14

I installed an Ecosmart 27kw tankless water heater yesterday and as far as heating the water goes, everything works perfectly.

The issue is when the water heater is running, I lose internet!

Specs:

  • Heater is 240v 27kw @ draw 112.5amps
  • Breakers are 3x 40amp dual pole across both sides of the split phase
  • Wiring is 3x 8awg
  • My internet is 10mbit ADSL down the phone line.

--

My suspicion is that the high amp lines are creating an electrical field which is interfering with the low voltage phone line system, killing my internet.

When turning on the hot water, I loose access to ping google.com, however I can still ping 192.168.2.1 [my router] which says it's not the router that's being interfered with via power loss.

Any recommendations regarding minimum distance between the high amp cables and the phone line. Am I even on the right track here?

Thanks - Jon


Update: Fixed by installing a new phone line externally, 2 meters away from the high amp lines with cat7 cable.

Jon Barker
  • 263
  • 1
  • 9
  • 1
    Probably accurate - https://www.dslreports.com/faq/8511 – TEEKAY May 24 '19 at 13:58
  • 1
    Where does the phone line run in relation to the supply for the water heater? Is your phone system properly bonded to your electrical grounding system? Are all connections tight, screw terminals etc? You could try powering the DSL modem off a battery or UPS temporarily to see if that relieves the issue. – PhilippNagel May 24 '19 at 14:00
  • I'm going to follow all the lines in a bit to see how close they get. They seem to come into the house at the same point as the meter inputs, but never had an issue in the past. I know very little about phone lines - will google regarding how to ground them and ensure that they are grounded. I don't believe it's an issue with screw terminals not being tight as this only happens during water heater turned on. No vibrations occurr at this point. The DSL modem/router are a combined unit. It is already running on a UPS system. I will disconnect the UPS source and validate same problem. – Jon Barker May 24 '19 at 14:05
  • 1
    Must be because [the internet is a bunch of tubes](https://en.wikipedia.org/wiki/Series_of_tubes) :-) – manassehkatz-Moving 2 Codidact May 24 '19 at 14:13
  • 1
    @manassehkatz I guess i plumbed it in wrong, should have attached the cold source to the phone line :) – Jon Barker May 24 '19 at 14:13
  • 1
    At the water heater, are the three cables grouped, all the wires of one cable to group 1 /phase 1, etc.? Or are they connected bric-a-brac because it doesn't matter? – Harper - Reinstate Monica May 24 '19 at 14:59
  • @Harper The three cables contain 3x wires, RED/BLACK/GND. **GNDx3** connects from the panel ground to the heater ground. **RED** connects from panel phase A to Red inputs in the heater. **BLACK** connects from panel phase B to Black inputs in the heater. – Jon Barker May 24 '19 at 15:31
  • See here for a video explaining panel wiring https://www.youtube.com/watch?v=9lQw8Po2H04&t=55 – Jon Barker May 24 '19 at 15:32
  • See here for a video explaining heater wiring https://www.youtube.com/watch?v=9lQw8Po2H04&t=203 – Jon Barker May 24 '19 at 15:33
  • 2
    The video is correct. Was this followed correctly in your installation? Reason I'm asking is that exchanging two reds for instance, the heater will function normally, but will throw a huge 60Hz magnetic field between the cables. A simple way of testing this is to put a clamp ammeter around each cable **one at a time**. Anytime you clamp a whole cable, it should read near zero because currents should cancel each other out. – Harper - Reinstate Monica May 24 '19 at 15:57
  • Have you tried powering your DSL router from a UPS or other battery supply yet? It would really help determine if it is a power conditioning issue or a problem that is somehow induced in the phone line. – le3th4x0rbot May 25 '19 at 01:18
  • The link didn't have a video, only an image. I moved the image into the post for clarity – Machavity May 25 '19 at 01:47
  • @trognanders yes - its already on a UPS – Jon Barker May 25 '19 at 15:10
  • But unplug the ups from the wall – le3th4x0rbot May 25 '19 at 18:11
  • @JonBarker cold source to phone line? Gosh no how will all those hot singles in your area get through if you used the cold line ? – Criggie May 25 '19 at 21:37

5 Answers5

7

First, make sure that your three supply cables are paired properly. The unit has 3 heaters internally. There are several ways cables could be crossed that would result in power from 1 heater coming up one cable and returning on another cable. The heater would work properly, but would kick stupid large amounts of EMF from the two imbalanced cables. Just double-check it.


Or, the heater may be throwing high frequency electromagnetic hash, with the cable(s) becoming antennas and making this worse. Now, electric resistive heating elements, alone, do not throw electromagnetic hash. That would only happen from

  • a) control electronics, which will surely only be on one cable/circuit; or
  • b) power choppers ("dimmers") which could be on 1 or all of the circuits, but there'd be no useful reason to have them on more than 1 circuit.

Also, there's a thing I don't like about how Ecosmarts are installed - they expect you to cram three #8 cables through one 1" hole, which is a lot to ask, and requires just the right cable clamps to not violate Code.

I would install a 6" square deep or larger metal box right below the EcoSmart and a short EMT conduit nipple connecting it to the EcoSmart's wiring hole. Bring the 3 cables into the large box with correct clamps; leaving space for up to 3 "surge suppressors" to be fit onto 3 knockouts.

Then I would consult with EcoSmart and ask them a) which circuit powers the control electronics and b) whether they merely switch all 3 heaters, or whether they use power choppers, and if they do, on which circuit(s).

On the circuits which do not use choppers or electronics, those can be wired straight through the 6" box, up the conduit nipple and to the terminals.

For the circuit(s) which do use choppers or electronics, you run a pigtail from the EcoSmart's terminal into this box. Then you mount a "surge suppressor" in one of the knockouts (or not, if it's a type that can live inside the junction box e.g. Meanwell SPD-20-277P). Then join those wires to the power line from the panel. This wires the Ecosmart and the suppressor in parallel (the usual way you "tee" a connection) - it's not wired in series like a switch.

enter image description here

At this point, the surge suppressor(s) should be damping out the EM interference before it leaves the metal faraday cage of the Ecosmart + junction box.

I suppose Ecosmart could build this into the product, but that would raise the price-point, and so you might not have selected the product.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
  • Thanks for this input. I'm 99% sure the cables are paired correctly as they are all color coded red/black and grouped by breaker by the panel, and grouped by input on the heater. Regarding imbalanced cables: So if a line and load aren't grouped on the same cable then the load produces an EMF because it doesn't have the line to cancel it out? Good to know. – Jon Barker May 24 '19 at 18:13
  • @JonBarker Current flows in loops. It flows up wire 1 and returns on wire 2. (or sometimes is split, returning on wires 2 and 3). Each direction kicks up rather large EMF in proportion to current. If the wires are tightly bound together (**i.e. in a cable**), the large EMFs are equal and opposite - and cancel each other out. Hence no reading on a clamp ammeter. – Harper - Reinstate Monica May 24 '19 at 18:22
  • 1
    Note that an Arlington NM843 connector *can* fit 3 8/2s into a 1" KO (in fact, it can fit an 8/3 and 2 6/2s) – ThreePhaseEel May 24 '19 at 23:09
  • @ThreePhaseEel thanks. I hope EcoSmart includes one, if people were left on their own to find it, I'd expect most DIYers and many electricians to use the wrong thing. – Harper - Reinstate Monica May 25 '19 at 04:49
5

Long shot...if I'm wrong I'll delete.

112 Amps is a HUGE draw. As you probably know, many houses have a total 100 Amp (sometimes less) service. If your service drop isn't significantly larger, or even if it is but the utility didn't provision it well (e.g., they can, as I understand from other questions regarding service-entrance vs. "other" cables for 100A and similar sizes, downsize a good bit based on normal expected usage), then you could have a significant dip every time the heater kicks in. While the DSL modem is likely designed to handle a range of voltages, that still might be enough to cause problems. Similar to the way a laser printer on a 15A circuit can cause enough of a dip to reset some devices or at least to lower voltage enough for a few seconds that a UPS will treat it as an outage.

The right way to test this would be to monitor the voltage on the line powering the DSL modem as the heater starts up. If your voltages drops from 115V to 95V (or something like that) then the modem may simply not handle the low voltage and/or the voltage change well and lose the signal.

The secondary ways to test this are:

  • See if lights (especially incandescent as LED will often handle voltage fluctuations just fine) dim when the heater starts up.
  • Plug the modem (and while you're at it, the router and any other nearby computer-related devices, except laser printers) into a UPS. I use APC, but any decent model will do fine and I think it is a great investment - one didn't-reboot-during-a-thunderstorm can make it worth it even if it doesn't help for this problem. If the internet stays "live" with the modem & router on a UPS then you have your answer - and your fix.
  • 1
    A good possibility. These are resistive elements, so they should not have any startup surge at all. Voltage drop will be exactly the same throughout heater operation as during heater start (unless the heater "throttles up and down" by cutting out elements, in which case my query about cable matching becomes relevant.) – Harper - Reinstate Monica May 24 '19 at 16:58
  • Thanks for the input here - doesn't apply for me, but may be useful for others so won't downvote. My incoming current is 200amp on the main panel breaker, and the DSL modem/router is already on a UPS which will be maintaining a steady 120v – Jon Barker May 24 '19 at 18:02
  • Aha! The UPS is the key - the utility could **say** 200A and still there could be issues if it was marginal in some way. But the UPS rules out my theory, at least in your case. – manassehkatz-Moving 2 Codidact May 24 '19 at 18:16
  • 3
    oh, yes, *this*. Just because they *provision* 200A service does not mean they're not using the same #6Al service drop from when they provisioned 60A. Difference being, now they have a smart meter, which will notify them "Hey, I just saw a 19 volt voltage drop" or "hey, this guy is actually drawing 110 amps" (which they then run against their database showing a #6Al drop). In theory, after the system has collected enough data, it'll open a ticket to change your service drop to something appropriate, without you lifting a finger. – Harper - Reinstate Monica May 24 '19 at 18:28
  • 1
    @JonBarker Try plugging the modem straight into the wall and switching the UPS off completely. It's possible that when the input voltage sags as you turn on the heater, the UPS kicks in and starts boosting the voltage to 120 V, creating a lot of interference in the process. – TooTea May 25 '19 at 13:21
5

Something you might want to consider here is that your phone line inside the house is probably something crappy and unshielded. Cat3, for instance, offers virtually no shielding at all. What I would suggest is upgrading your phone line from the box to your modem with something that is better shielded, like Cat6. If you can afford it, going even higher (Cat6a or 7) would afford you greater shielding. 10MB down a copper line is probably highly susceptible to even minor interference.

Machavity
  • 23,184
  • 6
  • 41
  • 90
  • 2
    It could be far worse. Plenty of houses, particularly if built earlier than the 1980s, have an incoming phone cable that isn't even up to Cat 3 standards. – manassehkatz-Moving 2 Codidact May 26 '19 at 02:57
  • 3
    I'll accept this as the answer as it was the closest one to solve my problem - I noticed that my phone line was running parallel to the high amp cables. I moved the phoneline outside the house along the eternal wall about 2 meters below where the high amp cables were. I used cat 7 shielded cable and ran it to the router away from the high amp lines. This solved the problem. Now my internet works normally when the hot water is on! – Jon Barker May 27 '19 at 12:22
2

Find out what the DSL modem sees.

DSL is designed to detect and avoid all kinds of interference entering the line. Technically, it splits up the whole band into many narrow channels, continuously monitors them for noise and only uses the noise-free ones to transmit data. Any interference should thus just make the line slower but not kill it completely. Also, the low-frequency end of the spectrum is often reserved for voice and completely ignored by DSL, so the 60 Hz current into the heater might not matter at all.

Instead of playing around with the heater to try to figure out what's going wrong, check out the diagnostics on the DSL modem. When you log into its web management interface (by entering its IP address into your address bar and logging in, possibly with default passwords that should be either in the manual or on a label on the unit), you should be able to find some "DSL Status" tab showing what's actually going on with the line.

There will be something like Line State saying up, showtime, synchronized or so. Does that change when you flip the breaker?

If it doesn't, look for something like Noise Margin. That will probably change a lot if the line starts picking up a new source of interference. That in turn leads to Attainable Data Rate dropping as the modem stops using the noisiest channels.

There will also be something like Line Attenuation and Signal Attenuation. This probably won't change as it measures how much signal is lost along the way to the DSLAM.

TooTea
  • 2,263
  • 12
  • 23
  • That's a good way to confirm the times, and that something is messing up the DSL signal. If the modem doesn't have such logging, then the ISP may be able to organise a line test across a certain time window. Downside, it doesn't show why the water heater is causing the interference, just that the timing lines up and confirms the heater switching as the cause. – Criggie May 25 '19 at 21:41
1

112A will induce voltages in any cables (phone connections) anywhere near that massive power-line you have.

What is meant by the term "split-phase" - is this single phase or guessing by the use of "3x 40amp dual pole breakers" a system where a 3 phase supply is split into 3 single phases?

If so, I strongly doubt it meets current electrical regulations...

Jeremy Boden
  • 139
  • 5
  • 2
    "Split phase" is the normal North American system of 240V --> 2 x 120V. 3 x 40A is really to get 120A total, but is done as 3 x 40A because that makes the wiring & breakers a whole lot easier. Each of those 40A is 240V == hot/hot/ground. Just think of it as 3 dryer or oven or conventional water heater circuits, but all feeding into one on-demand heater. – manassehkatz-Moving 2 Codidact May 24 '19 at 17:23
  • 1
    Yuck! - do they really allow that!!! – Jeremy Boden May 24 '19 at 17:24
  • 3
    It's the latest thing. I have my own reasons why I wouldn't do that, and it makes a **lot** more sense to me if done with natural gas (though arguably if you can get "green" power then electric is better for the environment). I think the concept is: why heat up 50 gallons and let it sit if you only need hot water once in a while. – manassehkatz-Moving 2 Codidact May 24 '19 at 17:25
  • 2
    @JeremyBoden Of course they do. They're not *paralleling*; the unit has 3 heaters each <40A fully isolated from each other. Nothing wrong with that! A very sensible way to get *that much* power. Multiple smallish cables is better than 1 big one (ask if you want to know why). Also, **this allows use on 3-phase** - 240V "delta" (US), 208 "wye" (US) or 220V "wye" (Brazil) both delta-connected, or 400V "wye" (Europe). Or even 480V "wye" US with bucking transformers or different heating elements. *At that point you are wiring the appliance with 3-4 wires*. – Harper - Reinstate Monica May 24 '19 at 17:36
  • 1
    I'd argue that multiple circuit breakers for one device is rather peculiar. Can't see that multiple heaters on dedicated wiring is better than one heater on one connection. – Jeremy Boden May 24 '19 at 17:44
  • As stated - this is standard in north america. I'm originally from the UK so used to 230v single phase, but split phase 120/240 is normal here. All regular appliances run on one of the two legs at 120v, and high current appliances take both legs and produce 240v without a neutral – Jon Barker May 24 '19 at 17:59
  • 1
    @JeremyBoden - TIL that there's equipment in people's houses that can zap me with 80 amps if I don't turn the *other two* breakers off. This should only be allowed on 3-phase with a tied handle breaker. Absolutely Wack. 100 amps? ffs... Prob shouldn't let people with pacemakers in your house. – Mazura May 25 '19 at 02:29