I installed this 100 amp Homeline panel. I realized after I installed it that I hadn’t grounded the box. As seen in the picture I have two 120V hots and a neutral. I’m not sure if I can use the neutral as a ground or if I need to install a dedicated ground.

100 amp homeline box

isherwood
  • 119,766
  • 7
  • 148
  • 349
Brock Neill
  • 449
  • 1
  • 7
  • Your metal conduit _may_ provide a ground path. See the linked duplicates for more on that. If so, you may need to bond your neutral bus bars so that they're also grounded. – isherwood Mar 13 '23 at 18:23
  • 1
    Yes, you need a dedicated ground path that is separated and isolated from the neutral wire. The shell of non-flexible metal conduit will suffice. Grounds must be kept isolated from neutral. (the only exception is a pre-2008 subpanel which was wired with neutral-ground combined, or "Protective Earth And Neutral" as the British call it. [Terrible idea, that](https://www.youtube.com/watch?v=JRHyqouJPzE). – Harper - Reinstate Monica Mar 13 '23 at 19:41
  • According to [other posts](https://www.diychatroom.com/threads/do-i-have-to-put-in-a-ground-wire-for-this-hundred-amp-box.749163), this is a subpanel. – Harper - Reinstate Monica Mar 14 '23 at 21:35