3

See below for (attempt at) solution

I'm wiring up a shop I'm putting together and came up with a plan with my electrician but I'm a bit confused on how to execute it. Namely, I'm trying to put a 240V outlet with no neutral pathway on the same circuit as a lightswitch, if possible. I've drafted up the following incomplete wiring diagram for reference: Draft wiring

Some specific questions:

  • I'm using 2-wire flexible metal conduit. So when I wire up the two hots to the dual-pole breaker to power up the 240V socket, which has no neutral pathway, these wires are left floating in the wind. What am I supposed to do with them?

  • Ideally, I would like to power the shop lights on the same circuit as the 240V outlet. Can I use one of the hots coming off of the dual-pole breaker to power the lights? Maybe I can use those two neutrals here as well?

  • For obvious reasons, I'm under the assumption that I'm supposed to be getting 240V across the two poles of the 240V outlet. However, my application of Kirchhoff's laws to the circuit gives me 0V across the poles. Can someone explain to me what I'm missing?

I'm happy to clarify anything I've said.Thanks for the help!

Complete schematic based on Harper's answer:

Hope I'm interpreting correctly. Fixed schematic

  • Where are you getting 2-wire flexible metal conduit? I have never heard of that. There's metal-clad cable which has conductors already in a metal sheath. Separate from that is flexible conduit that starts with 0 wires in it, and then you add wires. Which are you working with? – Harper - Reinstate Monica May 27 '20 at 17:41
  • Harp: I think he might be meaning armored cable. oops...just reread your comment. I think you covered my subsequent comment. – George Anderson May 27 '20 at 18:02
  • What wiring method are you using for the circuit? Armored or metal-clad cable where the armor is tightly wound over the conductors, or actual flexible conduit where there's room for more wires? Also, is this in a basement, a garage, a detached shed, or some other sort of space? – ThreePhaseEel May 27 '20 at 23:10
  • Yup. That is exactly what I had in mind. You did it a smidge different but that only shows how well you get it. I don’t need to tell you to make sure the lamp is 240V, but it won’t hurt to remind the next reader. – Harper - Reinstate Monica May 28 '20 at 01:38
  • @Harper-ReinstateMonica oh excellent! I'm glad I got it right. Thank you for you explanation, I found it really useful. I'm gonna run this solution by my electrician and then get started this weekend I hope! – GeneralPancake May 28 '20 at 04:13

1 Answers1

7

I gather your electrical experience comes out of low voltage DC?

1. 2-wire FMC.

Flexible metal conduit doesn't have any wires in it. You surely mean AC cable or something like that. What's more, since you're talking about neutral wires left floating in the wind, I gather you are using two cables for the same circuit. You are never allowed to do that. All related conductors must be in the same one cable or conduit. If you have complex wiring needs you need to use conduit, but what you are trying to do should be workable with /2 or /3 cable.

If your apprehension is that you think you are not allowed to use a white wire for "hot"... in cable you are allowed to re-mark a white wire black* at both ends and use it as a "hot". Obviously you no longer have a neutral at that point. But you may not need one.

So your answer is to use ONE armored/metal clad cable, and re-task the white wire to be the 2nd hot.

"But I want to run 2 circuits and get 240V out of them" -> That is called a multi-wire branch circuit and is one circuit in one cable with one neutral.

2a. Hooking up the lights (the easy way)

Eliminate one of the two metal clad cables. (by which I mean, task it for a totally different and unrelated circuit).

The white wire on the lights should be remarked black.* It should then be conected to the red wire on the recep.

This will deliver 240V to the light, but the vast majority of modern lights are multi-voltage 120V-240V. If you do not have a light like that, get one!

2b. Hooking up the lights (the hard way)

Eliminate both existing cables.

Replace the cables with a single /3 cable (black white red in the cable). Wire it as normal, except land the neutral on the neutral bar (or GFCI breaker if it's one of those; remembering NEC 2020 once adopted will require GFCI on 240V receps, and it's already adopted in MA with several more states coming July 1).

Now, you wire it as you have drawn it, except the one white wire goes to the white wire for the light.

3. Kirchhoff's Law.

Kirchhoff made the stupid mistake of using a duplex breaker to feed a multi-wire branch circuit. As a result, both AC sources are in-phase with each other. Both are "high" at the same time, and there is zero volts between them.

So of course the 240V loads completely failed. Not only that, Kirchhoff's 120V loads are overloading the neutral wire. You can laugh when Kirchhoff's house burns down.

Seriously, that simulator sucks. I gather it's made for electronics, not real mains electrical.

Assuming the simulator is capable of this, it would probably be better to draw the AC source as a single 240V center-tap transformer. Which is what it is actually.

See also the way you drew neutral with a ground symbol. Ground never handles current except during fault conditions. The return path is the neutral which is individually wired and not a backplane. It handles only its own circuit's return current, no sharing.

Ground is a backplane.


* Feel free to use brown, red, orange, yellow, pink, blue or purple tape instead. You cannot use gray, white or green as those are reserved for neutral, neutral and ground respectively.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
  • 2
    What I REALLY REALLY want to know is how in H. E. double hockey sticks does Harp crank out these insanely great answers so quickly. I'm starting to think Harp really is a sophisticated AI bot. Great answer, yet again, Harp. – George Anderson May 27 '20 at 18:12
  • 1
    @GeorgeAnderson I just hit "reload" far, far too often :) – Harper - Reinstate Monica May 27 '20 at 18:17
  • My computer died and I have been out of the loop, What is the meaning of "Reinstate Monica"? – Jim Stewart May 27 '20 at 19:04
  • @JimStewart, it's a long saga... [This is the latest](https://meta.stackexchange.com/q/340906/327010), but you could spend all day reading about it. – JPhi1618 May 27 '20 at 19:17
  • @Harper-ReinstateMonica You wouldn't be wrong that my experience comes from low-voltage DC. That and some circuit analysis I did for E&M labs in undergrad years ago. I really appreciate this detailed response. I will review it and redo the wiring and post it as an answer to this question, and I hope you will chime in if I have or have not gotten things write on my second go around. Thank you very much. – GeneralPancake May 27 '20 at 19:29
  • right* not write.... – GeneralPancake May 27 '20 at 19:48
  • 2
    @GeneralPancake Or edit the question to tell us what you *plan* to do, and we can give course correction before the fact instead of after :) – Harper - Reinstate Monica May 27 '20 at 20:16
  • 1
    @Harper-ReinstateMonica I've opted for your suggestion to edit the question. – GeneralPancake May 28 '20 at 00:36
  • Let's make it super confusing :) .... A MWBC, is **one circuit** in *one cable* with *one neutral* and requires **'3 wire' AC**... which has four conductors in it, because you need a ground... unless you run it in EMT, or re-identify the neutral as a CCC if you don't need one and then you can get away with using '2 wire' AC, which has three wires in it. - I hope that doesn't help anyone who shouldn't be doing this. – Mazura May 28 '20 at 02:51