2

I've got 2 lights in the house that have an intermittent flicker (we can go for days without having it at all, then it'll happen for a bit). I've not seen them do it at the same time. They are on the same circuit (but different switches). It's not much of a flicker really, closer to a very subtle change in light output, just enough to annoy and concern me (my wife didn't even notice until I pointed it out). They are 2 of the highest power consumers in the house, one being 200 watts, the other 180 watts. For comparison, our third highest consumer is 160 watts, is on a different circuit and has never been seen to flicker.

There is also a 60 watt bulb on the same circuit as my flickering lights and on the same switch as the 200 watt fixture. This one never has been observed to flicker (but perhaps I simply can't notice it as the light output is so much lower).

I'm at a loss as to how to narrow this down further. I've observed other light and appliance usage in the house and it doesn't seem to match up with anything. The closest I've gotten to a pattern is that the 200w unit seems most likely to flicker when used between 5-6am and the 180w when used between 8-9pm. I'm not opposed to calling an electrician, but since I can't reproduce it at will, that seems like I'd probably end up throwing a lot of money at it for no results.

edit

I've now been able to isolate as the other light on the circuit has started flickering (very faintly) now. It's only when the lights are on due to both (3-way) switches being "down". If they're both "up", the lights are flicker free. I'll be checking the connections at the switches now. If not the connections, is that failure usually a bad switch or a bad connection wire for the 3-way setup?

Brian Knoblauch
  • 1,087
  • 3
  • 15
  • 25
  • 1
    What kind of fixture are these lights in? Are these incandescent bulbs or LEDs? I had a total of 7 ceramic single bulb fixtures go bad with LEDs in them. After being in service for a year or so they began blinking, but I was in denial, then the switches would fail to respond to the pull chain. I am sure it was the pull chain switch because in some the switches failed entirely. These were all bought at the same time at a big home store. I replaced them with ceramic fixtures from a different manufacturer and reduced the number with a pull chain. Four of those that went bad were on a wall switch – Jim Stewart Dec 24 '16 at 16:08
  • Had a similar problem; turned out to be a failing in-line fuse on one phase coming from the street. Responsibility of the utility... – DJohnM Dec 24 '16 at 19:29
  • @JimStewart All incandescents. – Brian Knoblauch Dec 25 '16 at 22:12
  • Are these multiple bulb fixtures that total 200 W and 180 W or single bulb? If the wiring of the fixture is stranded and connected to the solid house wire by a twist on connector, you could remove the wire nut and examine the stranded wire. I have seen some stripped improperly so that too many strands were cut. In our house flickering hall lights were due to a loose neutral in the panel. (Wire showed heat damage.) – Jim Stewart Dec 26 '16 at 16:03
  • @JimStewart Multiple bulb fixtures – Brian Knoblauch Dec 27 '16 at 12:07
  • It's so intermittent. Something else that came to mind the other day... Wondering if maybe it's related to the refrigerator defrost cycle? I haven't had problems any of the times I've used either since I posted this question, and each time I checked the refrigerator and it was NOT defrosting. Not enough evidence yet to say for sure, but it's another lead to follow up on. – Brian Knoblauch Dec 27 '16 at 12:11
  • Do all of the bulbs in the multi-bulb fixture flicker simultaneously or do some flicker and others do not? – Jim Stewart Dec 27 '16 at 17:39
  • @JimStewart Simultaneous – Brian Knoblauch Dec 27 '16 at 18:35
  • OK so it is probably not a poor contact in the screw in bases. The next thing in order from the bulbs to the wall switch would be to redo the connection of the fixture to the house wiring. Is this stranded wire connected to solid house wire with a twist on connector? Is you house wire copper or aluminum? – Jim Stewart Dec 27 '16 at 18:41

4 Answers4

4

It was a bad switch.

The isolating it to when both switches were in the same position was as far as we could get for diagnostics. All connections were inspected and seemed fine. I finally gave in and just bought 2 new switches. Upon trying to install them I noticed mismatches in wiring colors so I brought in an electrician who was able to sort things out (and tagged the wiring for me). He then removed the oldest looking of the 2 switches and replaced it with one of my new switches. The flickering problem is gone and I have a spare switch now...

Brian Knoblauch
  • 1,087
  • 3
  • 15
  • 25
  • As a followup, I had to replace that same switch again already not even 2 years later. It seemed to be OK in the "up" position, but developed a fault in the "down" side, causing violent light flashing when on in that configuration and emitting a scary squealing sound when off in that configuration. – Brian Knoblauch Feb 21 '19 at 13:10
2

For old fixtures with a screw-in lamp base, I think the cause of flickering is often that the center hot contact is not making firm contact with the bulb. I pry the center contact up slightly with a screwdriver or a crochet hook. I also scrub oxide off the contact with a pencil eraser, but I'm not sure that does anything. Naturally be sure the switch is off and check the socket with a non contact or contact voltage tester before inserting anything in the socket.

Jim Stewart
  • 19,878
  • 1
  • 29
  • 47
1

I will tell you what I found with some flickering lights.

I had two light bulbs flickering on the same circuit. I inserted a voltmeter into one of the sockets (removed the bulb), and when the other light would flicker, I would see the voltage drop momentarily in the socket I was looking at. Which in my mind would indicate it's not the bulb (the fact that I had two bulbs do it at the same time is also a good sign there, heh).

Next step is to isolate the problem. You can either start "close" or "far"

If you're starting close, go to the switch, pull it out from the wall, put your voltmeter lead on the incoming power, and one on "common" or "ground" it should read 120. When the lights flicker does it change? If not then the problem is somewhere between the incoming lines and those bulbs (hint: might be the switch itself, or maybe where it connects to one of the fixtures). You could also try putting your voltmeter leads on the wires leading out of the switch, do they drop?

If voltage is still dropping there, go to the power box, identify the breaker it's on, and put one voltmeter lead on the breaker output, one on common. Does the voltage drop? You can also try the same thing with the main large incoming line (though that's pretty scary, might want to have a pro or a friend help). Does the voltage drop? If it's still dropping from the main coming in, time to call the power company and ask if they can look into it (in my neck of the woods they can install some kind of "meter" to monitor it for you temporarily).

In my case I tested the "main" and it didn't drop in voltage. I was then about to test the breaker when I noticed "that's odd, one of those breaker looks like it's sticking out slightly more than the rest" and sure enough, it was the one feeding my "periodically flickering" lights, so plugging it in more firmly I believe solved it for me.

If it's LED's (especially on a dimmer) then there are other things that could be at play, but still worthwhile to check if voltage is a problem.

rogerdpack
  • 610
  • 2
  • 11
  • 25
0

the best way to understand any of this is are the fixture from China and the bulb from USA? I notice that all bulbs have a different degree of width, if you use the tightest fitting ones, you leave the bulb socket loose for the smaller ones, you can replace the ceramic lamp socket or put a tiny amount of tin foil around the loose bulb so the contact is snug, do this with the switch off, and only wrap the outside with the threads, not the bottom contact, I've don't this, on many china ceiling fans, if it mine the foil trick is a fix, if it's for a customer, I just replace the socket and charge the player $$$ IT'S UP TO YOU, now as far as these advice thread, it's been almost 100 percent with bad info, as a handyman I always run across a crazy scenario, and I've found that most people posting insight are full of it, if you need help just find my facebook, chances are I've fixed just about everything in the last 40 years