Background:
I'm updating an outdoor garage wall single gang electrical outlet that's 2-wire ungrounded installed perhaps 70 years ago. I only have access to the outside of the wall. My plan:
Remove existing faceplate and outlet, make sure incoming cable/wire is in satisfactory condition. Install one or two weatherproof extension rings with gaskets to provide depth, one with 1/2 inch threaded ports. Attach 1/2 inch liquidtite conduit carrying 8 gauge THHN grounding "bus" running along outside wall to port. Install weatherproof outdoor outlet shield. Install WR/TR GFCI outlet, connecting original hot/neutral and new ground wires.
Question:
What's a good robust code-compliant method to connect the 8 gauge stranded copper THHN EGC conductor to the two 12 gauge solid grounding pigtail wires in the box? Normally I would used a 3M blue/gray wire nut, but since there is an increased chance of moisture getting in there, should I use a split bolt instead, or something else?
To clarify - since these are grounds, I want to make sure the electrical connection remains solid but am not so worried about their exposure to water otherwise.
Update: I've just learned about weatherproof wire nuts, with skirts and pre-filled with (dielectric?) grease. Seems like those are a good default both mechanically and to minimize corrosion for these outdoor wet locations.