I am (hopefully) getting some major electrical work done soon by a professional electrician. While it probably won't matter much (meter is only a few feet from existing panels, and new panels will be in the same location) as copper vs. aluminum cost will be minimal, I looked at local amendments (Montgomery County, MD, currently NEC 2017 but likely 2020 soon) and they currently include:
Section 310.15(B) Tables. Delete the first sentence and substitute with the following: The minimum size of conductors must be as shown in Table 310.15(B)(16) through Table 310.15(B)(19), as modified by Table 310.15(B)(1) through (B)(7), except that the minimum size of alumimum and copper-clad aluminum conductors must be No. 2. The use of aluminum conductors is limited to service entrance and feeder applications only.
(emphasis added)
Clearly, wire from meter to outside disconnect (electrician told me he has to check with the County to find out whether they are requiring that yet or not, as the County is in the process of updating code) could be aluminum. And I am pretty sure the next leg to the main panel could be aluminum. I am also pretty sure that if, for example, I had EVSE (someday...) or on-demand electric water heating (hopefully never) that I could not use aluminum wire even if all relevant components are rated for aluminum - i.e., meaningless fear.
But I am curious about feeder. Does that mean, as I think it does, that wires between the main panel and any subpanels could be aluminum, with a minimum size of 2 AWG. In other words, if I had a 60A feed to a subpanel, that could be 6 AWG copper THWN or 2 AWG aluminum but not the aluminum 3 AWG UF or aluminum 4 AWG THWN that would be allowed in other jurisdictions?