I am fresh out of cable staples and would rather not go all the way to Lowe's just to get a box. What are the implications of not fastening loose electrical wires to a stud? It's not like there's going to be that much vibration in my house.

Edit: This is what I am talking about.

wire clip

oscilatingcretin
  • 5,712
  • 46
  • 93
  • 113

5 Answers5

49

If you continue reading NEC 334.30 you'll come to subsection (B)...

334.30 Securing and Supporting Nonmetallic-sheathed cable shall be supported and secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (4 1⁄2 ft) and within 300 mm (12 in.) of every outlet box. junction box, cabinet, or fitting. Flat cables shall not be stapled on edge. Sections of cable protected from physical damage by raceway shall not be required to be secured within the raceway.

(A) Horizontal Runs Through Holes and Notches. In other than vertical runs, cables installed in accordance with 300.4 shall be considered to be supported and secured where such support does not exceed 1.4-m (4 1⁄2-ft) intervals and the nonmetallic-sheathed cable is securely fastened in place by an approved means within 300 mm (12 in.) of each box, cabinet, conduit body, or other nonmetallicsheathed cable termination.

FPN: See 314.17(C) for support where nonmetallic boxes are used

(B) Unsupported Cables. Nonmetallic-sheathed cable shall be permitted to be unsupported where the cable:

(1) Is fished between access points through concealed spaces in finished buildings or structures and supporting is impracticable.

(2) Is not more than 1.4 m (4 1 ⁄2 ft) from the last point of cable support to the point of connection to a luminaire or other piece of electrical equipment and the cable and point of connection are within an accessible ceiling

So if the structure is accessible, you must secure the cable. If you are fishing cable, you do not have to secure the cable. No trained mice with staplers required.

Tester101
  • 130,386
  • 77
  • 314
  • 605
  • +1 but, doesn't this cause a danger of hitting the wire when nailing/drilling into the walling? – BlueRaja - Danny Pflughoeft Aug 21 '13 at 19:09
  • 3
    @BlueRaja-DannyPflughoeft This is why you make sure you know what's in a wall, before you start nailing/drilling. – Tester101 Aug 21 '13 at 20:30
  • That is of course an insane request to make. Unless I was there when the house was built, I have no idea what's behind the walls. But I'd assume that I can nail a poster to the wall without killing myself. – BlueRaja - Danny Pflughoeft Aug 21 '13 at 23:10
  • 7
    @BlueRaja-DannyPflughoeft Unless you're using a high speed nail gun, the cable should have enough slack to move out of the way when you hang your poster. If you're cutting open the wall or doing anything else that is likely to damage the cable, you've probably already used a stud finder to locate the framing members. Most modern stud finders include a feature for finding electrical lines, so you'll probably already have a good idea that they're there. – Tester101 Aug 22 '13 at 11:56
  • 7
    @BlueRaja-DannyPflughoeft I also offer a money back guarantee on all my answers. So if you kill yourself hanging a poster because of this answer, I'll refund what you paid for the answer ;) – Tester101 Aug 22 '13 at 11:59
  • @Tester101 - Does the NM Cable have to be secured at the box when it's "unsupported"? – Alex Moore Dec 04 '13 at 18:02
  • @BlueRaja-DannyPflughoeft for existing walls, you just work carefully. If you're building a wall, you can install very helpful steel plates on top of the cable runs to protect against that very thing. – Ben Collins Jan 28 '16 at 04:09
15

Yes. It will not pass code without them.

NEC 334.30 and 314.17 Type NM (nonmetallic) cable shall be secured at intervals not exceeding 4.5 feet and within 12 inches of each box. When a single gang box 2-1/4” x 4” or smaller is used without a cable clamp, the cable shall be secured within 8” measured along the sheath.

Staples

Tester101
  • 130,386
  • 77
  • 314
  • 605
lqlarry
  • 7,557
  • 1
  • 18
  • 37
  • 12
    what if you are fishing wire through a wall? – Steven Jan 22 '12 at 03:02
  • 1
    @Steven - I've never heard of an inspector calling that. I guess electricians will have to start training mice to staple wire if the inspectors start calling it;) – lqlarry Jan 22 '12 at 03:33
  • 4
    @Steven see subsection (B)Unsupported Cables.(1) of NEC section 334.30. – Tester101 Jan 22 '12 at 18:24
  • 5
    @Steven, part of the reason for fixing the cable is so it does not get damaged when the plaster board is fixed to the wall, or over the many weeks between "first fix" and finishing the all. – Walker Jan 22 '12 at 21:33
  • @Steven That's typically why only low voltage wire is fished through a wall. Network cabling and such is considered safe to fish; however, if you hire an electrician to rewire your house, also price out a sheet rock crew. – Edwin Buck Oct 26 '14 at 17:14
  • 2
    I get annoyed at "because it's code" answers. What is the hazard? I'm not convinced that a free floating cable in a non-insulated cavity is in more danger from a drill or nail than one that is pinned to a stud. – Sherwood Botsford Jul 13 '19 at 23:16
6

The biggest problem could be if the cable moves away from the stud and you drill into the wall and nick the cable...

Depending on where you are based there could be building code/regulation violations involved as well.

ChrisF
  • 16,828
  • 5
  • 49
  • 74
2

Better safe than sorry. Unforeseen actions may occur within a wall cavity at later dates, and though it is highly unlikely that any action would occur to move or damage the cable, storm activity or remodeling may do such. Staples are cheap. Unless is it impossible to reach, secure the cable as per NEC requirements. Tidy work is quality work.