27

Background Info: My house is all electric.

Last month when I got my electric bill, I flipped. It was triple that of any month prior. Now I know the cold (heating) can affect this so I decided to turn my thermostat back, even though I never had to before. I've finally got the results back and to my surprise, it's still pretty darn high (but somewhat lower thankfully). The head-scratcher is that not only did I turn my thermostat down 4-6 degrees, it also hasn't been very cold here lately. It has ran a fraction of what it did the month prior, and that's just from the ambient temp difference. This isn't considering the fact that the thermostat is off for half of the day while I'm at work. I also wouldn't deem my system extremely inefficient, as I have a heat pump.

Anyways, so I'm suspecting there's something else at play here. Perhaps another large appliance like the washer/dryer, dishwasher, hot water heater, etc. However, I do not know how to troubleshoot this or determine how much energy any one appliance is using.

Are there any pro-tips or easy/cheap ways that I can measure, or at least get a general idea, of which appliance in my house could be causing such high energy usage? I've seen before meters that you plug into the wall (in-between the socket and appliance), but I imagine those are not the most inexpensive route to take. I was wondering if maybe I could see the real-time load for the entire house? Like at the meter, and then I could one-by-one disconnect appliances and notate the fluctuations in total usage.

Anything like that would be great, or if you have better ideas, please share!

Quick Note: I recently had someone move into one of my spare rooms. One of my suspicions that I'm looking to verify is that they take extra long showers and overwork my hot water heater. I mainly suspect this because they mentioned that they ran out of hot water, something that has never happened to me before.

I wouldn't be concerned if I was still considered "efficient" by my electric company, but as you can see, I went from being relatively efficient to not even close. enter image description here

UPDATE 3/3/2018 After doing some testing, I've come to realize that my heat pump isn't putting out any heat at all. So basically, I have been running off AUX heat exclusively. That combined with how cold it has been may very well explain the large spike in usage. I called a tech to come look at it. I will update and close this question once it has been verified.

UPDATE 12/10/2018 It has been a while so I thought I would share with everyone what the real issue was. After a few visits, it was finally discovered that my heat coils were stuck on. Even with the thermostat off, they were getting constant power. You could actually feel the heat radiating from the floor above the coils (they're in a crawl space). I'm lucky they found it, otherwise I could've had a fire on my hands. So yes, in essence, my AUX heat was running 24/7 for what was likely a month or two. CRAZY!

hack3rfx
  • 1,232
  • 2
  • 14
  • 26
  • 2
    Are your bills based off of actual meter readings or just estimates? Some companies use estimates every other month or so. So it is possible the second bill was not as low as you had hoped because the company overestimated your usage. – unutbu Feb 27 '18 at 21:14
  • 2
    Keep in mind that all the electricity you consume is converted to heat, more or less directly. With the amount of increase you describe, you should only check the heating elements. Either you are venting lots of warm air outside (air echanger?) or lots of warm water (water heater leak?). Anything else you'd have noticed already, IMO – Jeffrey Feb 27 '18 at 21:14
  • @unutbu Good thought, that I hadn't considered. Given my bill, it seems as though they are not estimates. They list out the amount of kWh that I've used at each price point (varies due to peaking). – hack3rfx Feb 27 '18 at 21:16
  • 4
    make sure that someone is not stealing power from you – jsotola Feb 27 '18 at 21:17
  • @Jeffrey Thanks. I've visually inspected everything I could think of. I even fix caulking where needed and installed new weather stripping and insulation – hack3rfx Feb 27 '18 at 21:17
  • @jsotola I did consider this, but there's nowhere that they would be able to "hook in" without me noticing. – hack3rfx Feb 27 '18 at 21:18
  • 1
    How much higher was the usage per day in kWh? This will help give an idea of how much more 3x more really is. – Jon Feb 27 '18 at 21:36
  • 1
    Heat pumps are often paired with a more expensive secondary heat source that runs when the heat pump can't keep up. What fuel is used by your secondary (emergency) heat source; is it gas or electric? – Jon Feb 27 '18 at 21:39
  • 1
    @Jon I'm not able to see a daily reading. I don't think we have had an update in my area for a long time. However, in Aug/Sep/Oct, I used between 609-643 kWh each month. Nov was 1053 kWh, December 2044 kWh, and Jan 3271 kWh. Jan (this month) it went down to 2155 kWh. – hack3rfx Feb 27 '18 at 21:42
  • @Jon It's all electric – hack3rfx Feb 27 '18 at 21:43
  • 5
    Is your new housemate home during the day? they could be keeping your thermostat from going into away mode, they may also be turning it up too. – Jon Feb 27 '18 at 21:57
  • 3
    You can view your thermostat usage history here: https://home.nest.com/thermostat/ the website shows when weather or user adjustments account for higher or lower usage. – Jon Feb 27 '18 at 21:58
  • @Jon They are not home during the day either, and I'm able to view my temp in real time with the Nest app. I did suspect this though. – hack3rfx Feb 27 '18 at 21:58
  • How long have you lived in this house? Have you lived through a winter season in it, or do you have historical data from previous owners / tenants to compare your usage? And where in the world do you live? Living in the NE US, or somewhere like Fargo, ND, where it gets cold in the winter, this usage probably makes complete sense... – mmathis Feb 27 '18 at 22:00
  • @mmathis I've been in this house almost a year, but I knew the previous owners really well and got historical data from the electric company. The highest valued bill was almost half of what mine was last month (January). I live in the mid-west. – hack3rfx Feb 27 '18 at 22:01
  • And you're comparing kWh usage and not $ usage right? – mmathis Feb 27 '18 at 22:04
  • @mmathis When I first moved in, I only researched the cost ($). Energy prices are about the same though, not much has changed besides peak times. However, the past few months (where it peaked), the majority of my kWh were at the lower end of the spectrum, in terms of cost that is. – hack3rfx Feb 27 '18 at 22:06
  • @Jon I do not have access to daily readings. – hack3rfx Feb 27 '18 at 22:31
  • 7
    First thing to do is to make sure your electric meter readings actually match the numbers on the bill. Second thing to do is to shut off all lights, space heaters, etc, turn furnaces off, etc, and then check to see how fast the meter is spinning. Then flip stuff on a few pieces at a time and see if there's a sudden jump. – Hot Licks Feb 28 '18 at 03:17
  • 1
    Many electric meters don't "spin" anymore, so looking at real time usage can be hard. There are energy monitor devices that hook up to your breaker panel that you can use to see usage in real time tho like [this one](https://sense.com/) (many others, just an example). – JPhi1618 Feb 28 '18 at 16:23
  • 12
    >3000kWh used in Jan alone, so >100kWh per day? That's an *average* of over 4kW, non-stop. You'd think that would be detectable by looking for the thing that's glowing red hot. – Nye Feb 28 '18 at 16:50
  • OP, if you're having a moderate (30-60F) day right around now, this would be a great time to check your heat pump for normal operation. First check your power meter to see its normal rate of spin/right-now KW. Then kick your thermostat up to cause a call for heat. Now go outside and check if A) the outdoor A/C unit is whirring and buzzing in the normal way, or if B) your electric meter is now spinning fast enough to change the Earth's rotation, which ends if you turn off the huge 50-70A "emerg heat" breakers in your panel. A not B = good. B not A = failed heat pump. – Harper - Reinstate Monica Feb 28 '18 at 16:54
  • 1
    @JPhi1618 most meters I've seen either have a button to change displayed parameters, or flip parameters themselves every 2-3 seconds. One will be instantaneous real-time KW (not KWH). If *your* meter doesn't have that, I'd raise holy hell with the electric company on account of the impossible bill... they should happily swap your meter to one that *does*. – Harper - Reinstate Monica Feb 28 '18 at 16:57
  • it's still saved me a lot, especially after my (forced) switch to a smart meter where they bill for PFC now, so you pay for the VA not watts; some of my wall-worts went from being billed at 3W to 18VA! needless to say i use more switches these days... Also, you can use a clamp meter for big appliances: something like https://www.ebay.com/itm/401249692081 is affordable and accurate enough. – dandavis Feb 28 '18 at 17:33
  • 1
    "I recently had someone move into one of my spare rooms. One of my suspicions that I'm looking to verify is that they take extra long showers and overwork my hot water heater. I mainly suspect this because they mentioned that they ran out of hot water, something that has never happened to me before." That's a big clue. Reheating a tank full of street cold water gobbles up a lot of Bthu. Leaving the hot tap dripping or dribbling also consumes a lot of power. – Trevor_G Feb 28 '18 at 20:01
  • 1
    btw you went from an average power usage of 1kW to just over 4.5kW. So it's not something like the fridge unless it's getting really hot. SO your looking for either something big, or a LOT of little things. – Trevor_G Feb 28 '18 at 20:11
  • How long ago did the roommate move in, and has there been a corresponding spike in your water bill? – mmathis Feb 28 '18 at 20:48
  • @mmathis I didn't realize this until I added the graph to this post, but my roommate moved in around late November. So there is definitely a correlation. However, that is also when it started to get really cold here. So it could be coincidental, or a two-factor effect. I suspect that if I remain "above average" during the warmer months, I can easily deduce that it is in fact my roommate driving my utilization up. – hack3rfx Feb 28 '18 at 20:50
  • I know when i shared a house with some people when we were students, some of them would leave a heater on in their room all the time - drove me insane!. – djsmiley2kStaysInside Mar 01 '18 at 09:45
  • 1
    A tenant that does not pay for hydro and likes fresh air can kill your bill too. Nothing like warming up the neighborhood through open windows when its minus 10 outside. – Trevor_G Mar 02 '18 at 01:24
  • Note that your roommate running out of hot water doesn't necessarily mean they use more than you, if you shower first. If you use, say, two-thirds of the hot water, there'll never be a shortage when it's just you in the house but then your roommate tries to take a shower and brr. – David Richerby Mar 03 '18 at 12:45

13 Answers13

25

Since you say your backup heat is electric, I'd say that's what is using all the power. It could be that the weather is unseasonably cold and that the backup emergency heat is kicking in often.

Your Nest Thermostat could be switching to AUX heat more often than your old thermostat would have.

Since you say your nest thermostat is new (last summer), It is likely that it is responsible for kicking on the aux (emergency) electric heat more often than your old thermostat. There are settings to change how often this happens described below.

Your Nest thermostat may calling for aux heat more often than your old one would have. This can be configured with Heat Pump Balance which you might try changing to Max Savings or balanced. Note that the link below states that Max Comfort, the most expensive option, is selected by default. This is probably the issue. If changing this doesn't help, then I'd call an HVAC specialist.

enter image description here

Because auxiliary heat is so expensive, running the heat pump longer is still cheaper than using AUX heat. Heat Pump Balance automatically turns the heat on early to reduce AUX heat use as much as possible and get to your target temperature on time. It can turn on the heat up to 5 hours before a scheduled temperature if necessary. So if your schedule says 70ºF/20ºC at 7pm, Heat Pump Balance can use Early-On technology to start heating as early as 2pm.

Heat Pump Balance gives you four options to choose from:

  • Max Savings - This is the best setting for saving energy. In Max Savings mode, the Nest thermostat gives the heat pump more time to get to your target temperature before turning on AUX and sets a lower AUX lockout temp.

  • Balanced - This setting will give the heat pump more time to work, but will still turn AUX on quickly if it looks like it won't get you to your target temperature on time. Balanced has an AUX lockout temp somewhere between Max Comfort and Max Savings.

  • Max Comfort - When you choose Max Comfort, the Nest thermostat will make sure you'll get to the temperature you want, even if it means using auxiliary heat. Max Comfort is the default setting for Heat Pump Balance and generally gives you a higher AUX lockout temp.

  • Off - You can also turn Heat Pump Balance off entirely and adjust your AUX lockout temperature yourself. The AUX lockout temperature can be changed in SETTINGS > EQUIPMENT > HEAT PUMP.

There might be something wrong with your heat pump.

It could also be that there is something wrong with your heat pump. IE, it is running and using some energy but not generating any heat. Eventually, this will lead to the thermostat switching on the emergency electric heat and that will use even more power. Call an hvac specialist and have it inspected.

Jon
  • 1,667
  • 11
  • 26
  • I have a Nest learning thermostat which I love. It always says Aux Heat, I never really knew what that meant. But I've never seen it read Emergency Heat. Is there a difference between Aux and Emergency heat? – hack3rfx Feb 27 '18 at 21:53
  • 1
    @hack3rfx emergency and Aux heat are the same. If everything is electric, AUX heat is going to be very expensive – Jon Feb 27 '18 at 21:54
  • 10
    That is probably my issue right there then. My thermostat is almost always on AUX. So would the best course of action be to have my Heat Pump checked and replaced if needed? – hack3rfx Feb 27 '18 at 21:55
  • 4
    @hack3rfx Yes, have the heat pump checked – Jon Feb 27 '18 at 22:01
  • 1
    @hack3rfx, is the nest new for this year? Not all heat pumps are wired the same, and it could be doing something wrong. It was a long process to get my thermostats wired up correctly to our HP system. – JPhi1618 Feb 28 '18 at 16:21
  • @JPhi1618 I got my nest in mid 2017 and at the time, it was the newest model. – hack3rfx Feb 28 '18 at 16:24
  • 5
    @hack3rfx It could be that the nest was installed incorrectly. An HVAC specialist would be able to diagnose that. I could imagine an issue where the heatpump is never being used because it was connected incorrectly and it is always falling back to aux heat. – Jon Feb 28 '18 at 16:26
  • 1
    @hack3rfx, maybe I worded that poorly - I'm not saying your nest could be old, I'm saying that your old thermostat could have behaved differently last winter. Maybe the nest is wired wrong or is set up wrong so it's calling for Aux heat too much or doing something else that's using more power. – JPhi1618 Feb 28 '18 at 16:26
  • @JPhi1618 It does run on the heat pump. Just not as much as it runs on AUX. With the 40-50 degree weather we've been having, I actually haven't noticed it on AUX in a while. – hack3rfx Feb 28 '18 at 16:28
  • 1
    @hack3rfx I've updated the answer with information about adjusting the heat pump usage on a nest thermostat – Jon Feb 28 '18 at 16:34
  • 1
    @Jon Thanks for the pictures. It was on balanced so I switched it to Max Savings. We'll see what that yields. – hack3rfx Feb 28 '18 at 20:04
  • 1
    @hack3rfx can you update your question once you have some usage results? Also, if this turns out to be the cause, don't forget to accept this answer ;) – Doktor J Mar 01 '18 at 21:24
  • 2
    @DoktorJ Yes, I had intended on doing so. Many of the suggestions are going to be a waiting game, as well as trial and error. So it may be a bit before I determine the resolution. It's unfortunate I have to pick one answer though because they are all helpful and well thought out. Most likely all items contribute to some degree making them all correct in some way. – hack3rfx Mar 01 '18 at 21:27
  • Slight variant on this: a neighbor had a defect that left the auxiliary heater permanently ON. They realized this only after the electric bill. Besides repairing, they decided to have an additional manual switch that is OFF by default so they'll always know when the expensive electric heating is on (this is Germany, where a) electricity is expensive and b) heat pump system rating is often so that auxiliary electric heating is needed only few days each winter) – cbeleites unhappy with SX Mar 03 '18 at 18:58
23

Do you have average temperature data for your area, so you can verify that it hasn't been "that cold". You didn't purchase any new electronics such as bitcoin miners with the latest craze did you? Have any close neighbors?

Cheapest thing if you have no electrical test equipment: go to the meter, on a lot of them you can see the least significant digit moving. Get a stop watch and time how long it takes to move 1 digit or however many you can easily decipher. Go to your circuit breaker and switch off one circuit at a time, starting with the biggest appliances. Go back to the meter and retest the time it takes to move however many digits. Turn the circuit back on and turn another off, repeat for all the major appliances and see which is drawing the most power.

I would suspect (assuming you turn off your HVAC most of the day): water heater top of the list, HVAC second. Dishwasher, stove, oven, microwave, also pull large amounts of energy but don't tend to be continuous and unnoticed.

John Thompson
  • 365
  • 1
  • 7
  • I updated the original post showing the averages for my neighborhood. I also haven't made any big (electronic) purchases lately. As far as my neighbors go, it's highly unlikely they have purchased anything large as one of them is now a vacant house, and the others are more elderly residents. Now, this probably isn't relevant as my town has a population of ~3k and it's most likely considered one neighborhood, or it's likely very few at least. – hack3rfx Feb 27 '18 at 22:04
  • 4
    There is a catch: if the main contributor is intermittent, there is a significant chance that it's off at the time of the measurement. The only chance to catch it would be to wait for it to be turned on. – clabacchio Feb 28 '18 at 13:38
  • I would add the fridge to your list. – yo' Feb 28 '18 at 17:57
  • 4
    @yo' Fridges are typically on a standard 15A receptacle, which would cap the usage at about 1300 kWh per month - the OP saw an increase of about double that over several months, reducing the likelihood that this is a single 120V device causing the increase. – mmathis Feb 28 '18 at 20:50
  • Nah, with electric aux heat HVAC is definitely top of the list. Do the math - even adding an extra 20 minute hot shower every day can't burn the delta kWh OP is showing. – J... Mar 01 '18 at 16:55
15

Mid-December through January were brutal in the midwest. Most days and nearly every night were below 10F.

Normal heat pumps cannot work at such low temperatures.

The heat pump was failing over to "emergency heat"

This is just a big bank of electrical resistors. I have seen installations where these resistors were on dual 70A breakers and ran well over 24kw - at common electric prices, that's $3/hour.

This wasn't your problem. But watch out for emergency heat incorrectly configured as "auxiliary heat" on the thermostat. The 'stat will call for that whenever it needs to speed up house heating a little bit, e.g. When warming it for your arrival back home. It presumes main and aux heat cost about the same or that you don't care. However the 'stat has no idea when the heat pump is too cold to work. The heat pump knows and it should call for emerency heat only when it cannot work IMO.

Harper - Reinstate Monica
  • 276,940
  • 24
  • 257
  • 671
  • 2
    Re: "only when it cannot work", the heat pump may "work" even at very low temperatures, but its efficiency drops off to the point where it takes the same amount of energy to pump the heat as the amount of heat it moves, making it no better and eventually worse than simply dumping energy through resistors. – R.. GitHub STOP HELPING ICE Feb 28 '18 at 01:28
  • 2
    Actually, this winter was pretty mild in southern Minnesota. – Hot Licks Feb 28 '18 at 03:18
  • 1
    That would certainly account for the extra 3.6kW average power he is consuming. – Trevor_G Feb 28 '18 at 20:13
8

Disclaimer: I am located in central europe, so this may or may not apply for you.

In our region, typically every energy company and several environmental NGOs offer a service to borrow an energy meter for free or with a very small fee. Like this one: https://www.swm.de/privatkunden/kundenservice/energieberatung/strommesskoffer.html (it's in german, but just have a look at the pictures) Usual procedure is, you write to them and they give you date and time to pick up the equipment, and a week or two later you return the stuff.

There are meters for usual plugs, but there are also clamp-on-meters, which allow you to measure power consumption of directly wired appliances (e.g. if you suspect your ceiling light to run a server cluster up there).

IMHO this is the simplest, cheapest and most accurate way of having a power consumption survey in your home.

  • 1
    I've not seen anything like that in the US. Interesting service, tho. The catch there is it looks like it only covers pluggable devices – Machavity Feb 28 '18 at 13:39
  • 1
    I know there are clamp power meters that work for non-pluggable devices. An example being this one: http://www.fluke.com/fluke/phen/clamp-meters/fluke-345.htm?pid=56070 but I can't name a specific power company wich lends out these. I would do the research around the companies I know, but it doesn't seem to be geographically applicable to OP. My first try would be to contact your local Greenpeace or any similar environmental organization. They tend to be pro-energy-saving and usually they know a lot about tricks like where to borrow a power meter. – NightLightFighter Feb 28 '18 at 14:15
  • Since the Fluke 345 is [about $3000](https://www.amazon.com/Fluke-Quality-Accuracy-Resolution-Temperature/dp/B01NAXFLN0/ref=sr_1_3?ie=UTF8&qid=1520098217&sr=8-3&keywords=fluke+345+power+quality+clamp+meter) to purchase, there won't be abundant sources for lending it. – wallyk Mar 03 '18 at 17:32
  • Non-logging clamp meters can be had for <$50. Power quality analyzers, like the mentioned Fluke 345, measure things like harmonics, which is way overkill for this problem. – user71659 Mar 03 '18 at 17:39
7

In a LOT of cases I've seen like this, it's turns out a problem with your water heater, assuming that if you have electric heat, you likely have an electric water heater. If the element is damaged, it leaks current into the water and immediately to ground, but because it's a high resistance ground fault, the breaker never trips. The fault in the element decreases the efficiency, so it almost never shuts off as it struggles to keep up with your hot water demand. You may not notice it in the hot water though, just in the high power consumption. Have an electrician check it for you.

JRaef
  • 14,724
  • 1
  • 17
  • 39
  • 1
    This is al ittle bit confusing because theoretically, the electricity leaking through the water should also produce heat. – user253751 Feb 28 '18 at 00:26
  • 1
    @immibis electric current through water does consume energy, but that energy is used to convert water into hydrogen and oxygen gas through a process called electrolysis. You might find it interesting that electrolysis actually feeds on heat energy. In this way thermal energy is used for part of the electrolysis energy requirement, and thus at high water temperatures, a current leak actually COOLS the water, requiring the appliance to compensate. How much it cools or how much gas is produced requires calculations beyond me but thermodynamically speaking, electrolysis is counterintuitive. – Nathan Feb 28 '18 at 07:13
  • 1
    Do electric hot water heaters really not have GFCI? – Samuel Feb 28 '18 at 09:23
  • 2
    @Samuel I've not seen any, no. But you could buy a GFCI breaker for the panel (the amps needed require a dedicated circuit) – Machavity Feb 28 '18 at 13:41
  • 1
    No, GFCIs are not used on electric water heaters. – JRaef Feb 28 '18 at 23:12
  • 1
    Props. This happened at my house. An element failed, the hot water tank drew enough power to double our electric bill for the month, then finally melted the insulation off the wires at the heater element. 220V @ 30A is not to be fooled with. – Yojimbo Mar 01 '18 at 00:46
  • I'm curious of the chances of this happening with a brand new water heater? I'm having similar issues and replaced the water heater. It made zero change in my electric bill. I have it now on a timer and my usage goes down to almost zero when it is off. It is constantly drawing electricity. Are there other factors that may cause it to constantly run? We've already checked for leaks. Could it be high water pressure? – Joe Raio Mar 08 '19 at 15:03
4

When heating a house, you don't pay directly for the temperature inside the house. You pay for the heat that gets away from your house. Dialing the thermostat down works because smaller temperature difference means slower heat transfer. On the other hand, increasing insulation gets higher temperatures at same cost.

If that new person enjoys fresh air and is keeping a window cracked open, or doesn't understand how thermostat works and instead of dialing it down opens the window, the thermostat will try to maintain the temp and this process can burn absurd amount of energy, as you're basically trying to heat up the world outside through the open window. I suspect the new person here, but damaged/removed insulation will yield same reason - when the heat is escaping, the thermostat will run heaters 24/7.

You should look for heat escape routes.

I was wondering if maybe I could see the real-time load for the entire house? Like at the meter, and then I could one-by-one disconnect appliances and notate the fluctuations in total usage.

Then just look at your meter. The old ones have a spinning wheel, and the new ones have a blinking light. The faster it goes, the higher the energy consumption. For rough estimation, just looking at it helps, if you want exact numbers then you start counting - factor should be written on the meter, eg mine says "6400 pulses per kWh". However, I believe that this is a dead end. If you haven't brought any new appliances into the house, the problem is most likely an old appliance that now works much more than it did earlier.

What you want to monitor is appliance usage. It can be a simple sheet of paper when people log usage next to washing machine, etc. But that data is not easy to analyze without old data - just as you suspect more water heater use now, but you don't have historic water heater data. However, take a look at your old water bills - increase in water usage should be roughly proportional to water heater usage.

Agent_L
  • 1,650
  • 11
  • 13
2

While the heat pump / HVAC is a very likely culprit and should be checked out first, it is possible that this is a combination of seasonal variations and the new roommate.

Looking at your graph, I'm guessing your roommate moved in sometime in November, as that's when your usage started exceeding that of your neighbors. Also, taking your neighbors' usage to be typical for your area and the season, you used an extra ~1300 kWh than they did in Jan (~800 kWh extra in Dec). Let's see if we can explain that away due to the roommate.

Water usage increases with the number of people in the house (roughly linear), so you should expect to use roughly twice as much (hot) water, meaning twice as much electricity to heat that water. Hard to pin down actual numbers without additional equipment or details, but hot water tends to be 10-15% of your utility usage:

enter image description here

source

This means you were using ~70-100 kWh per month to heat your water before the roommate. If your roommate likes long hot showers (and they very well might if they're not responsible for any of the electric bill!), though, that usage could more than double, so maybe it's an additional 150-200 kWh because of them. Any increase here should be readily apparent on your water bill, too.

Your roommate also does laundry and dishes, cooks, etc. Maybe you eat together, or combine dishes into a single run of the dishwasher, so this isn't exactly double your previous usage. Call it 1.5x though. Appliances tend to be another 10-15% of your electric bill (~70-100 kWh), so this could add an additional 35-50 kWh. That's 200-250 kWh extra total.

I assume your roommate has a computer, which is probably on all of the time. Even a low-powered one would consume ~70 kWh / month, but if they have a big machine and have it under load most of the time (maybe running Seti@Home, or another @Home project, maybe just gaming a lot at night, or maybe they're cryptomining), this could hit 500 kWh per month. That's 700-750 kWh extra total.

Add in some extra lights being on, maybe a TV in their room, device chargers, etc and that could be an additional 100 kWh a month or more. Total is now 800-850 kWh extra. That explains your December usage right there, though we're still a bit short on January usage. Maybe that is emergency heat, additional water heater losses due to extreme cold, etc, or it could be that our estimates were off.

As I said, this is not necessarily "normal" usage, but that it could be explained by non-broken things.

mmathis
  • 8,754
  • 12
  • 41
  • 60
1

You, and all answers, seem to focus on the fairly obvious high energy consumer - water heater.

You mentioned that you recently got a lodger in your spare room. How well do you know what they do in their room? A colleague of mine recently discussed how his energy bill tripled from one month to the next - all thanks to an average-sized bitcoin mining rig. These are (usually) very specialised computers that are very fast and very powerful - and as a result use a lot of energy. He calculated his actual usage increased by roughly 1,000 kWh per month.

I'm not necessarily suggesting that this is what is going on, but it's worth checking.

Aleks G
  • 451
  • 2
  • 14
  • I'm a developer and the only tech savvy person in the house. We don't do crypto currency at all. As far as what he does in his room, its mostly his tv and a playstation. No computer or anything. – hack3rfx Mar 01 '18 at 01:07
0

You mention that your roomer has a TV and a game console. Large format LED/LCD flat screen TVs, despite the sales hype about being "energy efficient" are actually consuming a LOT of power. I have a 45" LED "Eco" model, it consumes 1.5kW (1500W) when it's on. That's like running a hair drier non-stop, or three 500W flood lights. Then even when it is off it is still consuming 50W continuously (hot standby mode). On top of that, a lot of gamers will pause a game so as to not lose their progress, then just get up and walk away, leaving the TV on 24/7. When my gamer son moved out, my power bill dropped by 50%!

JRaef
  • 14,724
  • 1
  • 17
  • 39
  • 5
    What the hell kind of TV do you have? I picked up a cheap 60" Sony TV the other day, its *rated* maximum is 162W (and then you can tweak various settings to lower its power consumption). I could literally put nine of them in a 3x3 array for a 180" display, and still be using less power than you (though the display electronics to split the image across the nine screens might tip me a little past the 1500W mark)... – Doktor J Mar 01 '18 at 21:21
0

You can tell relative power usage of a circuit by the temperature of the circuit breaker protecting it. Feel them and see if any are noticeably warm. You could also use an ir thermometer to check them more accurately.

silver
  • 1
0

If you suspect a particular appliance that plugs into the wall, I suggest using a Kill-a-Watt. It can measure instantaneous power draw as well as aggregate energy usage. It's pretty cheap, less than $30. Since you say your house is entirely electric, I imagine your water heater runs off electricity, but it may be wired directly without a plug.

There's another device on the market called Sense (http://sense.com) that works for all electricity usage at your home since it measures right at your breaker box. The product claims to tell you what appliances (based on the way they draw power) are on and when they are on down to the second. I've been interested, but it is $299 at the time of this writing, but I would think that is the ultimate, if pricey solution.

0

You might be interested in buying an Efergy Elite 4.0 Wireless Electricity Monitor. They cost about $100. I used mine for about three years until I had measured and recorded the KWH on most of the circuits in the house. It helped me to clearly understand that the main KWH users were heat, AC, and hot water heater. It led me to upgrade our AC/heater (Split Unit), add attic insulation, install an attic fan, insulate attic stairs, and other things and was able to prove it was saving money with before and after KWH consumption history. You use it at the circuit breaker panel; but, you have to be comfortable taking the cover off and connecting the meter clamp over the internal wires. It has a sending unit that you mount beside the panel, and a receiving unit you can place where you want. It also keeps daily KWH usage for about a week. I kept records in an Excel spreadsheet over a few weeks per circuit. Haven't used it in a couple of years now, but will if I start suspecting unusual usage. Oh, one more thing, it can measure 240v as well as 120v circuits.

getterdun
  • 1,695
  • 2
  • 13
  • 16
-1

If you have an idea of what appliance might be causing the issue, you can use a device called kill-a-watt to measure the power draw.

amazon link

john
  • 1
  • 3
    That's assuming it is fed by a standard power cable; which most devices with really high draw wouldn't be able to run off of. If you suspect it's a device plugged into a normal socket, then this might work. In general, you'd expect really high power draw to come from things like heat pumps, electric heaters and hot water tanks; which in general don't use a standard 120 V socket. – JMac Feb 28 '18 at 20:18