I have a 40amps range breaker. I want to upgrade it to 50amps. I know that the wires need to support 50amps if I want to upgrade it to 50amps. However, I am not able to figure out whether the wires support 50amps. How would I find out whether the wires support 50amps? Here is
the image of 40amps circuit breaker that I want to upgrade.
Asked
Active
Viewed 52 times
0
Peeyush Kumar
- 103
- 2
-
Do these wires go off into a *cable*, or a *conduit*? – ThreePhaseEel Feb 18 '19 at 23:32
-
Can you get a picture of any markings on the wires or the cable sheath the wires are coming out of? – Harper - Reinstate Monica Feb 19 '19 at 05:12
1 Answers
3
You need a number 6 wire. The picture looks like 8. It's written on the wire. Following AWG _
Joe Fala
- 6,254
- 8
- 34
-
-
-
Just wanted to know what the rating of the cook top is. Most cook tops are 40 amp max anyway. The max rating isn't a suggestion it's a requirement. It's to protect the unit in case of fault. – Joe Fala Feb 19 '19 at 01:48