My main elect panel in the house has a common neutral/ground bar and not separate bars. If I run from this panel to a sub panel in a detached pole barn and attach the two hots for 240V and one neutral that is connected to the neutral/ground combination bar in the main panel, am I grounded properly? Would I also need a ground rod in the pole barn and if so, does it get connected to the neutral bar or is it grounded to the sub panel itself?
Asked
Active
Viewed 2,414 times
1 Answers
1
Larry, I can relay what is required in our area. For each and every premise now is allowed one service panel only; thus requiring only three wires to feed. All other panel on the premise are required to be fed, for the sake of safety, with four wires. These include two wires as phase conductors, one neutral and one ground. Additionally, all panels that are located in a separate building require ground rods, no longer just one ground rod but two separated by 6'. In the service panel the neutral and grounding all come together at the neutral bus bar. The subsequent panels must have all neutrals and grounds separated. Good Luck; PCL
Paul Logan
- 6,835
- 1
- 10
- 15
-
At this point, I am totally confused. Some people say the ground in the sub panel must be disconnected from the neutral. If I only have 3 wires from the main panel to the sub panel, two hots and one neutral, why would I detach the ground bar from the neutral and how does the sub panel get case grounded. Does the sub panel case need to be tied to the neutral since most people say that a separate ground rod is not adequate. I also have seen some comments from people who say the you need to have a 4 wire system with ground between the main panel and the sub panel as well as a ground rod. – Larry Dec 17 '18 at 20:13