0

Essentially, I want to upgrade the electric service to my house from 100A to 200A (or more).

Now for the details:

1) I called my utility company and I was told by them that my meter and service allow up to 320A (which I was told here likely means 80% continuous rating for 400A service).

2) My meter and main breaker are located some distance from the subpanel with individual circuit breakers. As such, I have two boxes with circuit breakers separated by ~100ft of service wire.

3) My current main breaker is integrated with the meter. The box is rated for 125A and the installed breaker is a 100A, 2-pole breaker. See the following picture: Main Breaker Panel with Service Meter

This one details the current panel specifications: Main Breaker Panel Specifications

4) I have about 100ft of service cable going through conduit to my subpanel, which has the individual circuit breakers. I forgot to check for other wire specs (ex. THW, THWN, etc.), but I saw that it is 4GA wire on the conductor wires.

5) My subpanel is also a 125A rated subpanel. It has 8 slots for (apparently) 16 circuits. See the following picture: Subpanel Specifications

What I want to do:

1) I want to get 16 slots and ≥200A at my subpanel.

It's actually quite simple.

How I think I can do it:

1) Somehow get a total of four hot wires coming out of the main breaker box and add another 100A 2-pole main breaker to get a total of 200A.

2) Run another set of service entry wires from the additional main breaker through the conduit.

3) Install a second subpanel, identical to the first, to be serviced by this new set of wires I just ran through the conduit.

Questions I have:

1) For step 1, can I add a second main breaker that is connected to the meter through a jumper wire. Essentially, I would be adding a panel like this one (only using that product as a representation of what I intend), or do I need to replace the existing meter/main breaker panel with something like this one?

2) If I have 2 2-pole breakers or 1 4-pole breaker, can I run a new set of conductor wires without having to upgrade the existing ones? The difference is, if I replace the existing ones with 2/0 wires (for 200A), it will cost $1500. If I add new ones (protected by their own breakers on a 4-pole), it will cost $150.

3) Are the existing wires too small, since this website says that 4GA is only suitable between 70A and 95A, depending on the wire temperature rating? I'll be sad if they are too small.

4) Does it make sense to add another subpanel, or would it be better to replace the existing one with a 16+ slot subpanel?

If I am forgetting to ask something important, or if you need more info, please advise.

Thank you.

EDIT: My question was flagged as being similar to this question, which I also posted previously. This is a follow-up that details, more-specifically, a practical renovation project rather than a theoretical question regarding how breakers are built into circuits.

EDIT: Just called my utility again, and they told me something different this time. The current rep had no idea why I was told 320A last time and said they don't keep service ampacity numbers on their end. Instead, I'll just have to put in an application (because I'd be messing with the meter) and a technician will come out to talk through the project and determine what's required.

Hari
  • 2,160
  • 3
  • 29
  • 47
  • What's the story with the two meters? What's in the lower area of the meter housing? – Harper - Reinstate Monica Jan 06 '17 at 07:50
  • Second meter is for a different unit. It's not relevant. The lower area is the main breaker panel... Like I said, the meter and main breaker are in an integrated unit. – Hari Jan 06 '17 at 08:35
  • @HariGanti, it's actually VERY relevant. You CANNOT increase the amperage of that meter pan, nor can you add another 125A breaker. Each position of that dual meter pan is rated for 125A. What makes it relevant is that it is a dual socket. You cannot simply change or upgrade one side. Either the whole thing would need to be replaced, or your side abandoned and a new 200A meter socket installed along side this existing one. – Speedy Petey Jan 06 '17 at 12:55
  • @HariGanti, dare I say you are GREATLY over-simplifying this. It is not nearly as easy as you make it seem. And I don't know who at your utility said that meter/service was capable of 320/400. They are clearly mistaken. I assume they meant you can have up to that size service with the proper service entrance equipment. – Speedy Petey Jan 06 '17 at 12:57
  • Possible duplicate of [Optimal Breaker Configuration for Split Phase Mains Power](http://diy.stackexchange.com/questions/105694/optimal-breaker-configuration-for-split-phase-mains-power) – Speedy Petey Jan 06 '17 at 12:59
  • 1
    Voting to close as too broad. There's way too much being tackled in this post. Consider simplifying to one clear question, and post others if needed. – isherwood Jan 06 '17 at 14:42
  • @SpeedyPetey, No offense, but I am not sure how you can say definitely that the meter/service is for anything other than what I stated (unless you work for my utility company). I asked the service upgrade department what my service location (so only my meter, on the left) is capable of drawing, and I was told 320. Unless you have additional information about how that's wrong, it seems imprudent to assert it. Also, they don't know what the main breaker size is, of course, so I would need to upgrade that to receive 320A. – Hari Jan 07 '17 at 01:24
  • @isherwood, I attempted to break down my goals into a set of questions that I had about it. Given that it relates to one project (upgrading my current rating), I believe it still works as a single question. It's more complicated because the layout of components is more complicated. That aside, is there a way I can simplify it for you? – Hari Jan 07 '17 at 01:26
  • @HariGanti, I know because after 30 years of doing this for a living and nothing else I know what a 100A meter pan, a 200A meter pan and a 320/400A meter pan look like. That IS NOT a 320A meter pan. Even that whole pan, with just a 2" riser, is not capable of holding the wires necessary for 320A. – Speedy Petey Jan 07 '17 at 02:34
  • @SpeedyPetey, gotcha. My last edit was based on my most recent call to the utility, which brought to light that the first rep I spoke to had no basis for saying 320A. As such, it seems you are probably right in that, as is, that meter can't service 320A. Any idea what it can service? – Hari Jan 07 '17 at 06:04

2 Answers2

3

Spaces vs Circuits

First let's explain the 8/16 thing, or "8 spaces but 16 circuits". At some point, panel manufacturers developed what I (alone) call a "double-stuff" breaker, which crams 2 breakers into a single space. This is intended to solve crowding problems in too-small panels.

enter image description here photo source: Home Depot

Relying on these, marketing called their boxes 2X-circuit (X-space). Around 2014 they mysteriously stopped doing that. Recent NEC changes required AFCI or GFCI breakers on damn near every circuit... AFCI and GFCI are not made in double-stuff breakers.

Your 16/8 service panel is a legacy of that bad labeling. You have an 8-space panel, intended to replace an 8-space fuse box.

Panel space is dirt cheap. Go nuts.

You are dreaming of a 16-space panel. And even that is dreadfully small and you will find it rather limiting even with 100A service.

The practice of many electricians is to give you the smallest panel possible. That's first, to force you into more subpanel work if you expand further (more money for them) and second to save themselves $20 in part cost.

The cost of a larger panel is trivial tiny compared to total project cost. It is very correct to be extreme. Please spend an extra $100 for a 42-space panel, unless you just can't make it fit. Honestly I'd go 60-space. Not least, those larger panels are 225A-ready.

You never know. You might do a kitchen remodel and go hey, I'd like a separate circuit for refrigerator done microwave done dishwasher done disposal done 3 outlet circuits done. You have the space.

When you buy a PC, do you really calculate your needed hard drive space and buy just what you need... Or do you just buy the big 3TB drive? Of course you do. Same thing here.

More work to do at the meter

OK so the power company says their side of the cable is 320A. If they say so.

They say their meter is 320A. If they say so.

But your meter housing is not 320A.

To support more than the listed 125A, you will need to upgrade your meter housing. There's no question of that. That's your equipment and you have to pay for it, probably, unless your power company does something different with cost sharing.

You won't be able to replace parts of it, you will probably even have to replace both sides of it as a single unit. However it is very nice to have your main breaker in the meter. It means you can fully de-energize your main panel, which makes it safer for you to do yourself.

The 320A may be shared

Since it's multi-unit, the power company provisioning 320A makes more sense. Trouble is, this 320A service is probably shared between both units. So it's not as much as you think.

You really need to talk to your power company about what they consider this "320A" to be. It may be a relabeling of what other power companies call 400A service. So they may be willing to feed two 200A panels, or 100/100/200. This is a conversation you can have only with them.

More food for thought is sub-metering units, and separately metering common spaces. The new thing in rental properties is to have one main meter and the landlord has sub-meters per tenant. Many landlords prefer (and some law requires) commons space usage to be on a separate (sub) meter, i.e. heating, yard and commons lighting, anti-freeze pipe wrap or roof/gutter heat, coin laundry, Christmas decorations etc.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
  • Thanks. FWIW, my service location (meaning the meter itself) has a different physical address than the other meter, and I inquired specifically about my address. Given the number of comments concerned about this, I'll call them again and verify that the 320A/400A/I'll-ask-what-they-really-mean is not a shared rating. Also, I just realized that the two meters/breakers are in one housing... So both sides will need to be upgraded. – Hari Jan 07 '17 at 01:31
  • Is it preferable to replace the existing subpanel to increase the number of slots available, or install a second subpanel? – Hari Jan 09 '17 at 06:52
  • Depends. First, do any subpanels *need* replacement due to damage (rust), de-listing (FPE panels), obsolescence (PushMatic) or just plain cheapness (Homelite). Then, how do you choreograph it so the house remains usable during the work (in a DIY situation that can be weeks). Adding a subpanel and making the original a sub-sub-panel is a great method. Move circuits at your leisure then remove it. – Harper - Reinstate Monica Jan 09 '17 at 19:00
  • The one subpanel I have doesn't need replacement. It's actually brand new, but simply doesn't have more than 8 slots, so I'll be filling it fast. If I kept it, I'd need to add jumper wire connecting the hots and neutral going into the existing box to provide power for the new box (if I can just use jumper wire). I also don't really need electricity in the studio for a while. Would replacing a panel really take much longer than a day to bolt to the wall and wire it up? – Hari Jan 09 '17 at 19:56
  • 1
    An 8-space panel won't be so bad. Depends if you run into any complications. – Harper - Reinstate Monica Jan 09 '17 at 20:01
  • Can jumper wire be used to bridge the hots and neutral between two subpanels? I'm just concerned that replacing with one panel means that if ever need to upgrade the main breaker, I need to run entirely new wires to it, instead of simply running a second set from a 4-pole breaker (as I outlined in my original question). Does my question make sense? – Hari Jan 09 '17 at 20:14
  • Any sub-panel is fed off a regular 2-pole breaker position in the main panel or another sub-panel. You're asking if the wires coming from one such breaker can leapfrog and serve two sub-panels. That's complicated, and really rates a whole 'nother question. http://diy.stackexchange.com/questions/106189/can-i-feed-2-sub-panels-off-one-breaker – Harper - Reinstate Monica Jan 09 '17 at 21:23
  • I was thinking that might be the case... I actually saw the question before this comment and thought it looked awfully similar to this... I'm guessing you'll answer the question yourself? – Hari Jan 09 '17 at 21:37
  • Probably not, since I honestly don't know the answer. – Harper - Reinstate Monica Jan 09 '17 at 21:39
  • Let us [continue this discussion in chat](http://chat.stackexchange.com/rooms/51473/discussion-between-hari-ganti-and-harper). – Hari Jan 09 '17 at 21:42
0

Your plan of having two sets of wires between the meter and panel is not allowed. Until you get into giant sizes of wire, it has to be a single wire for each hot and neutral. You are going to have to pay to replace it with thicker wire.

If there is a location closer to the meter where you could install a panel and run new circuits from, you could do that and make your current panel a subpabel. That would reduce the amount of wire you need, if the existing wire to the label can reach the new one.

Grant
  • 5,589
  • 2
  • 22
  • 39
  • 1
    He is not looking to run parallel conductors. He is looking for an additional feeder run with the existing feeder. – Speedy Petey Jan 06 '17 at 12:52