32

I have noticed that when I touch the water of my Hot Tub when I am grounded (barefoot standing outside of tub) I am getting a very small electric shock. Using a multimeter it is reading 2Vac between the water and the ground outside.

I have an RCD on both my ring main and a dedicated RCD on the Hot Tub, none of which trip.

Now the odd thing is that even with the socket switched off (but still plugged in) it still reads 2Vac. If I unplug the socket it reads 0Vac.

How is it reading 2Vac with only neural and earth wires connected?

Lee
  • 579
  • 1
  • 4
  • 7
  • 35
    If you google "hot tub electrical shock deaths" there are lots of articles. You should stop trying to troubleshoot this and go hire a proper electrician. – scorpdaddy Jun 28 '19 at 15:37
  • 9
    Basically neutral is not zero... So, you need to get this checked, and sorted, quickly. Waiting for you to find it eventually may injure someone... – Solar Mike Jun 28 '19 at 16:08
  • 7
    Look closely at the RCDs. Do they have a trip rating? Typical numbers are 6ma, 8ma or 30ma. Also, RCDs are not the be-all-end-all fixer of all defects electrical. – Harper - Reinstate Monica Jun 28 '19 at 16:12
  • 1
    US GFCI normally have a TEST button. No idea if your RCD does. But if it does, does the TEST button work as expected? – manassehkatz-Moving 2 Codidact Jun 28 '19 at 16:20
  • 4
    This question could do with a country tag, because earthing arrangements are different in different countries. – Andrew Leach Jun 29 '19 at 06:43

8 Answers8

48

Edit: This is sounding more and more like a problem with either a neighbor's electrical or the utility's supply. See last entry.

DON'T get in that hot tub again!

The "very small" shock was due to high impedance between you and the current. Impedance is extremely luck-based. Someone getting out of the pool might splash water where it had not been before, now the impedance is much lower and that "small" shock puts you in a wheelchair.

Hot tub miswiring is so common it's legendary. RCDs do not protect you from all wiring errors.

Don't get in the hot tub again until you positively find the cause and remove it.

8ma vs 30ma protection

RCDs also do not protect you from shock, necessarily. In Europe, RCDs have been used for a long time, and for a different reason - protecting houses from fires, not protecting humans from shock. Also, since they use whole-house RCDs, they must use a higher (more permissive) threshold, otherwise small leaks from many appliances will "stack" to cause nuisance trips. So whole-house protection is typically 30ma threshold.

Whereas in the US, GFCI is specifically for human safety, and it is 6ma or 8ma. This is too sensitive for a whole house, so it is applied circuit by circuit on circuits where it is helpful. (near sinks).

Your whole-house RCD would need to be 30ma, which is not enough for life-safety protection. It's less likely to outright kill you, but it's plenty enough to stun you - and when you are in water, being stunned means drowning.

Your hot tub should indeed have its own RCD, at the 6-8ma sensitivity level. However if you walk into a store and buy any random RCD, it's quite possible you'll find yourself holding a 30ma one. Perhaps your hot tub installer did exactly that.

RCDs do fail

I.E. they stop properly detecting ground faults. That's why the device has a "TEST" button. Use it.

It may be miswired to bypass the RCD

In fact, this is likely if the hot tub installer hit a situation where the RCD tripped when he hooked it up correctly. The RCD would trip when hooked up correctly, if the hot tub had a ground fault. Typical installer move is to jury-rig it any method that will work, then get paid.

This can also happen with amateur installers. They typically refuse to learn how to do the job properly (because that takes time learning about subjects they just don't care about), and simply "try random combinations" until one works. Many will work and also kill you. This might be one of those.

If the hot tub has a ground fault, fix it - seriously

Sometimes RCDs trip because the downline device is connected correctly, but actually does have a ground fault. This tends to surprise the heck out of people, they are in full disbelief -- "MY appliance has a ground fault? This cannot be!" (even they know nothing about ground faults).

I've seen people replace RCDs twice simply because they cannot believe they actually have a ground fault. And of course they feel totally justified in bypassing safety protection altogether.

So don't be in denial about that. There is a real possibility that the hot tub has a ground fault. If so, fix it.

It might not even be the hot tub

There's an outside chance this shock is entirely unrelated to the hot tub. It's possible the dangerous voltage is being sourced from some other thing in your yard, and the hot tub is correctly providing grounding, thus completing the circuit. If so, the cure is a thorough search of your house's electrical system for any defects. And if neighbors are close, you may need to bring out someone to test for problems coming from them.

In any case, this is nothing to trifle with.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
  • 1
    Thank you for the reply. The Hot Tub is actually the inflatable type, the heater/pump unit has the RCD hard wired about 10cm from the plug, it's sensitivity is 10mA cut off. I contacted the manufacture who told me: "the pump includes a grounding system, which is double insulated and links all of the electrical parts of the pump directly to the grounding of the electrical system of the house (known as a class I electrical product). The spa therefore relies on the earthing arrangements that you have in the property (and the electrical socket you are using) are up to the required standard." – Lee Jun 28 '19 at 16:58
  • 9
    @Lee ***Oh dear.*** Then it's possible the shock has nothing to do with the hot tub, and you could sell the hot tub, and be standing in your backyard and get shocked. – Harper - Reinstate Monica Jun 28 '19 at 17:36
  • 9
    They are, either through ignorance or lawyers, mixing up grounding and ground fault protection. Bottom line is that when water is involved (a) a little problem can become deadly and (b) double insulation only helps until a nick in the insulation let's water get to where it shouldn't. Listen to Harper. – manassehkatz-Moving 2 Codidact Jun 28 '19 at 17:39
  • So I am assuming there is some sort of earth fault in my house since I get a shock from the pool when I put the RCD on test and switched it off at the socket - so earth wire must be carrying the voltage? Is there any way I can test with a multimeter? I have now unplugged the hot tub and will get someone to check out my house wiring – Lee Jun 28 '19 at 18:06
  • 3
    if I test the voltage between the Earth coming into my house (the supplier side of the meter outside) and ground (actually sticking the probe into the soil), it is reading 2Vac as well. Not sure that is the right way to test...... – Lee Jun 28 '19 at 18:11
  • Soil doesn't conduct well so that doesn't tell you much. – manassehkatz-Moving 2 Codidact Jun 28 '19 at 18:18
  • @manassehkatz: modern multimeters have very high input impedance. Much higher than the resistance of a human body. (As Harper points out, a random fluke could lower the resistance enough to make it still dangerous if there is an actual high voltage source, but my point here is that you should be able to measure that voltage with a meter if there's anything. Unless the ground is normally forming a voltage divider but might sometimes not be.) – Peter Cordes Jun 28 '19 at 23:51
  • 1
    Could the OP possibly have a floating ground or neutral? Possibly even from the utility? – le3th4x0rbot Jun 29 '19 at 00:51
  • 2
    @trognanders I'd be more inclined to suspect that the utility has a stray current issue if it's not an issue in the premises wiring. a floating neutral would cause all sorts of *other* havoc besides this, anyway. – ThreePhaseEel Jun 29 '19 at 05:04
  • 1
    @ThreePhaseEel Not a completely floating neutral, but the connection to the earth has a high resistance and there's stray current from somewhere (could even be inside his house.) – Loren Pechtel Jun 29 '19 at 05:21
  • 1
    @LorenPechtel -- ah, excessive ground resistance + stray current could definitely cause that. (When someone says "floating neutral", I think of a neutral that's somehow no longer hooked up to the utility) – ThreePhaseEel Jun 29 '19 at 05:39
  • 2
    @ThreePhaseEel I think you maybe correct, it does sound like https://en.wikipedia.org/wiki/Stray_voltage#Persons – Lee Jun 29 '19 at 18:22
  • 12
    I was electric shocked by touching a non-electric shower. Turned out the shower was well earthed. The **floor** was live because water leaked through to inadequately earthed trunking underneath. GET A PROFESSIONAL TO FIND AND FIX THE FAULT! – user20637 Jun 29 '19 at 20:07
  • 2
    Is there any place online where one could learn all these things? I don't want to become a certified electrician, but I find the subject interesting, and I do small repairs/installations in my own home from time to time, so I'm quite interested in learning to do it _properly_. – Vilx- Jun 30 '19 at 09:53
  • 1
    Just to +1 the utility idea: I had a friend who was being shocked by fittings in his parents bathroom one weekend: - the utility had reversed the live and ground in the substation just up the street. – Chris Becke Jun 30 '19 at 15:41
  • 1
    @Vilx- just hang around here long enough lol. I'm glad you don't want to become a certified tech, electrician is not a "study and take the state exam" thing, you have to apprentice for 5 years, that is your day job. – Harper - Reinstate Monica Jun 21 '20 at 14:59
15

I had an electrician to check out the problem and:

  1. I am in the UK and there is only live and neutral at the meter (earth and neutral are the same wire at that point)
  2. The Hot Tub water is directly conncted to Earth
  3. The mains electrics in my property all checked out fine, incoming supply fine.
  4. No faults with the Hob Tub
  5. RCD's tested and working
  6. He is surpirsed I can even feel 2Vac, he could not feel it.

So it's still a bit of a mystery, but if I stand near the Hot Tub (off and unpluggedd) and measure voltage between the ground (the actual soil) and the Earth wire, it reads 5Vac, no current. If I switch off ALL power (break live and neutral) at the meter I still get the 5Vac Anyway, the Hot Tub is safe to use.

Lee
  • 579
  • 1
  • 4
  • 7
  • This sounds like an issue with faulty utility wiring introducing a stray current into the earth... – ThreePhaseEel Jun 29 '19 at 17:14
  • 3
    this is what I am thinking: https://en.wikipedia.org/wiki/Stray_voltage#Persons – Lee Jun 29 '19 at 17:59
  • Yeah, you're on the right track, I'm pretty sure; fixing it will require talking with the utility, though. – ThreePhaseEel Jun 29 '19 at 19:28
  • 3
    It's not surprising to have a potential difference between true (literal) ground and the neutral wire of a circuit with a high current flowing through it. The reason is that the neutral wire's resistance is non-negligible with high currents, so a potential difference between different locations *on the same "neutral" wire* (and between those locations and "true" ground) develops. That's one reason houses have several distinct circuits and care is taken to balance loads among those circuits instead of putting all lights on one and all heaters on the other. – Peter - Reinstate Monica Jun 30 '19 at 13:48
  • The soil, has high impedance and may therefore try to pass a fixed current from whatever the source is. The voltage read by your voltmeter is correct, but may depend on the impedance of the voltmeter. If you use a voltmeter with 10 times the impedance, you may find that the soil still wants to pass the same amount of current, so the high impedance voltmeter reads 10 higher. If your voltmeter is cheap, your body impedance may be higher than the voltmeter! Also, if soil was wetter on the day you got the shock than the day your electrician visited, that could explain why he couldn't feel anything – Level River St Jun 30 '19 at 22:51
  • @Lee just to be sure of this. When you say "shocked" do you mean like a static shock from touching a doorknob, or a more persistent feeling? – Stack Tracer Jun 30 '19 at 23:56
  • 7
    Another tale from the UK. One day my father tried to turn on the tap in his bathroom, and got a bad shock. He called the power company, who could find nothing wrong. Sure enough, he could now touch the tap without getting shocked. Then it happened again days later - and again the power company could find no fault. It turned out his neighbour 100m away had hung a painting on a wall; the nail had hit the wire to a light-switch, and connected the live wire to the earth wire, which meant that the earth wire and everything connected to it was now live - but only when that light was turned on! – Gary McGill Jul 01 '19 at 10:42
  • 3
    @GaryMcGill How does the breaker not trip when earth is connected to live, forming a short circuit? – clemisch Jul 01 '19 at 13:30
  • @clemisch: My father lives on an old farm property where steel nails are considered a more-reliable, longer-lasting substitute for fuse-wire. :-) [I'm not sure whether it's possible that the "earth" wire wasn't properly grounded? So it found a better path to "ground" via my father...] – Gary McGill Jul 01 '19 at 13:34
  • 1
    @clemisch Maybe the earth wire was also disconnected. – user253751 Feb 20 '20 at 13:53
3

Now the odd thing is that even with the socket switched off (but still plugged in) it still reads 2Vac. If I unplug the socket it reads 0Vac.

How is it reading 2Vac with only neural and earth wires connected?

By ground wire not being at 0Vac.

Typically this would be caused by problems elsewhere in your home, such as an appliance drawing high amount of current and your ground rod making poor contact with the ground. It could also be poor connections in the ground wires themselves.

If you want to test it yourself, you can do the ground voltage measurements from various outlets and also turn appliances on/off. If your house has all the grounds connected together well, they'll probably all read the same voltage. In that case, the problem is likely with the central grounding rod.

jpa
  • 1,275
  • 7
  • 11
2

Its an inherent fault that's apparent on our UK TNCS supply type. Our earth (your hot tubs earth and its water) is always at the same protentional as your neutral, which is nearly always above Zero. You access this via the water in the tub and touch true earth (zero volts) via wet grass a you will get a shock IMO they should not be installed using this system ...period

Brian
  • 21
  • 1
0

enter image description here

I got an electric shock whilst in a Lay-Z-Spa Vegas.

It was leaking from the thermostat housing, with water leaking and dripping on the heater causing a short to travel through the water pipe.

I took the top of the thermostat housing and found the square rubber seal split. I used silicone caulk to repair the seal and refitted it.

No more leaks, no more shocks. Happy spa days!

Niall C.
  • 20,709
  • 17
  • 90
  • 131
  • 2
    No more *for now*. You really, *really, **really*** need to have that spa on a GFCI breaker (or outlet if it plugs in). Seriously. The shock you experienced ***should not have been possible***. What you had there was a "single point of failure" (one thing broke, lethal situation created). We don't like those in electrical. Is grounding also proper? Look at that too, but GFCI first! – Harper - Reinstate Monica Jun 21 '20 at 15:03
0

I now use foam mats underneath and all around the hot tub to mitigate the risk of an earth fault. In fact my neighbour had a fault on the incoming cable (under her garden) which caused a small fire in an applicance, scottish power were all over it, never seen so many turn up at once. TNCS is just a bad idea to save money on copper.

Lee
  • 579
  • 1
  • 4
  • 7
  • While insulating foam/rubber mats sound like a great idea, I wouldn't count on them for 100% safety. What happens if someone splashes water on the mat and the water runs to the edge and connects with the ground? – FreeMan Jan 31 '22 at 17:18
0

I am actually experiencing same thing right now. it has been tested by electricians to confirm. i am getting 3.5-4v ac from earth ground to hottub water even with my main disconnect at meter off. same v measure from earth ground to steel siding. hydro will be doing some testing feb 2/22 but they said if its under 10v then that is within the standards and nothing will be done it is just how their system works. location ontario canada - Getting voltage readings from a hottub doesnt always mean its coming from the hottub. I have put rubber mats all around the tub to ensure no shock from situation happening.

jason
  • 1
  • 1
  • 2
    While I believe this answers the question (10v or less is within standards), it could use an [edit] to improve formatting and remove some of the narrative. It's hard to find that answer, and I almost flagged it for deletion. Also, it's important to note _where_ you are as standards vary around the world. – FreeMan Jan 26 '22 at 17:27
  • As it’s currently written, your answer is unclear. Please [edit] to add additional details that will help others understand how this addresses the question asked. You can find more information on how to write good answers [in the help center](/help/how-to-answer). – Community Jan 31 '22 at 14:31
  • While insulating foam/rubber mats sound like a great idea, I wouldn't count on them for 100% safety. What happens if someone splashes water on the mat and the water runs to the edge and connects with the ground? – FreeMan Jan 31 '22 at 17:19
-1

I experienced the same problem. Our jacuzzi is standing on artificial grass. So when the pump of the jacuzzi is working , the jacuzzi generates some electrical current in the water. Just like a car that is generatong current from headwind. When you get out of the car you get a electric shock. The current in the water is very small but accumulates. If the jacuzzi is not grounded the current becomes stronger and you can feel small shocks when you are standing barefoot near the jacuzzi and touch the water. So the grounding of your wall socket will prevent build up of static current caused by pump flow / static generation.

  • This does not really answer the question. If you have a different question, you can ask it by clicking [Ask Question](https://diy.stackexchange.com/questions/ask). To get notified when this question gets new answers, you can [follow this question](https://meta.stackexchange.com/q/345661). Once you have enough [reputation](https://diy.stackexchange.com/help/whats-reputation), you can also [add a bounty](https://diy.stackexchange.com/help/privileges/set-bounties) to draw more attention to this question. - [From Review](/review/late-answers/154372) – gnicko Dec 26 '22 at 04:37
  • Current doesn't accumulate. Yes, static electricity is pretty much harmless but I don't think the asker is talking about static electricity. – user253751 Mar 02 '23 at 18:08