I have a convection microwave oven that has a normal 15A 100V plug. I can only conveniently access a 20A 250V outlet, which looks like this: The outlet. (I am located in Taiwan).

Are there any safety issues with finding a way to connect them? What should I look for in an adapter?
By the way, as a layperson, how does this this kind of thing even work in theory? Is it that 20A of current comes out of the wall, and so it'd be dangerous for a 15A appliance to handle it, or is it that the the appliance draws up to 15A of current, and the wall can provide up to 20A? How does the voltage come into play?

Machavity
  • 23,184
  • 6
  • 41
  • 90
lifeformed
  • 201
  • 2
  • 4
  • 12
    The "20 A" means that receptacle can supply a maximum of 20 A. The appliance is said to "draw" current and the appliance, when working properly, draws an amount less than 20 A that it is designed to draw. The circuit will not force 20 A into the appliance that is designed to draw 10 A. However, the voltage specified is exactly what the circuit "delivers" and is not the maximum it can deliver. An appliance designed to have power delivered to it at 100 V cannot accept power delivered at 230 V. – Jim Stewart Aug 06 '21 at 09:44
  • 1
    Related (same situation, though a different perspective on the question): [Why would replacing this 240 V outlet with a 120 V outlet trip my breaker?](https://diy.stackexchange.com/questions/228080/why-would-replacing-this-240-v-outlet-with-a-120-v-outlet-trip-my-breaker) – TylerH Aug 06 '21 at 15:14
  • `How does the voltage come into play?` ... voltage is the "pressure" that forces current to flow ... increasing the applied voltage will increase the amount of current that will flow in a circuit, possibly beyond the capacity of the appliance – jsotola Aug 06 '21 at 19:53
  • Related - 100V AC is a Japanese main island standard. They also have split frequency, with half the country at 50HZ and half at 60HZ Check that your appliance can take the local AC frequency as well, before starting. Otherwise you need a replacement microwave. – Criggie Aug 07 '21 at 02:27
  • Depends on the appliance. A microwave, like the one you're thinking of using? Almost certainly not. A toaster or hairdryer? Probably. – Vikki Aug 07 '21 at 17:35
  • What it means is the 250V supply will probably blow your 100V appliance apart; the shrapnel hopefully missing your eyes. – user_1818839 Aug 07 '21 at 20:19
  • 1
    These 250V recepticles are used almost exclusively for air conditioning units in Taiwan, and unless you own the place your landlord likely won't like you changing that. I'd get an extension cord (a good quality one) – Setsu Aug 08 '21 at 06:53

6 Answers6

33

No. That is a NEMA 6-20 receptacle. Your NEMA 5-15 appliance is specifically designed to not plug into it.

Because it would destroy the appliance if you did.

That is why the system of plugs works like it does.

enter image description here

Yours is a Taiwan derivative that does not allow multi-amperage, so it does not have the T-shaped L2 phase.

Anything that plugs into the wall needs a specific voltage. The device automatically draws the right amount of amps that it needs.

Your appliance needs 100-120V. There is nothing available at this socket except 200-240V. There is no affordable way to convert the output here into what you need.

DO NOT use a common stepdown (auto)transformer! This receptacle has no access to neutral. The market is absolutely flooded with "step down (auto)transformers" which will seem to work but will place your microwave's neutral at 120V from ground, a dangerous situation.

If you want to, it's probably possible to have an electrician re-wire the circuit so the socket can be changed to what you need.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
  • 8
    "Anything that plugs into the wall needs a specific _voltage_" lacks a final _range_. For many modern devices, that range can be wide (e.g. 100-240V for the charger of my PC). For the question's 100V device, that range is much narrower, perhaps 90-110V. – fgrieu Aug 06 '21 at 17:04
  • It's too bad the IEC C13 standard didn't include notches to distinguish 120V devices and 240V devices (placing the notches to allow a 120/240 switch to be placed in the socket and allow insertion of a cord only when set correctly). Then it would have been possible to safely use a dual-voltage devices with a 240V outlet simply by getting a suitable cord. – supercat Aug 06 '21 at 18:21
  • 9
    @BlueRaja-DannyPflughoeft: In Japan, the standard voltage is nominally 100 V. A number of consumer devices (including those with large transformers like microwave ovens) are specifically designed for 100V, and seriously misbehave on 120V, especially at the high end of the tolerance. – fgrieu Aug 06 '21 at 18:23
  • 1
    What is the problem with a step down transformer? Why would neutral being at 120V create a safety hazard? – Keeley Hoek Aug 06 '21 at 19:10
  • 2
    @Keeley neutral needs to be near earth voltage in order to be safe. You can only get away with a "hot" neutral if the appliance is double insulated. Microwaves generally aren't. – Harper - Reinstate Monica Aug 06 '21 at 21:39
  • 1
    There was a time where I would have agreed simply by the plug, but I have a mass-produced device with a normal 120 plug that if I put 240 in the pins would be just fine with it. – Joshua Aug 06 '21 at 22:17
  • 1
    What you do with the stepdown transformer is you attach what you choose to be the neutral leg to the ground pin on the outlet. (This choice isn't arbitrary. It has to be the neutral leg on the microwave.) If the transformer can't do that, get a different one that can. – Joshua Aug 06 '21 at 22:27
  • 7
    @Joshua Welcome to DIY stack exchange. Your plan requires an **isolating** transformer, which is a *black swan* on the Taiwan market (and for that matter US Amazon), which is 99.9% glutted with those cheapie stepdown transformers, *which are autotransformers* and are not able to isolate. That's why I'm studiously avoiding sending OP off to buy a transformer. – Harper - Reinstate Monica Aug 06 '21 at 22:57
  • Oh my. I can't say much for Taiwan but Amazon is setting itself up for a huge lawsuit. If they so much as sell the device with a ground pin outlet that isn't ground they've doomed themselves. – Joshua Aug 06 '21 at 23:11
  • @Joshua the ground is ground. The problem is the neutral output isn't neutral. Almost all electrical equipment sold on Amazon is third-party sellers via Amazon Marketplace. Amazon claims on those sales, they are "just a platform" (like eBay) connecting buyers to sellers, even though the items ship via Prime (because the third party uses Amazon Fulfillment). The stuff doesn't even comply with US safety standards (UL, CSA etc.) so is not legal to install here. It's quite the swindle. – Harper - Reinstate Monica Aug 06 '21 at 23:28
  • 3
    A true transformer could safely allow plugging your microwave in. However, such a transformer probably costs more and weighs more than your microwave. – Loren Pechtel Aug 07 '21 at 01:47
  • 1
    @Harper “Microwaves generally aren't [double-insulated].”  Doesn't that depend on location (hence local regulations)?  Here in the UK, for example, AIUI all devices must be earthed or double-insulated. – gidds Aug 07 '21 at 10:53
  • @Harper-ReinstateMonica: Why are cheap autotransformers able to so effectively beat out cheap isolating transformers? – Vikki Aug 07 '21 at 17:33
  • 1
    @Vikki mass production/volume/economies of scale. The autotransformers are widely used by *expats* to run home-country appliances. Also, an autotransformer is doing buck-boost so it only needs half the copper. – Harper - Reinstate Monica Aug 07 '21 at 19:03
  • @gidds the key part there being "earthed or". A microwaved that is earthed (which virtually all are) would not be safe when plugged into a power supply where neutral is 120V from earth, but would be safe when plugged into a supply with no significant voltage from neutral to earth. – James_pic Aug 09 '21 at 13:34
  • @James_pic Can you explain why?  I'd naively assume that the metal frame of the microwave would be earthed but not connected to the magnetron, circuitry, or anything else with any connection to the live/neutral — which could therefore be at any offset from it.  Is that wrong? – gidds Aug 09 '21 at 20:15
  • 1
    @gidds your notion is correct ***if** everything works properly*. But you are [one layer of swiss cheese](https://www.skybrary.aero/index.php/James_Reason_HF_Model) away from critical failure. – Harper - Reinstate Monica Aug 10 '21 at 03:40
  • @Harper I count _two_ failures needed for any danger: one failure causing the case to be connected to live or neutral or something in between, and a second failure of the earthing (or circuit breaker). (Of course, this is why I'm not a professional electrician...) – gidds Aug 11 '21 at 08:10
12

At the moment NO.

You have three choices:

  1. sell that device and purchase one that is rated 230V.

  2. get a 230 to 110 transformer.

  3. replace that supply and socket with one of 110V.

Which of these is most convenient is down to your circumstances.

Solar Mike
  • 24,863
  • 2
  • 28
  • 57
  • 1
    The transformer to power a microwave will be big and heavy. And 110V might not be available in Taiwan house wiring (not sure). – user253751 Aug 06 '21 at 11:04
  • 2
    @user253751 those transformers are easily available, about 20cm by 20 cm by 30 high - usually in yellow protective boxes for use on industrial sites and rated to 3kW . I have one to power some of my woodworking tools. – Solar Mike Aug 06 '21 at 13:44
  • 2
    20x20x30cm of mostly solid metal is indeed quite big and heavy – user253751 Aug 06 '21 at 14:17
  • 1
    @user253751 so did you miss the bit about "protective box"? every handled one? has a carry handle and "normal" people can carry it with one hand... me, I can put a loop through two and still use one hand. – Solar Mike Aug 06 '21 at 14:30
  • 13
    Also, if OP attempts a search for a transformer, they have a 98% chance of finding one that is *dangerous* -- the universal red "step down transfomer" a huge number of which are actually made in Taiwan. That doesn't work to step down center-neutral 240V, because it will be trying to take neutral reference *from a phase* - moving output neutral 120V from ground. OP would need an *isolating transformer* and those are obscure enough that they won't be affordable. – Harper - Reinstate Monica Aug 06 '21 at 18:13
  • 1
    @Harper-ReinstateMonica well those 230 to 110 transformers are sold in hundreds of locations in the UK - so common and easily available and not too expensive. Here is a link : https://www.screwfix.com/p/carroll-meynell-3000va-intermittent-step-down-isolation-transformer-230v-110v/17027 – Solar Mike Aug 06 '21 at 18:22
  • 6
    @SolarMike Problem is, if you tell a person in Taiwan to go to the local shop and grab a transformer that is sold in "hundreds of locations", they won't find any of those in Taiwan. They will find PLENTY of the red ones that will kill you. Those yellow ones would work, but are unobtanium outside the UK. – Harper - Reinstate Monica Aug 06 '21 at 18:48
  • 1
    4. Plug it in somewhere else, since most of the other outlets in the house are probably suitable. – jay613 Aug 06 '21 at 19:23
  • 2
    Given the comment of @jay613, are extension cords allowed in Taiwan? Is there a 100 V receptacle near enough that you could use an extension cord? You would want one that is rated for the current that this oven draws. – Jim Stewart Aug 06 '21 at 21:23
  • @SolarMike I'm amazed the price is that low. There's a lot of copper in there! – Loren Pechtel Aug 07 '21 at 01:49
4

The other answers are all correct, you cannot, but they don't address your question of how this works in theory, so I'll take a stab at it.

You can think of voltage sort of like water pressure, and amperage sort of like the velocity of water flowing. Right now in that socket is 250V worth of pressure. Since nothing is connected, no amps are flowing. That 20A is the max amount of amount of flow the socket can support till things in the socket start breaking.

Your microwave is only rated for 100V of pressure, so if you hooked it up to the 250V, it'd be like hooking a garden hose to a fire hydrant: the pressure would be too much and it burst, probably allowing no current through, though it might allowing unrestricted amps until it exceeds 20A worth of flow and the breaker would trip.

The 15A on your mircowave means that it is guaranteed to allow 15A or less to flow under normal voltage and operation. Most devices work sort of like a valve, when off allowing no amps to flow, and under different conditions allow more or less amps to flow. Generally, as long as the amps required by a device is less than the max allowed by your power source, you're fine.

This is all governed by Ohm's law, which if you google you can find far better examples, explanations and analogies than I could come up with.

yesennes
  • 263
  • 1
  • 2
  • 7
  • Having the receptacle's max ratings embossed on the FRONT seems unwise. Likely to cause confusion such as this to naive end users, and not likely to help electricians by being on the front. I wonder if Taiwanese Panasonic 100V receptacles also have "250V" embossed on the front? Or if in fact they are manufactured differently and are rated for 100V? – jay613 Aug 06 '21 at 16:37
1

In addition to the good accepted answer, please note 2 things:

First:
the ratings of the outlet socket and plug cable are not the most important deciding factors. What's more important is the actual voltage supplied to the socket, and the actual voltage range accepted by the appliance. If a socket is rated at 250V, you could actually have either 220V or 110V wiring connected inside it, so if you have a way to measure it, you might find the voltage to be suitable for the device after all. (But be careful, it could cause serious injury or death if you make a mistake while doing it).
As for the appliance, if it's fitted with a 100V cable, it usually does not accept 220V, but you should not get that information from the cable itself. The machine should have a nameplate similar to the image blow, that tells you what voltage and frequency it accepts.

enter image description here

Second:
Most countries that have 200 to 240 V outlets (like Europe) operate at an AC frequency of 50 Hz, and most outlets that provide 100 to 120 V usually have an AC frequency of 60 Hz (like North America).

According to Wikipedia, Taiwan has both 110 V and 220 V residential voltages, and both operate at 60 Hz, so the frequency should not be an issue of you (but the voltage definitely is).

But for readers in other countries, it is not recommended to use a microwave designed for one frequency in a country that has the other. One reason is that the timer clocks in some microwaves depend in the frequency to count the cooking time. Using the wrong frequency can cause the clock to run faster or slower than it should.
In other words, when you cook for 5 minutes it actually stays for 6, or the other way around.

Amin Dodin
  • 111
  • 3
1

If the outlet is supplying 230V, you cannot connect a device rated for 120V without bad things happening; the device would almost certainly be destroyed, and very likely start a fire.

The 20A rating on the circuit is the most current it can safely deliver to a load; if a load draws more than the rated limit, excess heat will build up in the circuit's wiring which could start a fire. The circuit should have protection against this in the form of a fuse or circuit breaker which should trip before any damage occurs in the circuit. In the context of your question, that's 20A.

The 15A rating on the appliance indicates the peak load it could impose on a circuit; in other words, if the circuit can't deliver at least 15A, you'll probably trip a circuit breaker or blow a fuse if you try to use the appliance.

You can connect a 15A appliance to a 20A circuit, with caveats. There is no issue with doing so for any appliance in good working order. A properly engineered appliance should have internal circuit protection so that any internal fault should trigger the internal protection and not rely on the external circuit for over-current protection. If it's a cheaply-made appliance, it might not have such internal protection, so connecting it to a circuit with a very generous current rating could be risky, but then it could be risky connecting a cheaply-made appliance to any circuit.

Anthony X
  • 1,319
  • 10
  • 16
-11

VERY DANGEROUS, but you could in theory connect the 110 hot lead to 1 hot side of the 220, and the 110 neutral to the 220 ground, and leave the 110 ground unconnected" but now the chassis will be floating and there will be current on the ground--BOTH VERY BAD! DON"T DO IT.

  • Aside from the trivial side-effect of killing the operator, this is also almost guaranteed to cause a ground-fault trip on your DB. Unless your whole building does not bother with ground-fault detection, in which case.... How are you still alive? – PcMan Aug 08 '21 at 15:29