Context - I'm in Indiana (USA) replacing my existing gas cooktop with an induction cooktop.
My existing setup has 6 gauge wire running from the panel with a 60a breaker to a stove with a 7.2kW rating.
My new induction cooktop has a 9.6kW rating.
Based on Table 220.55 and using this calculator (http://www.electriciancalculators.com/QSEFYsecureLVNHTX/calculators/rangecal_REV1.html) I get a combined rating of 11kW. This seems fine for the 60a breaker, except 210.19(A)(3) Exception 1, which states that I can only tap from a 50 amp circuit.
This leaves me with 3 options as I see it.
- Install as is, assuming the 60a circuit also qualifies for the exception.
- Downgrade the breaker from 60a to 50a at the panel. This should still fit the 11kW load.
- Run a new circuit from the panel.
I'd prefer to do 1 if possible, but 2 should be pretty simple as well.