Trying to install my new ecobee SmartThermostat. Furnace is a Trane heat pump, 20 years old from when the house was built.
When I looked at the existing thermostat, it has RGWY.

So I thought I needed to install the PEK. I went up into the attic and found a wire nutted snarl. Someone probably assumed no one would ever have to look at their work ♂️
Anyway, it looks to me like the blue comes from the control box and is tied together with the white wire going to the thermostat, two white wires going back to the control box, and the wire running to the actual furnace.
I added the labels. If I’m correct here, then what I actually have at the thermostat is GRCY. Does this make sense? Will this work if I use that white wire as C and have no W?
Oh, I also measured the voltage between R and W/C, and it read 28 VAC.
Thanks for the help
Update:
Here is the wiring diagram and control box wiring:
Plus the heater wiring and diagram:

I pulled the rest of the wire out of the wall and the 4 wires tied back in the furnace are clipped off here, so I could theoretically do some rewriting if necessary.
Update 2: Unwrapping the tape
It looks like they have the blue/C jumpered to the white/W using a capacitor.. Weird. I can’t think of any reason they would do that.. Maybe using it as a fuse? I’m so confused, lol
So I think I’m going to take the capacitor out, connect my thermostat C wire to the blue/C going to the AC, leave the white/W without the jumper. Thoughts? Should I leave it in?
Thanks again!