I’ve got a trivial problem that has become complicated by a non-trivial setup.
My goal is to install an 80amp (100amp breaker) EVSE to charge my electric truck. An incentive from my electric provider will pay up to $850 for the installation of an EVSE, and since the EVSE itself was provided with my vehicle, I figured it would be an easy way to get the wire paid for. My provider requires that the installation is performed by a licensed electrician. After calling a few electricians, I was able to get one to come out to install it (It is difficult for me to get anyone to come out to my property due to its rural location and far drive).
I was surprised when the electrician told me that it was impossible to install the EVSE at the rated 80 amps, he mentioned that the upgrades would not be feasible, and he wouldn’t take the job (Out $250 for the service call….)
The electrician gave three main reasons why this install was not possible:
- The wire feeding the sub panel was not large enough to handle the load and would result in unacceptable voltage drop.
- After performing a load calculation, the load on the sub panel is too large to handle the additional load.
- The service size (And utility transformer) is not large enough to handle the entire load of the property if I were to add the additional EVSE.
Absolutely none of this makes sense to me due to my understanding of the electrical infrastructure on my property. I fear I may be missing something.
The Details:
- My property is served by a 600 amp service (50 KvA transformer)
- 2 x 200amp panels to the house
- 1 x 200amp panel to the shop
- I’d like to install the EVSE in the shop
- I have a 16kW solar array that is on the roof of the shop, but not directly attached to the shop electrical panel.
- The wire from my meter to the shop is labeled ENCORE WIRE CORP 500 KCMIL AA-3003 AL
- The shop is ~400 feet away from the main panel
- The breaker at the main panel for the shop and solar is 200amp, but the shop panel itself has a 150amp breaker
- The solar system that is connected has a utility mandated disconnect which has a 100amp fused disconnect.
Existing loads on the shop:
- A whole bunch of outlets (Served by 2 double pole 20amp breakers), in practice not more than one is used at a time
- A 15amp breaker feeding a hydronic heating system
- A 50amp breaker feeing a whole bunch of outbuilding sub panels
Existing loads on the house
- The house (400 amp) has a lot of electrical loads
- 4900sq feet
- 2x EVSE (50 amp NEMA 14-50)
- Geo Thermal Heat Pump
- Electric Oven
- 2x Electric Clothes Dryer
When searching online to try and figure this out myself, all of the NEC load calculations don’t make sense for the “Shop” space that I have, so I don’t understand what is reasonable. I was planning on just going ahead and doing this myself (After wasting $250 for the service call), but I figured I’d ask the internet if my understanding is incorrect.
Questions:
- Is it reasonable to put an 80 amp (100 amp breaker) EVSE on my shop panel?
- Will I experience unacceptable voltage drop with my 500kcmil wire if I put the EVSE on it?
- The electrician was saying that the 80amps of solar counted AGAINST my load calculation, and the 80 amps plus the 80 amp EVSE plus the additional loads would put me over the limit for the wire to the shop. In my mind the 80amps of solar (Located at the shop) will help with voltage drop and shouldn’t be accounted for when considering loads on the shop panel.
- Is the size of my utility transformer (50KvA) upto the job?
- I don't want to break "Harper's Law", so any suggestions on the wire? Manual indicates that I need 3AWG copper. I am going about 30feet in an exposed area (In the shop)
I understand that my setup is atypical, so if you require any additional information, please let me know.
Appendix:
Additional information that isn’t relevant to the question but will hopefully dispel any “You don’t need this” type answers.
I 100% agree with both Harper and Alec that 80amps of EVSE charging is not necessary…….but……. My utility combined with my solar setup has me in a sort of loophole that I am trying to take advantage of. I am fortunate enough to live in a state that provides net metering on a basis of cost (Not KwH). This combined with Time of Day rates means that I make a lot of “Credit” during the expensive day time hours, and have a ton to use during the night time. I’ve got a 4 hour window where the electric costs are 1/3rd what they would be during the day. This combined with the very large battery pack in my truck means that I want as much as I can take during these 4 hours. I’ve had the truck for a while, and know that with my current use case it takes around 8.5 hours to charge @ 40amps.
Photos:
Wire to shop panel
Shop Subpanel
Main Panel
One Line Diagram from solar install: (Should hopefully clarify a few things