I am installing a new branch circuit for an electric range (current range is gas). The only difference between this and all the other electrical work I've done is this will be the first time I've used Al wire in a residential branch circuit. I just need a quick sanity check to make sure I am doing everything correctly before I proceed.
- Breaker is a Square D HOM240
- Wire is Al (brand new 2022-manufactured AA-8000) 6-6-6-6 SER
- Recept is a Utilitech NEMA 14-50R
- Load calc already done and I have verified that I'm OK adding the load to this panel
The terminals on both recept and breaker are rated Al/Cu and 75C so I have no qualms about that. I own (and use) a torque driver, so no qualms there either. The wire is 90C (derating to 75C still allows #6 for 40A), so I am good there.
The one thing I'm unsure of and need the sanity check on is the use of grease/paste. I keep reading that you need to use antioxidant paste on Al wire connections, but does that apply to this situation as well, or is that just for the old stuff and dissimilar metal connections?