I feel as though I have a pretty good handle on wiring strategies - well, I did until I came across this today. What in the world am I looking at??
To provide some context, this dual gang switch supports a fan with light kit and it is a part of a circuit that also has outlets on it. As you may be able to see, there are 3 wires entering the box.
- 1 hot and 1 neutral are tied into the first switch
- the switches are tied together
- 1 hot from second switch exits the box
- 2 neutrals are tied together with a ground?!?!
- the 3rd hot is effectively tape-spliced to the hot entering the first switch
Honestly, I have no clue what's going on here. Unless anyone has a suggestion, my thinking is to pull it all apart and at least figure out which wire is line, but even then, I'm not sure how the fan switching is wired up here since if you assume that there's a wire for line and a continuation for the outlets, that leaves only 1 x 14/2 going to the fan - which makes me believe that line may be coming from the fan and then continuing on to the outlets.
Any thoughts or suggestions for testing and correcting?
UPDATE: As was mentioned in the answers, here's what was going on.
- somebody decided to "fix the glitch" with regard to wanting separate switches for the fan and light - and having only 1 x 14/2 cable running from the box to the fan - by using the white and black wires for the 2 hot leads and then using the ground for a common neutral (that's why it's wired that way)
- there are 2 other 14/2 cables coming into the box - 1 was the line from the box (I verified this by taking everything apart, turning on the power, and seeing what was hot) - the other served outlet loads in the room.
- that tape...it's just as bad as you might imagine. I've added a picture for dramatic effect.
For now, I've at least got everything connected with proper connectors. This weekend, I'm going to replace the fan with a 2 wire (no light kit) and will run a new 14/2 leg for some recessed lights. Oh, and the box - definitely replacing the box.