I've received some great advice on here regarding my situation, and now I believe I have a good grasp on how to proceed. I will outline my situation and proposed solution, and would love to see what anyone has to say about it! I apologize to anyone who's read my posts recently, but I'm nothing if not thorough.

I had an electrician set up service from a meter/main with a 200 amp breaker. enter image description hereFrom the lugs in this meter/main, he then ran 250kcmil Al (2 hot, 1 neutral) and 2awg Al ground 600' to a small cabin workshop with a 100 amp sub panel. 200' into the run, he installed a large pull box at the site of where I am building a garage/small apartment. He also ran conduit from this box to where a 200 amp sub panel will be in the garage.

The plan from here was to use Polaris connectors to splice each of the feeders and the ground so they both carry on to the cabin and also to the garage. enter image description hereThe 250 kcmil will then attach directly to the lugs of the 200 amp garage sub panel.

What does everyone here think of this set up? Even if it isn't your ideal design, does anyone see anything wrong with splicing the feeders in a weatherproof box, after the meter/main, to serve the two separate sub panels? Keep in mind, most of my utilities will run off gas, so no dryers or ranges.

Thanks again for any input and sorry again to anyone who's watching me tread water on this issue in the forum!

VTcabin
  • 31
  • 2

1 Answers1

1

I think you have shown the IPLD Series, which are dry location only. If below grade (and even recommended if in a NEMA 3R box) you need a IPLWB or other wet location connector.

NoSparksPlease
  • 14,833