I have read in a previous forum post
Is it OK to borrow a ground wire from a different circuit?
that NEC in article 250.130(C)(4) allows the grounding of an ungrounded circuit by connecting to

an equipment grounding conductor that is part of another branch circuit that originates from the enclosure where the branch circuit for the receptacle or branch circuit originates.

The article quoted does not specify any restriction in terms of the relative gauge of the conductors in the two circuits.

I was wondering whether or not is a good idea to "borrow" the 14 AWG conductor of a nearby 120V-15A circuit to provide ground to my 240V-30A washer/dryer circuit and substitute the existing 3-prong outlet with the grounded 4-prong one.
Is the extra resistance due to smaller gauge wire (14 vs. 10 AWG) negligible in a typical circuit of length sized for a 1000 sq ft apartment or is it enough to create a significant delay in triggering the 30A breaker if a ground fault occurs?
The fact that NEC glosses over any potential gauge mismatch would let me think that the first option is correct.

However, some additional research seems to suggest that concerns over using a smaller gauge ground wire are relevant. In this post
https://www.jlconline.com/how-to/electrical/dealing-with-thinner-gauge-ground-wire_o
the expert suggests that the potential problems arising from a smaller ground wire can be solved by using arc-fault circuit interrupter (AFCI) breakers, because such devices are triggered by a small 30mA current in the ground wire. In my case though, if I am correct, this would not help, because the small ground wire current would trigger the 15A breaker of the lending circuit and not the 30A breaker of the borrowing one, which has no ground wire. Any suggestions is highly appreciated. Thanks

UPDATE

Following crip659 recommendation, I finally mustered the energy to move washer and dryer out of the way and open up the 240 outlet, which of course is located in the most inconvenient spot to reach. It was a worth effort, because it led to some important discoveries.
The first one is that in its current configuration the outlet is very dangerous: it has a plastic box, but both its face plate and frame are metallic. And not "grounded" (i.e., for a 3-prong dryer circuit, not connected to neutral) as revealed by a continuity test. Additionally the isolation of the wires is not in the best of shapes Dryer outlet plate
Dryer outlet plate

Damaged wires
Damaged wires

The second discovery is that, as crip659 hypothesized, the dryer outlet is indeed fed by a NM cable with a ground conductor. However it appears that some sadist took pleasure in cutting it short, in such a way to completely hide it inside the cable sheating. This happens both at the outlet end as well as at the breaker panel end. Why would anyone go so out of his way to make sure that no ground connection can be made is beyond my comprehension. Tip of the ground conductor inside the outlet
Tip of the ground conductor inside the outlet

The fix on the outlet side is an easy one. I would just cut off the damaged ends of neutral and hot wires and move the outlet by a few inches to account for the shortened conductors.

The fix on the other end, however, is something that worries me more, because my panel does not appear to have a turn-off switch. Breaker panel
Breaker Panel

Dryer wires in breaker panel
Dryer circuit wires inside breaker panel

Tip of ground conductor entering the breaker panel
Tip of ground conductor entering the breaker panel

I would not want to touch the breakers or anything connected to a live wire, but I can of course switch all the breakers off and work only on the de-energized side.
Off the top of my head I can think of two potential easy fixes, none of which is particularly elegant. I would appreciate any comments/critiques/suggestions on their merit and code-compliance

  1. If the length of the ground conductor inside the breaker box is sufficient, I could use a Wago 221 2-port connector and a 10AWG bare copper extension to connect to the ground bus (is a Wago connector allowed inside a breaker box?)

  2. I could create a junction box next to the breaker panel, splice just the ground conductor, route it to the breaker panel through a convenient knock-out and connect it to the ground bus. In this case, I'd probably use a shielded green 10 AWG wire labeled as "Ground conductor of the dryer circuit".

Any thoughts?

EDIT 2.

I just thought of another possibility that is so simple to be either genius or totally idiotic. It goes without saying that, in a typical scenario involving these two alternatives, the probabilities are highly stacked on favor of the latter. Anyway, here it is: can I just terminate the mutilated wire ground of the dryer circuit by bonding it to the breaker box, right there at the point of entry? Since the box needs to be grounded, what more is there to gain by going all the way to the ground bar?

FINAL RESULT

Thanks to everyone who took the time to provide comments and answers. You all contributed to help me get to a final outcome that is better than what I originally envisioned. At the end I went with the easiest solution, extending the grounding wire inside the breakers panel.
@pmont unfortunately the leftover wire was too short and did not leave any room for crimping. There was barely enough space to close the lever of a Wago connector, but I managed to get it seated all the way. I pulled pretty hard and the connection did not budge. Here is how it looks. The Wago connector
The connection at the panel entry
enter image description here
The final result

MarcoD
  • 435
  • 3
  • 13
  • I guess my difficulty is from not knowing how AFCI breakers work. Are they able to determine which circuit is responsible for the detected ground current or do they shut off all circuits? I doubt is the latter which may create a lot of issues – MarcoD Mar 18 '22 at 04:58
  • 1
    A ground for 30 amps needs to be 10 gauge, so 14 gauge will not pass inspection. – crip659 Mar 18 '22 at 11:34
  • 1
    Can you run a separate 10AWG grounding wire back to the panel, or to the grounding electrode conductor, by any path at all? – ThreePhaseEel Mar 18 '22 at 11:43
  • Are you sure you don't have a ground wire or ground path? Most cables have a ground wire(maybe not used) or wires in metal conduit where the conduit is ground path. – crip659 Mar 18 '22 at 14:33
  • ThreePhaseEEl and crip659, wiring back to the panel is a work of a larger scale than I was planning to do, going through walls and ceilings. Reading the formulation of NEC 250.130(C)(4), in which origination from same box is the only constraint and wire gauge matching is not even mentioned, made me wonder whether NEC allowed for the limited scope of grounding an existing ungrounded circuit, to borrow a smaller ground wire from another existing circuit. My rationale was that doing that would only improve the safety of the code-compliant grandfathered 3-prong dryer circuit – MarcoD Mar 19 '22 at 12:51
  • Gotcha, @Harper-ReinstateMonica, it's just that sometimes, the table shows a smaller size for the ground than for the current carrying wires. Makes sense, I was looking at it the wrong way. Original comment deleted to avoid confusion. – FreeMan Mar 20 '22 at 18:26
  • Best way to extend the short ground that was clipped off is to solder an extension. Not the easiest, but the most solid connection. There's not enough length on that ground stub to crimp onto. Yeah that was a sad sack who cut it so short. – pmont Mar 20 '22 at 21:21
  • Thanks pmont. I ideally see your point but then the reality that I would have to face is the horribly botched soldering job that my skills in that craft all but ensure. In that location especially with all that isolation ready to be melted, I would get the father of all shorts. Why do you think a Wago connector would be unstable? That wire would barely ever get any solicitation to move – MarcoD Mar 21 '22 at 04:43
  • I'm not sure if soldered connections are explicitly forbidden by US code, @pmont, but I've seen a _lot_ of recommendations _against_ doing so here at [diy.se]. Mostly for the reason the OP mentions in his comment, above - poor soldering skills leaves a questionable connection which can start arcing, producing heat which can melt the solder at a minimum and start a fire at worst. – FreeMan Mar 21 '22 at 13:33
  • Yes I would only recommend soldering if you have experience and the right equipment. A high power soldering iron is needed for 10AWG, plenty of flux, pre-tin the extension to minimize overheating the existing stub. If you don't have experience with that, avoid DIY. If you can access enough of the ground stub to crimp something onto it, that's an easier job. I don't recommend Wago connectors, they can work loose. Get a butt connector and crimp down hard for a solid connection. – pmont Mar 21 '22 at 15:37
  • @FreeMan, yes that is exactly the point. Among all the connection methods, soldering is the one that depends on the highest degree on the maker's skills. When done properly it gives the best result, when done poorly it can become a ticking time bomb – MarcoD Mar 22 '22 at 05:30

1 Answers1

6

On your edited data:

Wow, yes, that is pretty incomprehensible. But keep in mind, in the 60s and 70s, those electricians felt toward grounding pretty much the same as electricians today think of torque screwdriver requirements: they think of it as know-nothing lawyers fooling around with stuff that's worked for 50 years. (which is wrong at every level, but that's what they think). Or it could be a DIYer who didn't have Internet back then.

Your plans for working around the broken ground wire seem solid. I've done the "box near the panel" myself on a rewire of a factory, where someone cut all the wire ends at the edge of the panel to steal the breakers. See if you can loosen a clamp and pull a little more wire in from the wall.

By the way, the "box near the panel" is a great trick when you need AFCI on a panel, but the breakers are obsolescent or you just want to pay $20 for an AFCI receptacle instead of $40 for a breaker.

Edit: That panel

It's obvious the dryer guy did not install this panel. It appears to be fed by a 4-wire feed - note all grounds and neutrals are carefully segregated. So this must be a post-2008-style subpanel fed from either another panel, or a main disconnect/breaker elsewhere. (in NEC 2020 style; some cities have required this for 50 years, probably the same reason for the 4-wire feed). So look for a main breaker or main panel elsewhere.

Despite the age, it's not a split-bus panel because it's apparent the panel is all original, and all the 240V breakers have been put down the right side (a best practice that's impossible on split-bus). So, main breaker elsewhere.

If you can't find a main disconnect, all these breakers "rock out" - push further outward on the handle and the whole breaker will unclip from the bus (which is in the middle). Then the heel comes off its little hook and you have a breaker in your hand with wires attached to it. (which is fine; it became de-energized when it unclipped from the bus). This, by the way, is why backfeed breakers must be bolted down. So you can pop breakers off a live panel, change their wires with the breaker in your hand, and snap them back in. Have the breaker be off so it doesn't arc when you clip it on.

Note that you need a torque wrench or driver to set the screw torque correctly. (NEC 110.14). That's serious business that has been traced to many wire burn-up's.

Unfortunately, you'll be doing this a lot. Challenger panels are fine, but Challenger breakers had a VW-like scandal where it turns out they had rigged their UL testing. So they don't trip reliably and must be replaced. The good news is that BRyant inherited the bus design and kept it for their own BR breakers, and their line is made by Eaton. Eaton BR is the most popular breaker line in America, and if you look on the breaker it says "Type BR / Type C" (you need Type C).

So all the breakers need to be replaced, but it's still under $100 for all of them. That's about what you were going to spend on the 2-pole GFCI!

On retrofitting a too-small ground:

This is a universal problem: grounding the 30A dryer. With a universal answer: "NOPE". The wire is too small.

Code is clear in 250.122 that a 30A circuit needs a 10 AWG ground. 15A circuits are wired typically with 14 AWG wire.

14 AWG is smaller than 10 AWG, so it is not a suitable ground wire. In the case you link, that person's #16 ground wire was legal when it was installed, and is now grandfathered because the owner can point to the date on the building permit. Your de novo use of #14 on a 30A circuit is not grandfathered, and has no date because it has no permit. (it may not need one).

AFCI is Arc Fault Circuit Interruptor. It uses a digital signal processor to "listen" for arcing on the wires. What you just described is a GFPE (weak GFCI that operates at 30A instead of 5mA threshold). AFCI and GFPE are not the same thing. However, some implementations of AFCI do include a GFPE as a "cheap" way to detect H-G or N-G arc faults (since they are also ground faults). Those would work; however 9 years later when it starts nuisance tripping and you replace it with a year-2031 AFCI, that year-2031 AFCI may not have any GFPE at all. Indeed, GFPE-absent AFCIs are already on the market.

As such, if you want GFPE, use a GFPE or GFCI, not an AFCI.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
  • Harper, thanks for clarifying the GFCI/AFCI issue. By using GFCI, in my view the case for borrowing the 14AWG wire to ground the dryer circuit becomes even more compelling as it does not only provide a direct, albeit undersized, path to ground, but by decoupling ground from neutral it also allows the use of a GFCI 2-pole 30A breaker to protect the dryer circuit. Wouldn't this be the same scenario that NEC allows for ungrounded 120V outlets protected by a GFCI breaker? Actually better, as in that case there is no ground wire at all, while in this case a ground wire is present but undersized. – MarcoD Mar 19 '22 at 10:03
  • Harper, thanks for all your support. It is really highly appreciated. It’s funny you mention the Challenger scandal because just yesterday, as I was researching this unknown to me company, I stumbled upon this and thought, here we go, my usual luck haha. My apartment is in a 3- story condo built in 1991, so not that old. All the other circuits are neatly grounded. I thought maybe a previous owner modified the outlet to suit his dryer, but I hardly see any amateur brave enough to do such a mutilation job inside the panel. – MarcoD Mar 21 '22 at 05:16
  • 1
    @Harper - Reinstate Ukraine, why is putting all the 240V breakers down the right side of a bus a good practice? – aerospark Mar 21 '22 at 06:00
  • Thanks for explaining me how to safely work with the breakers even without a main switch off, I had no idea. Being in a condo I would not be surprised if the main switch controls the whole column of 3, as it is for the water. So I do have to change all the Challenger breakers, correct? I wonder if the whole condo complex has them. Probably not, since you mentioned that my panel looks circa 2008, 17 years after the complex was built. By the way, my dryer is 120V, my motivation to ground this circuit is to use it to create a series of 120V/20A outlets, but that’s the subject for another post – MarcoD Mar 21 '22 at 06:18
  • 1
    @aerospark because bus stabs have finite capacity, and running large breakers down one side means there is a small breaker opposite it. Some people think it's clever to put the largest breakers opposite each other, but that's a worst case scenario for bus stab load. With quadplex breakers it's very easy to exceed stab limits. – Harper - Reinstate Monica Mar 21 '22 at 18:48
  • 1
    @MarcoD I said the panel was done *in the NEC 2008 style*, no, it was not done in 2008. Nothing wrong with Challenger buses, they're identical to BR. I notice how that electrician doesn't mention that, because there's more profit in replacing whole panels LOL. – Harper - Reinstate Monica Mar 21 '22 at 18:50