3

I want to install a timer switch (it has four wires, red (load), black (hot), white (common), green (ground) to replace one switch in a 2-gang switch box having five incoming cables (see first photo). One switch controls the fan (want to replace with timer), the other switch (3 way) turns on the recessed ceiling lights. I made a diagram and attached pictures.

Which of the two common pigtails will I tie the switch common wire to? Also can someone confirm that my black hot wire ties into the black pigtail? And that I create a new pigtail to tie the red source for the switch to the black of cable #5? Any help would be appreciated. Thanksenter image description here

Peter B
  • 33
  • 3
  • Hello, and welcome to Stack Exchange. First, nice diagram! Second, that light switch does seem to be a three-way; is there a second three-way switch for controlling the lights, and how do you plan to handle it? – Daniel Griscom Dec 02 '18 at 19:52
  • Hi Daniel, thank you for your comment. Yes there is a second three way switch for the lights on the other side of the (long / narrow) bathroom. So I don't plan on doing anything there, just with the fan switch. – Peter B Dec 02 '18 at 20:06

2 Answers2

2

First, let's label these cables:

Please confirm that this is correct:

  1. Incoming power
  2. Travelers to 2nd 3-way switch
  3. Always on - receptacles? lights in other rooms?
  4. Either incoming power to 3-way switched lights or switched hot to 3-way switched lights
  5. Fan

Note that if this diagram is correct, the power and neutral for the 3-way switched recessed lights is separate from everything else. That is perfectly fine, but you need to keep it separate.

Replacing the fan switch

"Top"/"Bottom"/"Left"/"Right" are to be ignored when it comes to old switch vs. new switch because each manufacturer (and even each model within a manufacturer) does things differently. In your particular case, the new timer/switch has colored wires so that makes it easy:

  • Black wire on top of old switch is hot. This connects to hot/black on the new switch.
  • Black wire on bottom of old switch is switched hot. This wire, black from cable 5, connects to load/red on the new switch.
  • White wire on new switch should be connected together with the 3 white wires that you show near cable 5 - connected to 1, 3 and 5.
  • Ground/green should be connected together with all other grounds. Typically you will have a bare ground wire coming out of each cable if these are typical NM (aka Romex) cables. If you do not see any bare wires and it is a metal box and the wires are coming through metal conduit (which may be hard to tell unless you have some other part of the wall open) then the ground is the metal conduit. If that's the case, you can connect the timer/switch ground/green wire to the metal box using an appropriate screw.
  • Thank you Manassehkatz. Yes, the cable labeling is correct. So if I understand the 1st two bullets of your response correctly: the black/hot of the new switch connects to the bundled pigtail of black/hots and the load/red of the new switch gets pigtailed with the black on cable 5. yes? – Peter B Dec 02 '18 at 20:29
  • the black/hot of the new switch connects to the bundled pigtail of black/hots and the load/red of the new switch gets pigtailed with the black on cable 5. yes? – Peter B Dec 02 '18 at 20:30
  • Correct - black to bundled hot, red to 5 black. – manassehkatz-Moving 2 Codidact Dec 02 '18 at 20:31
  • great, I will put it together in the morning and let you know how it goes. thank you – Peter B Dec 02 '18 at 20:37
1

Real easy.

There's a rule that says "currents must be equal in every cable" and it follows "you must use the neutral partnered with your hot".

First. Look at the wires on the switch you want a neutral for. (They're all black here).

Second. Follow them back to the cables in which they enter the box. Looks to me like cables 1, 3 and 5, most clearly 5.

Third. Look at the white wires in those cables, as these are candidates. Where do they go?

Lo and behold, all 3 cables' white wires converge at one wirenut. Done!

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671