Are there any special requirements I should be aware of before adding lights and outlets to my covered back patio? I know GFCI protection will be required on the outlets, but can I run regular Romex cable over soffit? It's an open air, concrete patio and wood post construction with typical soffit ceiling.

There is an empty outlet box installed on the far right of the porch, about 15-18 inches off the ground. I would like to use that, and add a second outlet closer to the french doors via conduit and THHN.

I don't have a picture of the porch itself, but it can be seen behind the playground. The ceiling material is the vinyl soffit, which I thought to be typical for porches and patios.

ad

FreeMan
  • 37,897
  • 15
  • 71
  • 155
clwhoops44
  • 348
  • 1
  • 3
  • 13
  • 1
    You'll want to either A) Use a GFCI _breaker_, or B) Use a GFCI outlet _inside_ and put all the patio devices on the LOAD side of the outlet. While outdoor GFCI outlets are made, even when installed in water-tight boxes, the elements are pretty harsh on them and they require more frequent replacing, and they're a bit spendy to have to replace them more often rather than less often. – FreeMan Jun 25 '20 at 12:56
  • I'm not too familiar with patio roofs that have a soffit ceiling, so I'm not sure this qualifies as "typical". Can you post an overall shot of the patio/roof, then a couple of detail shots of the soffit where you're planning on running the wiring. Also, indicate where you're planning on putting the outlets. They're probably not going up in the soffit, so there will be extra considerations for them. – FreeMan Jun 25 '20 at 13:21
  • I do not think this is a duplicate the op said there was a porch and the construction had soffit type construction the answer you linked was not the same. If the porch had a plastic roof it would not be allowed! So much different. – Ed Beal Jun 25 '20 at 13:50
  • Not at all what I was envisioning - the pic makes things so much more clear, thank you! (Nice playground, BTW!) – FreeMan Jun 25 '20 at 14:03
  • I'll reiterate the unanswered question: Where are the outlets going to go? The cabling requirements _may_ change based on the outlet locations. For example at/near the base of the posts vs in the soffit or at the top of the posts. – FreeMan Jun 25 '20 at 14:07
  • @FreeMan after seeing the pic, do you believe that romex is acceptable for the lighting? There is an empty outlet box installed on the far right of the porch, about 15-18 inches off the ground. I would like to use that, and add a second outlet closer to the french doors via conduit and THHN. – clwhoops44 Jun 25 '20 at 14:10
  • I would leave that to @EdBeal or one of the other electricians to answer. I know there are differences, but I don't know the details. BTW- Romex™ is a brand name, NM-B is the standard type of cable used for _indoor_ or protected wiring. Romex has become "genericized" like Kleenex has, but neither `Romex` nor `NM-B` are suitable substitute terms for `THHN`! – FreeMan Jun 25 '20 at 14:21
  • The receptacles would need to be in the “dry” area up under the roof, in this case a receptacle could not be low on the post as that is a damp location, Romex /nm cable would require conduit for protection below 8’ but cannot be used there because conduit would be a wet location there code gets kind of crazy UF can be used in conduit but 3/4” is needed to prevent damaging the covering. This is how I do the ones in my barn a box up in the dry area, connecting to a piece of conduit to a bell box using UF cable (UF is underground feeder) and rated for wet locations a in use or extreme duty cover – Ed Beal Jun 25 '20 at 14:29
  • I'm sorry, I'm not doing a great job painting this picture. The outlets will be mounted ON the house, 8 feet away from the posts and completely covered by the roof. I would like to install two separate outlet boxes, connected via conduit and THHN. I would like to use Romex (NM-B, I suppose) only for the lighting. I just wanted to make sure there were no special code requirements for covered outdoor areas that I should be aware of. – clwhoops44 Jun 25 '20 at 14:32
  • I ran out of room with the last comment And then noticed your comment on the box 18” from the ground , feeding from a low point use UF cable in conduit below 8’ once up in the eve you no longer need the conduit. But you could do it that way my answer was guessing a new circuit run up in the open eves. Nice playground I agree. You can use any wiring method , I use whatever I have when using conduit thhn or left over UF my barn has 6 or 8 receptacle drops and probably 50/50 because I had some left over from a job so I used it up. – Ed Beal Jun 25 '20 at 14:36
  • 1
    @FreeMan and Ed Beal thank you both. We just put it up for the kids this past weekend. About 25 work hours with my dad and grandfather's help. Glad it's finished lol – clwhoops44 Jun 25 '20 at 14:43
  • @EdBeal maybe edit that info into your answer to make it easier to digest instead of having to piece it together from several comments. – FreeMan Jun 25 '20 at 15:00
  • @clwhoops44 It would help if you would put this info in your question instead of leaving it in the comments. It makes it much easier for others to find. Also, 3 generations working together on the playground is awesome! – FreeMan Jun 25 '20 at 15:00
  • If it's a soffit ceiling, I'd think it'd be just like running wire in your attic. – Huesmann Jun 25 '20 at 15:09

1 Answers1

3

Code considers areas normally dry to be ok for nm cable 334.10. Under your roof is one of those locations that is not subject to dampness or wetness. Some jurisdictions consider a porch to be a damp location. It usually depends on the roof type. For example, a normal 3 tab roof with tarpaper is considered a dry location, but a roof with corrugated plastic and even metal if not insulated is a damp location.

If you use a GFCI in this location, it needs to be WR weather rated, as the electronics are coated to protect them from moisture. They cannot be located above 5'7", but they can be used to protect the load side.

I would think as long as above 8', exposed romex or NM cable would be allowed by your description of the soffits & normal roofing.

Updating because of change to thhn;

Where damp or wet, THHN /THWN cable (almost all thhn is dual rated but thwn is the wet rating) needs to be used. Your circuit will need to be in conduit box to box. 1/2" will be fine for your setup. All wiring methods below 8' require protection, but THHN requires conduit from start to finish.

The reason most home owners use UF and NM wiring methods is because 12&14 gauge circuits with thhn requires 3 different colors: hot usually black, neutral usually white, and ground usually green. (Hot can be any color other than gray, white, green. Neutral can be white or gray, ground can be green or bare).

Home owners usually use pvc conduit as it is easy to cut and glue. From your box, there can not be more than 360 degrees in bends or 4 90's. Wire pulls get tough after 3. If you need more than 360, a conduit body is normally installed. I use a conduit body at a 90 in many cases, called an LB, LR, or LL (the hole being back, right, or left). There are also form C bodies that are inline. A box can also be used.

The one thing I see home owners do wrong in most cases is the wrong kind of box. Outside, a bell box or weatherproof box is required unless recessed in the building structure.

The pvc conduit needs a strap within 3' from the box and supports per table 352.30 1/2"-1" max space 3'.

These are the additional things to think about, but they should get you on your way to a safe install of your lights and receptacles.

Stephen S
  • 187
  • 1
  • 6
Ed Beal
  • 101,306
  • 4
  • 72
  • 150
  • Aren't standard GFCI's WR??? + – JACK Jun 25 '20 at 13:57
  • I'm pretty sure I've seen _some_ GFCIs specifically labeled "WR" and they were priced higher than others, @JACK, so... probably not. – FreeMan Jun 25 '20 at 14:05
  • No freeman is correct WR rated gfci’s are special for outside use but I also use them in bathrooms where humidity is higher they last longer because the electronics are coated / potted to prevent moisture problems. – Ed Beal Jun 25 '20 at 14:16
  • 1
    I wasn't aware of that but then I always installed the GFCI's inside and daisy chained the outside outlets to it. – JACK Jun 25 '20 at 14:24