We had some rain that blew sideways yesterday and tripped our outdoor GFCI which is connected to our tankless gas water heater. The orange light is showing and we can’t reset the outlet. I’ve turned off the main breaker feed to the water heater to avoid any more damage. We are shivering in our showers and need a solution.

enter image description here

enter image description here

enter image description here

enter image description here

Model for water heater: Takagi AT-K5U-OS-N at AC 120v

Criggie
  • 9,262
  • 1
  • 21
  • 58
Leslie
  • 81
  • 3
  • 2
    Pictures and model numbers would be helpful. I’m guessing this is a gas water heater that needs 120V for ignition / control? – pericynthion Nov 10 '22 at 05:57
  • 3
    Is this hard wired or does it have a plug? If it has a plug you can plug it into a different socket not governed by the broken gfci. – Willk Nov 10 '22 at 22:53
  • 2
    Based on the new photos - GFCI is almost certainly a code requirement because it's outdoors AND handles water. Since the unit is hardwired, I think it is a code requirement to have a disconnecting means within sight of the unit (similar to A/C units), which having the GFCI outlet outside right underneath would satisfy (you could press the TEST button to disconnect the electric to the water heater). GFCI outlets are often cheaper than GFCI breakers, and outdoor outlets are often useful, so the arrangement makes *some* sense. – maples Nov 11 '22 at 12:46
  • 2
    Oof, looks like the bottom of the GFCI box is open, so the GFCI is open to the elements? Is that OK with US code? AFAIK it's not OK here (Europe, The Netherlands), and I personally wouldn't ever want it. I'd say get another one of those rubber stopper thingies you see on the side, but then for the bottom. Then that box should keep your GFCI nice and dry, no need to move it inside. – Daniël van den Berg Nov 11 '22 at 14:31
  • 2
    @DaniëlvandenBerg: The WR rating on the GFCI indicates that it's supposed to be weather resistant, and in most places rain doesn't fall upward (winds may cause localized sufficient updrafts to propel rain into the bottom of enclosures in some places, but wouldn't expect that here). – supercat Nov 11 '22 at 20:34
  • 1
    @DaniëlvandenBerg - The hole in the bottom is to allow the power cord that's plugged into the outlet to exit the box. Of course, in this case such an exit isn't needed. – Hot Licks Nov 11 '22 at 22:25
  • 1
    @DaniëlvandenBerg I have a box exactly like it; there are plastic inserts that slot into the grooves around the opening to seal it. You're supposed to only remove them when the outlet is in use (to allow the cord to exit). My question would be whether the BACK of the box was sealed properly against the house. Idiot contractor I bought my house from put these on, but left gaps BEHIND the box. First hard rain blew the outlet. I replaced it and properly sealed it, has survived several hurricanes since. – Doktor J Nov 12 '22 at 20:10

3 Answers3

27

Disconnect the load wires from the GFCI. Turn the breaker back on and try to reset the GFCI.

If it cannot be reset, the problem is in the GFCI. This is common for GFCIs mounted outdoors. You will need to replace the GFCI, and you should try to make it more weatherproof. It needs a good weatherproof cover (UL listed for that purpose) or better yet, relocate it indoors.

If the GFCI can be reset with the load disconnected, then you have a ground fault in the load (i.e. the water heater, the wiring to the water heater, or any other outlets that may be sharing that circuit).

pericynthion
  • 540
  • 3
  • 9
6

Since you suspect moisture as the cause of the GFCI trip, use a hair dryer to evaporate the moisture in the GFCI box. After your hot shower, relocate the GFCI indoors.

Phil Freedenberg
  • 993
  • 6
  • 10
  • 1
    In our house a circuit on a GFCI breaker tripped due to water getting into an outside box. I removed the box cover and dried out the box with hair dryer. The OP should remove the box cover (two sccrews) and direct the air in with a hair dryer, but be careful not to overheat the GFCI receptacle. Alternately, you could use a shop vac (or any vac) with suction and see if pulling in fresh air would allow the GFCI to reset. You might even try suction on the receptacle without removing the cover. Vac on one receptacle so air pulled in through the other. – Jim Stewart Nov 11 '22 at 16:31
-1

Get that water heater onto its own dedicated circuit asap. Putting a GFCI outlet - especially an outdoor outlet -- in front of it is a bad idea and a code violation.

If this is a 120V point-of-use water heater, strongly consider replacing it with a 240V unit.

Even the control/ignition circuit for a gas water heater should dedicated to that purpose.

See also Point-of-use tankless water heater electrical connection

Tim Sparkles
  • 459
  • 4
  • 10
  • 2
    Agreed about using a dedicated circuit, IDK if it's a code violation or not but good practice. Having it on GFCI would be good idea and might be mandatory (again, IDK about code but seems like it would be required). If this is on a shared circuit, it's almost certainly not an electric tankless and may even be a gas water heater, in which case 120v would be reasonable. – maples Nov 10 '22 at 17:33
  • 2
    A GFCI breaker would be a good idea, yes. An upstream GFCI outlet, no. Even a gas water heater should be on a dedicated circuit as good practice; I'm not sure what the code says in that case. Sharing a circuit with a gas furnace might be ok, but as a homeowner I'd want to be able to control them independently at the panel. – Tim Sparkles Nov 10 '22 at 17:41
  • 3
    Dedicated circuit is a good idea, but very likely *not* really a must here as electricity is used for controls and gas burner ignition - all of which would use far less than 1/2 of a 15A circuit, so the circuit does not, based on basic code, need to be dedicated. – manassehkatz-Moving 2 Codidact Nov 10 '22 at 19:53
  • It's outside, it has to be GFCI'd. (agree with everything if it wasn't). It should be a blank GFI, so the gardener doesn't trip the circuit with a weed wacker. – Mazura Nov 11 '22 at 05:46
  • @Mazura: Would isolation transformers be an acceptable and practical alternative to a GFCI for power loads? Unlike a GFCI which will trip if current flows through any path other than the line and load terminals, an isolation transformer would make it impossible for current to flow through any other path in the first place. – supercat Nov 11 '22 at 20:38
  • "The role of the isolation transformer is to allow the AC voltage to reach the operating product and its circuit (the load) while preventing flow of current through the user and back to the neutral line. This cannot happen because the isolation transformer does not have a wire from neutral to Earth, so the current will not flow through the user." - unless they're grounded? I don't understand how lifting the ground is supposed to make it any safer, but apparently that's what hospitals use. – Mazura Nov 11 '22 at 22:13
  • https://www.digikey.com/en/articles/how-to-use-ac-isolation-transformers-in-medical-equipment-to-prevent-shock @supercat – Mazura Nov 11 '22 at 22:13
  • The problem with isolation transformers like they use in hospitals, is that you have to make sure the secondary lines are actually floating, since you could accidentally connect or couple one to ground and nothing would be obviously wrong. Operating rooms use sensitive _line isolation monitors_ that alarm, special medical-grade power supplies with reduced live- and neutral-to-ground leakage currents, and even transparent plugs so one can verify proper wiring. – user71659 Nov 11 '22 at 22:54
  • @Mazura: If one were to wire the output of a safety-rated isolation thransformer to a GFCI and nothing on the line side of the hot nor neutral was connected to anything else, then nothing to which the output could be connected would be able to produce a current imbalance that would trip the GFCI. From what I understand, many UK bathrooms have historically had (don't know if they're still employed in new construction) two-prong "shaver" outlets that include an isolation transformer. – supercat Nov 13 '22 at 20:48
  • @Mazura: Prior to the invention of GFCIs, protecting from shock people who used electric shavers near water would have been difficult, but requiring that equipment only be used in dry locations would have undermined its usefulness. – supercat Nov 13 '22 at 20:50