I will be installing a Tesla wall charger in the garage and have a few questions about the codes and such. It will have a 100 amp breaker and it will be pulling 80 amps for 2-6 hours at a time so with that in mind I am rating my wire as "constant load".

I will be installing it about 2ft from the breaker box and will run the wires partly in the wall and partly in front of the Sheetrock. Now I believe the codes call for all wiring to be in some sort of conduit when inside the wall. Can I just use that blue plastic stuff for that portion? And for the run outside the wall what is the rules for that?

Also because it would be a million times easier is there a way to go through the stud? I mean I guess I could pull off the sheetrock cut a hole and replace it. Bear in mind it's a garage and the walls are unpainted or anything just plain siding. Also if it was to stay in the wall I could easily pull it through the back of the charger just like an outlet box.

The image is a rough sketch of what I'm planning on doing.

enter image description here

isherwood
  • 119,766
  • 7
  • 148
  • 349
rasmukri
  • 129
  • 1
  • 7
  • Question about [wire size for 100 amp service](https://diy.stackexchange.com/a/29077/43874), has some good info on the wire part of this project. – JPhi1618 Mar 18 '19 at 17:44
  • Keep in mind with wires that large, you will have **turning radius** issues with the wires, and that will be a limiting factor. As such, though I usually disrecommend this, I advise using **copper** conductors, because they will be smaller and allow a tighter bending radius. The distance is very short so the cost won't beat you up too bad. – Harper - Reinstate Monica Mar 18 '19 at 17:44
  • Are you sure about 80/100 A? According to [Tesla Wall Connector](https://www.tesla.com/support/home-charging-installation/wall-connector) it seems that for a single charger the practical max is 48/60 A and you can only take advantage of more power if you install multiple connectors to charge 2 cars at once. – manassehkatz-Moving 2 Codidact Mar 18 '19 at 17:45
  • 1
    I have a 2014 model with dual chargers and I get the full use of the High Power wall charger. I'm all good on that stuff but good looking out for newer models they only do 72 amps. I already have some 4awg copper wire lying around the house so I plan on using that – rasmukri Mar 18 '19 at 17:48
  • Does your charger need 120v and 240v power (three wires + ground) or just 240v power (2 wires + ground) ? – JPhi1618 Mar 18 '19 at 17:50
  • 1
    240v 2 hot and ground. No neutral line – rasmukri Mar 18 '19 at 17:51
  • I don't follow the diagram. Isn't it the case that the wires coming out of the electrical panel will be inside the wall cavity all the way to a listed box where connection to the Tesla cable will made. If the connection is "hard wired", then the Tesla cable will go into the box through a plate with a hole in it. Alternatively, could there be a receptacle in the wall box and the Tesla charger plug into that? Maybe the current is so large that there is no receptacle/plug combination which is suitable and approved? – Jim Stewart Mar 18 '19 at 18:14
  • Yes there is a connection inside the charger box the wires connect to. My concern is getting the wires to there the easiest, cheapest, right way and up to any building codes. All I need is help on what is the best way to get from point A to point B that is safe. – rasmukri Mar 18 '19 at 18:54
  • So your electrical panel is flush with the inside wall of the garage and there is drywall on the wall? I have wondered how people easily add circuits with that arrangement. Does one have to cut and repair drywall to add a circuit? The outside wall of my garage has no drywall so it was easy for me to add circuits and add a surge protector. Of course, a patch in drywall in a garage wouldn't have to be extremely well executed. – Jim Stewart Mar 18 '19 at 19:07
  • 4AWG Cu is the wrong size. The problem is it's only rated for 70A. – Harper - Reinstate Monica Mar 18 '19 at 23:25
  • What *type* of wire is this 4AWG you are planning to use? – ThreePhaseEel Mar 19 '19 at 22:52
  • The blue tubing "ENT or Smurf tube" cannot be used where subject to damage per NEC 362.12.8 , in 1 county I work in they allow it in places that have semi permanent appliances like behind a washer and dryer, the other 2 county's say only above 8' exposed because of this reference. So it would be good to check, in those locations I usually use schedule 80 pvc. – Ed Beal Mar 19 '19 at 23:28
  • Ok so this will be installed in Douglas county NV, I have also decided to change the install location. There is a main breaker box outside I will be hooking it up to instead as the sub panel inside because it is kinda full for my liking. the run will be about 100ft and will be about 20ft outside before making its way into the attic and then coming down the wall. Also I will be using 2 awg hot and 8 awg ground both THHN wire. So outside I'll use PVC and the attic prob PVC also as it'll be easier to keep it all the same. – rasmukri Mar 20 '19 at 16:55

2 Answers2

1

With a normal cable, you'd use the same rules as NM

The normal cable for this job would be a type SER (Service Entrance, Reinforced) cable. While a typical SER cable for a 100A circuit would use 1AWG aluminum wires with a 3AWG aluminum ground, the Tesla charger is incompatible with aluminum wire, so you'll need to use a copper SER cable with 3AWG wires and a 5AWG ground instead. Anyway, because this is a SE cable, we look to NEC 338.10(B)(4) for the rules:

(4) Installation Methods for Branch Circuits and Feeders.

(a) Interior Installations. In addition to the provisions of this article, Type SE service-entrance cable used for interior wiring shall comply with the installation requirements of Part II of Article 334, excluding 334.80.

As a result, we follow the same rules as NM cable when installing this stuff, including the use of nail plates to protect it when it runs through notches or holes in studs, unless those holes are more than 1.25" from the edge of the stud, as per NEC 300.4.

ThreePhaseEel
  • 79,142
  • 28
  • 127
  • 220
  • Because it's a 100A circuit, I'd use a nail plate on the stud no matter where the hole was drilled. – dabi Mar 19 '19 at 05:22
0

Not sure with high amp circuits. Normal 15 and 20A circuits need to be protected from a nail skewering the wire where it passes through a hole in a stud. OR they must be some minimum distance from the edge of the stud. You can protect by conduit, or by putting a metal plate over that part of the stud. This allows a 1/2" hole in the stud with clearance on either side.

You may want to run separate wires for this reason. It will also be easier to bend around corners. This also prevents a stray nail from shorting two conductors, and spreads the I2R heating from being as concentrated. Given that in a garage, larger nails are likely to be pounded into a wall, there is a case for paranoia. Really don't want a 120v nail head in the room.

Surface wire has to be safe from casual damage, up to a certain height above the floor surface. (Door height? May vary by jurisdiction) You can use cladded wire or conduit.

In principle this allows you to fasten wire casually to the ceiling run down part of the wall, then run the rest of the way down in conduit. Looks like hell. But you know where your wires are.

Check your local codes. I'm in Canada so our codes will differ, and I'm not current on code even here.

My suspicion is that we are going to see a raft of code revisions over chargers. Few other things use so much power for extended periods of time. Could make a case for de-rating the conductors, and requiring the next size up.

I would talk to your electrical building inspector and ask what he would pass.

Sherwood Botsford
  • 3,348
  • 16
  • 37
  • Yeah I've heard about doing that with the metal plate to normal small wires. But wasn't sure about if it was still acceptable for large wires like the 4 AWG I'm gonna use. Also I'm doing this work in Nevada so there is prob not too many crazy local codes. – rasmukri Mar 18 '19 at 21:13
  • The hole would require a nail plate if closer than 1-1/4" from the face of the stud. As someone else mentioned on a big run like that I might want to use a plate in a garage. – Ed Beal Mar 19 '19 at 23:15