I'm installing a 24V DC low voltage under-cabinet lighting system in my new kitchen. I had electricians run some 18AWG runs before the drywall went up from under every top kitchen cabinet, all terminating in one central location (under the kitchen sink). They also put another j-box in that central location with some 14/2 romex (120VAC) to power the transformer itself.
I've managed to get it working by pulling out the individual 14/2 conductors and terminating them inside the transformer. But obviously I know I can't leave unprotected conductors in the air under a kitchen sink, so I need to figure out a way to protect them between the j-box and the transformer.
I'm also bonding the 7x 18AWG cables for all the separate lighting runs together using WAGO 221s, but since there are so many of them I don't have space to do this in the tiny compartment inside the transformer, so I have to join them outside and just get pigtails into the transformer itself. I'm guessing I also can't (and don't want to) leave these exposed in the air, but I'm not sure how to protect low voltage wiring between transformer and j-box.
(Note: I've only bonded 3 of the low voltage runs in this picture)
My questions:
- What is an acceptable way to protect the 14/2 Romex here? Should I wrap it in metal flex conduit? If so, how can I terminate this on both the wall j-box side and the transformer side?
- Same question but for the 18AWG low voltage wiring. The main difference there is that the "bonding" of all the wires is done outside the transformer, though perhaps I can push those into the low voltage in-wall box and only run / protect the pigtail into the transformer.
My transformer has 3/8" knockouts btw
Update for future readers: I ended going with a mix of Ecnerwal's solution (for the low voltage) and Harper / jay613's (for the high voltage). This let me avoid conduit or Flex / MC cable altogether which was a win!
As Harper said I couldn't find 8-port wire nuts, and my big box store didn't have the 8-port push in connectors, so I just used 2 5-port wago's with a pigtail between them. I pushed them all in the wall and added a single 18/2 cable coming out into the power supply.
I also couldn't find a grounding bushing for 1/2" (my home depot only has those for 1.5" and up), so I drilled a hole in the extension box and screwed in a green 10-32 screw with a bare wire, nutted to the ground from the panel.