, and will likely never repay the cost of running a 240V circuit and outlet and breaker. For bitcoin miners though, it does add up.

US homes might have a 240V drier and hot water cylinder because these are high-power-usage devices. 2% saving there is worth it.

Criggie
  • 9,262
  • 1
  • 21
  • 58
  • 1
    For the dryer and water heater wire size is a factor too. 240v 30A 10 AWG dryer would be 120V 60A 6 AWG. Wouldn't matter for me - my dryer receptacle is attached to the side of my panel. But if it is in another room the wire cost is important. – manassehkatz-Moving 2 Codidact May 02 '23 at 04:24
  • 1
    I don't think my bandsaw has a PSU beyond "receptacle on the wall". – FreeMan May 02 '23 at 14:50
  • @FreeMan sounds like my bandsaw - a wall plug, a switch, and a mains voltage AC motor. Nothing fancy. The motor's name plate might have wattage info that could be relevant here ? – Criggie May 02 '23 at 21:47
  • 1
    I don't think *any* bandsaws have switch-mode PSUs. That sounds like a programmer-centric idea :) – user253751 May 02 '23 at 22:24
  • @user253751 "efficiency-centric" perhaps ? – Criggie May 02 '23 at 23:42
  • no, programmer-centric. Everything must be a computer. Because Stack Exchange springs from Stack Overflow it has a lot of users who are programmers – user253751 May 03 '23 at 00:31
  • @user253751 I couldn't code my way out of a paper bag. So theres zero chance this answer is programmer-centric. Datacenter bias perhaps, or just efficiency. – Criggie May 03 '23 at 01:05
  • very well then - assuming everything has a SMPS is datacenter bias – user253751 May 03 '23 at 01:09