I'm in the process of running a circuit from the panel in my garage to an equipment area for a koi pond I built. Because of some rock at about 16 inches depth in part of the run, I'm taking advantage of the code allowance for 12" depth for the circuit which will be 20A and GFCI protected. In addition, I'm running it in nonmetallic conduit. There will be a receptacle at the equipment location but I'll also use this opportunity to add one at a nearby patio.
I've dug the trench and installed the conduit, no wires pulled yet. Currently I have an outdoor extension cord providing service to the pond and patio. While traveling, a contractor came by to do some work and plugged in on the patio. They ended up tripping the breaker and couldn't reset it (locked garage) so they left. One of my neighbors later noticed that the pond equipment (life support for the koi, really) was off. He called and we got it started. But this got me thinking that it would be pretty easy to have something in the other outlet trip my pond off.
So, I've decided I probably need to forego the patio receptacle. But I was curious. The way 300.5 is written is says max 20A overcurrent protection and GFCI. I've interpreted this as the total of all wires in the trench/conduit. But, is it possible to run 2 circuits in that conduit if each is less than 20A? I'm guessing not, but I don't really understand the full interpretation of that.
Thanks