We recently installed a whole house fan that has a max current of 6.5A at 120V. Due to the dangers of whole-house fans accelerating fires, we wanted to be safe and wire in a smoke alarm relay so that if the smoke alarms go off the fan is automatically shut off.
Our smoke alarms are hardwired Kidde alarms and we found the SM120X device to perform the relay. We were able to put the smoke alarms and the whole house fan on their own 15A circuit.† The relay seemed to work the first time we turned on the fan (on the normally closed / NC wire) but the second time the fan lasted less than one second before shutting off. It appears as though the relay has been killed since the NC wire now no longer carries any current as tested with a multimeter and after having reset the entire circuit. When the relay is bypassed, the fan works fine.
Then doing more research after the fact, the problem is likely that the relay is only rated for 10A of non-inductive load and a whole house fan is a fairly large inductive load... this also fits with the fact that the second time it lasted a moment before dying since the inductive spike had some time to travel back and fry the relay.
One suggestion I read was that if the inductive load is only a "few" amps that an RC snubber (a resistor and capacitor in series placed in parallel to the load) could protect the relay. However, they did not mention what a "few" was or what size snubber.
So, what should be used to protect the relay from the inductive load?
† We made sure to install the relay in the living space (a closet) and not the unfinished attic since we noted that the documentation states "Do not exceed the temperature or humidity limits of +40°F (4.4°C) to 100°F (37.8°C) (such as in garages and unfinished attics)". So, we didn't completely ignore the manual...