0

I would like to add an outlet in my home. I was going to do it the typical way and add a new neutral and load to an existing outlet. Run the wire to a new location and add a j-box.

The issue is the closest outlet already has 4 wires coming into it.

Can I still add the outlet by taking off of the existing outlet?

isherwood
  • 119,766
  • 7
  • 148
  • 349
Marc
  • 1
  • 1

2 Answers2

1

This is in conjunction to Harpers answer. I'm not sure but this might be what you are looking for: enter image description here

FYI the pigtail method is now required by the NEC. Try article 300.13(B). Device Removal.

When you do pigtail it make sure you have the correct size wire nut.

  • 1
    The pigtail requirement is only for the neutral, oddly enough and only for MWBC's – Kris May 02 '17 at 22:40
  • 1
    @Kris -- it's not odd when you think of what opening the neutral on a MWBC does to the voltages present there... – ThreePhaseEel May 02 '17 at 22:42
  • @ThreePhaseEel that makes good sense. I totally didn't catch that it would become a series circuit. Nice. – Kris May 03 '17 at 03:01
0

You're asking how do you attach the two extra wires when all the screws on the receptacle are in use? The question right before yours wanted to know the same exact thing and I wrote an answer here.
https://diy.stackexchange.com/a/113980/47125

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671