I want to install a 100 Amp panel to my attached garage. The location is about 50-60' from my service panel, which is 200 amp utility service. The purpose of this circuit is for a small pottery kiln and circuits for things like a table saw, miter saw, drill press, misc. small things and new lighting.

The kiln draws single phase 240 @~27-35 amps, recommended a 50 amp breaker using a standard 6-50 receptacle.

The workshop will be probably 2-3 20 amp circuits and a 15 for the lights. There will also be a 20 amp circuit dedicated to ventilation—the fan load is so far < 5 amps, just don't want to limit it.

After a lot of looking around and researching it seems like the best option is to put in a full real panel like this one: enter image description here which should give plenty of expansion room and additional safety and other options.

My plan is to bury conduit from my main house panel to feed this new breaker panel in the garage. Looking into these options and the desire to save money given the price of cable it seems like 1-1-1-3 SER Aluminum cable could fit my needs and should fit in 2" Schedule 40 conduit. SER is not allowed to be buried even in conduit

The problem is when trying to verify this I find a whole lot of arguments but not enough solid code reference as to whether SER cable can be buried in conduit (raceways?). Yup this is not to code, cable must be rated for wet locations to be buried apparently.

While I do want to save money, this has to pass inspection so that is my primary concern. Seems like if SER is not allowed to be put in buried conduit I need to use THHN or perhaps better XHHW? I have worked with aluminum wire before just at much lower gauge so not too worried about being able to handle it. (I will be pulling a permit for doing this).

Questions about cable run:

  • What is the proper type of cable for this run in conduit? SER, USE, THHN, XHHW, XHHW-2? Figured out it should be THWN-2 Not sure of an AL alternative yet though Will be using XHHW-2 CU, found a legit online source.
  • Can I do this with aluminum wire without having issues later?
  • My primary goal is 100 amp and I doubt I'll need more than that in the garage so it doesn't need to be overbuilt too much.
  • From my research, do I need to bury the conduit at least 18 inches?

For the garage panel I know that since they are not within sight range or reach of each other I must install a main breaker in the garage panel to shut its power off but I had some additional questions there.

  • I plan to feed the run from 2 50 amp breakers in the main panel; is this accurate/necessary? Okay, so this was wrong: Changing to single 100 amp breaker. Even checked my notes again and I had this right so derp on this, lol
  • Should I also put in some kind of service disconnect before the sub panel in the garage for any reason?

My locale is the U.S. and my city has adopted the following:

  • 2015 International Residential Code (IRC)
  • 2015 International Building Code (IBC)
  • 2014 National Electric Code (NEC)
  • 2015 International Plumbing Code (IPC)
  • 2015 International Mechanical Code (IMC)
  • 2015 International Fuel Gas Code (IFGC)
  • 2015 International Energy Conservation Code (IECC)
  • 2015 International Swimming Pool and Spa Code (ISPSC)
  • ​2015 International Existing Building Code (IEBC)
  • 2009 ANSI (As referenced in the 2009 International Building Code)

I tried to provide as much information as I could but let me know if more details/clarification is needed. Thanks for the help!

OCPik4chu
  • 110
  • 2
  • 9
  • 1
    "2 50A breakers"? you mean paralleled? don't do that. You will need to use a proper 100A breaker in the main panel. Also consider adding some 240V circuits to the workshop. They are pretty handy. – ratchet freak Jun 21 '17 at 15:16
  • You can power two subpanels off two 50A breakers, but separate wires to each obviously, and if you then have all 8 wires in a single conduit, don't forget your 30% derate. You can also power a 50A subpanel and run a separate 50A circuit *just* to the kiln. I mention that because 100A breakers are *considerably* more than 50A. – Harper - Reinstate Monica Jun 21 '17 at 15:28
  • @ratchetfreak oh yup, that was a derp on my part. I even had on my notes to use 100Amp breaker to feed the sub panel. So got that covered. – OCPik4chu Jun 21 '17 at 15:57
  • 1
    The linked panel is a good start, but go bigger! Bigger panels are cheap before you install them, but a PITA to upgrade later on. You may not see a need for the extra spaces now, but if you ever want to add circuits later (especially if you decide to remove the kiln) you'll be grateful. This also ties in with @ratchetfreak's suggestion of adding some 240V circuits for the wood tools, as a bigger panel will give you plenty of space for those double breakers. – mmathis Jun 21 '17 at 16:04
  • Is this a single building, or are you feeding a separate building? – Tester101 Jun 22 '17 at 13:10
  • @Tester101 Single building, attached garage. – OCPik4chu Jun 22 '17 at 14:15
  • @OCPik4chu Why would you bury cable, if you're staying in the same building? – Tester101 Jun 22 '17 at 16:33
  • @Tester101 Figured for protection and appearance. It does need to be run outside at least as I dont have good access inside to run cable like that. If I ran it in conduit against the side of my house it would also at least double the 90 degree bends too. Aside from that I know it would be a lot easier than digging a trench. Is there a limit to the number of bends that I could do in a run like this? – OCPik4chu Jun 22 '17 at 18:38
  • @OCPik4chu There's no limit to the number of bends. However, there is a limit of four ninety degree bends between pull points. These pull points must be accessible. So if you need more than four 90s, you'll need pull points. – Tester101 Jun 22 '17 at 18:43

3 Answers3

3

The type of cable you linked to is SE cable covered by Article 338 of the National Electrical Code. It connot be used underground with or without a raceway. Here is the pertinent code language.

338.12 Uses Not Permitted.

(A) Service-Entrance Cable. Service-entrance cable (SE) shall not be used under the following conditions or in the following locations:

(1) Where subject to physical damage unless protected in accordance with 230.50(B)

(2) Underground with or without a raceway

Notice item 2.

You could use several other types of insulation in a raceway, including THHN, XHHW, XHHW-2. USE is for direct burial and can be used without a raceway except where exposed to damage so you need to sleeve it in PVC or metal raceway above ground.

Aluminum also needs an anti-oxidation compound such as NOALOX or ALNOX, there are many brands.

Rigid or IMC conduit can be buried only 6" deep. Table 300.5

SE cable can be used as a feeder for interior wiring so if you kept the feeder inside the house and garage without going outside you could just protect it with PVC in the garage and be good. Or you could run the cable outside just not underground.

You will need a single 100 amp 2 pole breaker to feed the sub panel. 2 -50 amp breakers is not acceptable by the Code.

A separate disconnect is not required. The panel in the garage is not a motor so the "within-sight rule does not apply". The breaker in the main panel can act as a disconnect. You actually don't even need a main breaker in the panel if you don't want one. You can buy a Main Lug Only panel if you wish. The main only panel you linked will do just fine without a main.

Good luck and stay safe!

ArchonOSX
  • 19,642
  • 3
  • 28
  • 49
  • Ok so then sounds like my best and correct choice is one of the 3 *HH* options and while another user showed how it could be done with two 50A breakers I feel the extra cost of a 100A breaker is easily a money saver compared to running 2 full runs for the 50A so I will stick with that. I do have the NOALOX already from another project so good there. The desire for PVC + cable/wire was just for extra protection of the cable and peace of mind. I am aware there is direct-buried cable options. 6" depth is good to know, im leaning towards deeper just based on location now. Thanks! – OCPik4chu Jun 21 '17 at 17:29
  • Sounds good. One last thing, if the kiln will not operate for more than three hours it is not a continuous load. Therefore the wire and breaker can be sized just to handle the maximum current. If it only draws 35 amps you could use a 40 amp circuit breaker with #8/2 with ground copper wire. A 50 amp circuit will require #6/2 with ground. If it operates for more than 3 hours it has to be calculated at 125% of max current. Hence, the 50 amp circuit. – ArchonOSX Jun 22 '17 at 07:08
  • The kiln time can be anywhere from a couple hours to half a day so that is why I went with the 50A for continuous load. The mfr also recommends the 50A breaker for this kiln. – OCPik4chu Jun 22 '17 at 14:22
  • after some digging I found [this place](https://www.wireandcableyourway.com/XHHW/) So ill be going with the #2x3 for the H/H/N feeds and the #6 for the GND which should work out well and is a very good price compared to anything Ive been finding so far. – OCPik4chu Jun 22 '17 at 14:54
  • If you are doing a 100 amp sub panel, then #3 copper is good for 100 amps Table 310.15(B)(16) and the ground can be #8 copper for a 100 amp circuit Table 250.122. You might as well save some money where you can. – ArchonOSX Jun 22 '17 at 15:36
  • Oh yea you are right, I mixed up the #6/2 comment you made with what I was doing. Yea saves me a solid $.60/ft easily doing #3 instead of #2. Thanks – OCPik4chu Jun 22 '17 at 16:22
2

The lugs will be aluminum so aluminum wire is the best way to avoid dissimilar-metal problems.

You need to bury conduit 18" or direct-wire cable 24" unless you are using rigid conduit and not crossing driveways.

That panel is rather small

It's really only a 12-space panel, and any 240V loads will take 2 spaces. You'll run out fast. When you see "X-space >X circuit", that is a marketing lie. The only number that matters is spaces. Spaces are cheap - a common mistake in electrical is using too-small a panel, running out of spaces and having to do very expensive panel replacement, all because you decided to get a bargain on a panel. This. This is the place to splurge.

The >X circuit figure relies on double-stuff breakers, which are expensive and don't work anymore because most new circuits need GFCI or AFCI, which take a full space. And that's how a lot of people got nailed: They think "I can support 24 circuits out of this panel" only to run smack into the new GFCI and AFCI requirements on almost every circuit. Whoops!

Look for a 24-space panel. It doesn't matter what the "main" breaker is, as long as it's >100A.

Myself, I'd consider a 42-space panel. This is the place to splurge.

I also recommend getting panels that are industrial grade, Square D Homeline is a builder grade cheapie. My litmus test is industrial grade panels are also available in three-phase, and they use the same breakers for their 1-phase loads. Sanity-check their prices on GFCI breakers; for instance Eaton CH and Square D QO have excessively high prices because they use narrow 3/4" breakers.

By the way, "42 space" instead of "40 space" is the mark of an industrial panel. It's 42 because that size is a multiple of 3, and so they can use the same housing for their 3-phase panels.

Siemens is a name I hear a lot. GE's Q-line doesn't look too bad either, you have to watch out because several makers (Eaton) make both cheapies and goodies.

Conduit OR cable

Conduit and Cable are two very different wiring methods. Use one or the other. Cable is extremely stiff and awkward, and you really do not want to stuff it into conduit. That's just the kind of "stretch" project that tends to defeat homeowners and makes them give up and call an electrician. In any case that may not be your problem; read on.

If you are using proper outdoor rated underground cable such as SEU (not SE-R), you don't need conduit. If the cable goes outdoors, it needs to be outdoor listed whether it's in conduit or not. However in certain places, more protection is needed, and you can use a variety of metal shields including a stick of conduit to provide physical protection. That is not conduit as a wiring method.

If you are using conduit as a wiring method, you shouldn't use cable - it will be very hard to pull. Use individual wires, typically THWN-2 type note the W. Four individual wires can slide a bit past each other, making the whole bundle much more flexible. Still, don't be bashful about going oversize on the conduit to make the pulling easier - that way you can avoid painful defeat and the expensive electrician bill.

Do not underestimate how difficult it is to pull wires around two 90 degree bends.

Since the wire is larger than 6 AWG, you can buy just one color of wire and use tape to mark them black, red, white and green. So price both "by the foot" and an appropraite spool.

You don't need a main breaker in the sub

Since it is part of the same building. If it were in a detached structure, you would be needed. "Line of sight" doesn't apply here, it applies in factories to large machines.

That said, a local shut-off switch is nice. For a "main breaker in the subpanel", the overcurrent amp rating is irrelevant. It is only a shut-off switch, unless it also has for instance a GFCI function. If I recall, all garage general-use receptacles must be GFCI.

How to use two 50A breakers

100A breakers are much more expensive than two 50As. If you wanted to do this with two 50A breakers, there are two ways to do this, but both involve two sets of cable. You cannot parallel, at all, at these wire sizes.

  • Feed the subpanel with a 50A breaker. Feed the kiln directly off the other 50A breaker and (electrically) bypass the subpanel altogether. It's OK if the wires are routed through the subpanel, using it as a gutter, but they can't be connected to it.
  • Install two 50A subpanels. That would be a good use for those 12-space panels.

Since you would then have four conductors in the conduit (neutrals in split-phase don't count), your current limit for any conductor would be 80% of the 90 degree C ampacity. This is usually not a problem since you usually must work off a lower degree-C column.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
  • So Ive already upped my panel choice but I will def up it again, thinking [this guy](https://www.lowes.com/pd/Square-D-48-Circuit-24-Space-100-Amp-Main-Breaker-Load-Center-Value-Pack/50311147) I cant really justify the 42 space panel, plus my main panel still has iirc 8-10+ open spaces in it too. For conduit/cable thats good advice, the conduit I wanted just for extra piece of mind but Ill go with the wires over the bundle for sure. I didnt know I could just tag/pull all the same so that is good savings there. Ill go with one color for H/H/N and a green for GND. – OCPik4chu Jun 21 '17 at 18:44
  • I'll also go with a 2" conduit for ease of pulling. I was a cable monkey in a former life so I very much understand that difficulty lol. The double 50A breaker solution makes sense but sounds like I lose out on the savings of the 100A breaker by needed almost 2x the cable so ill stick with the single run of 100A. Also thanks for clarification on that 'line of sight' thing though I have heard from others about special cases, but I think I'll still double up for peace of mind (100A breaker in main to 100A breaker in garage) And yes good catch, I know the 'W' means wet so ill update my list. – OCPik4chu Jun 21 '17 at 18:55
  • Re: cable size, I should be using #1 Au for this, am I correct in that conclusion? and GND can be up to #3 or #4 Au ? – OCPik4chu Jun 21 '17 at 18:56
  • One last question, when I am looking at finding THWN/XHHW there is varying listings between allowed amperage whether wet or dry location. I'm guessing this is due to the temperature restrictions? **So #1 Al XHHW is completely usable in my situation if I am understanding these charts correctly.** (or #3 CU XHHW) Also I realize ive been typoing aluminum as AU not AL whoops. cant edit comments tho. – OCPik4chu Jun 21 '17 at 19:22
  • 1
    Yeqh I'm pretty extreme about panel spaces, it's kind of a running joke around here! Price it both ways, the 7 wires would be smaller (4Al/6Cu) than the 4 wires. [The oracle](http://www.southwire.com/support/voltage-drop-calculator.htm) is saying 1/0Al for the conductors. Be sure on your lengths, a 250' spool might be just enough for 4 wires. Versus saving on a cheaper ground but paying the higher per-foot price. Those charts are complicated and in my experience you are always stuck working out of the 60C column. – Harper - Reinstate Monica Jun 21 '17 at 22:05
  • 1
    XHHW is better at running high temp, but the issue is that does not help your terminations, which are often the limiting factor. As you can see all the smaller wires' ampacity are limited to the 60C column. https://solutions.borderstates.com/thhn-vs-xhhw-what-is-the-difference/ – Harper - Reinstate Monica Jun 21 '17 at 22:12
  • So I will be going with #3 XHHW-2 copper for the main feeds and #6 for the GND as I found a decent source for it. I did upgrade the panel to a true 24 space one. the 42 space panel was just too much panel/money for what it will be used for. Thanks for the info. Also I used that exact site when checking the difference in thhn/xhhw lol. – OCPik4chu Jun 22 '17 at 16:45
0

Just a thought that if you go with some Eaton panels the breakers are lifetime guarantee, you just walk into any electric shop with the bad one and they hand you a new one.

David Moritz
  • 652
  • 3